Default Bathroom fan venting

yes it's "legal" (not much is "illegal" in this basackwards state) but I still don't like this as general practices go. To great a probability of adding moisture/elevated humidity levels to the attic space. (imho) Never mind the fact that getting a builder to install gutters is like pulling teeth.

What say you?
Attached Thumbnails
bathroom-fan-venting-14cardinaldr020808-066.jpg   bathroom-fan-venting-14cardinaldr020808-064.jpg   bathroom-fan-venting-14cardinaldr020808-065.jpg  
Reply With Quote
  #2  
Old 2/8/08, 7:08 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Bathroom fan venting

You guys are on a run today! What is with all this "code" and "legal" stuff?

At least they vented it to the outside!
If I got $1 for every un-vented vent I come across....
Reply With Quote
  #3  
Old 2/8/08, 8:25 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bathroom fan venting

I agree with David. It would have been nice if they had skipped the vented piece of soffit in the immediate area to reduce the risk of running the vented air right back up into the attic----but at least it isn't venting to the back side of the soffit like the two I had yesterday </IMG>
Reply With Quote
  #4  
Old 2/12/08, 5:16 PM
William C. Martin William C. Martin is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Cleveland, GA
Posts: 59
Default Re: Bathroom fan venting

Attached is what I find aboout 33% of the time. Exhaust in the attic under the insulation.

The other is where the exhaust blows on the sheathing.

Would take an additional 15 minutes and $10.00 to do it right when being built.
Attached Thumbnails
bathroom-fan-venting-p2050005.jpg   bathroom-fan-venting-p2070017.jpg  
Reply With Quote
  #5  
Old 2/12/08, 5:26 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Bathroom fan venting

Quote:
Originally Posted by cduphily
yes it's "legal" (not much is "illegal" in this basackwards state) but I still don't like this as general practices go. To great a probability of adding moisture/elevated humidity levels to the attic space. (imho) Never mind the fact that getting a builder to install gutters is like pulling teeth.

What say you?
Chris,

I see these on an everyday basis and have never run into moisture issues in the attic at that location. They are absolutely fine. I just make sure they are connected.
Reply With Quote
  #6  
Old 2/13/08, 3:06 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bathroom fan venting

I always enjoy the "duck tape to the nail" installation method.

bathroom-fan-venting-104_5324.jpg
Reply With Quote
  #7  
Old 2/13/08, 8:15 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: Bathroom fan venting

William,
Was the second photo taken in a townhome?




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #8  
Old 2/15/08, 7:55 PM
bjones1 bjones1 is offline
Active Poster
 
Join Date: Mar 2005
Location: Coe Hill, On
Posts: 364
Send a message via MSN to bjones1
Please Note: bjones1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bathroom fan venting

I'm kind of curious to see where this thread goes, I've been asked to vent 2 bathrooms in a reno and the only place available is either through the roof or through the soffit. I'm looking at both the pro's and con's.
Reply With Quote
  #9  
Old 2/15/08, 8:01 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Bathroom fan venting

Quote:
Originally Posted by bjones1
I'm kind of curious to see where this thread goes, I've been asked to vent 2 bathrooms in a reno and the only place available is either through the roof or through the soffit. I'm looking at both the pro's and con's.
There's nothing wrong with venting your bathroom fans into the soffit area.

A roof penetration would be susceptible to leaks.
Reply With Quote
  #10  
Old 2/15/08, 8:29 PM
bjones1 bjones1 is offline
Active Poster
 
Join Date: Mar 2005
Location: Coe Hill, On
Posts: 364
Send a message via MSN to bjones1
Please Note: bjones1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bathroom fan venting

Quote:
Originally Posted by dvalley
There's nothing wrong with venting your bathroom fans into the soffit area.

A roof penetration would be susceptible to leaks.
Thanks David. Those were my thoughts as well. I just put a new roof on this one last year and I just dont like going through a roof for venting a fan.
I inspected a house 2 years ago that had all 3 bath fan vents connected to the main stink-pipe. Had another where 2 were ducted to the roof vents.
Reply With Quote
  #11  
Old 2/15/08, 8:35 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Bathroom fan venting

Quote:
Originally Posted by bjones1
Thanks David. Those were my thoughts as well. I just put a new roof on this one last year and I just dont like going through a roof for venting a fan.
I inspected a house 2 years ago that had all 3 bath fan vents connected to the main stink-pipe. Had another where 2 were ducted to the roof vents.
Use the soffit with pre-made louvered covers. They're fine.
Reply With Quote
  #12  
Old 2/15/08, 8:39 PM
bjones1 bjones1 is offline
Active Poster
 
Join Date: Mar 2005
Location: Coe Hill, On
Posts: 364
Send a message via MSN to bjones1
Please Note: bjones1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bathroom fan venting

Quote:
Originally Posted by dvalley
Use the soffit with pre-made louvered covers. They're fine.
Thanks David. That's what the owner bought.
Reply With Quote
  #13  
Old 2/15/08, 8:40 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bathroom fan venting

Quote:
Originally Posted by dvalley
Use the soffit with pre-made louvered covers. They're fine.
Ditto that..
Reply With Quote
  #14  
Old 2/15/08, 8:43 PM
bjones1 bjones1 is offline
Active Poster
 
Join Date: Mar 2005
Location: Coe Hill, On
Posts: 364
Send a message via MSN to bjones1
Please Note: bjones1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bathroom fan venting

Quote:
Originally Posted by bdoles2
Ditto that..
ditto the Thank-you
Reply With Quote
  #15  
Old 2/15/08, 9:21 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Red face Re: Bathroom fan venting

Quote:
Originally Posted by dvalley
There's nothing wrong with venting your bathroom fans into the soffit area.

Or do you mean down through the soffit using an outlet designed for under the soffit venting? I endorse this but not into the soffit/eave interior. "Into the soffit" has not been allowed up here for the last 2 code cycles, I believe.

A roof penetration would be susceptible to leaks.
I'm not afraid to vent through the roof. Just know how to seal it well. I installed a great roof vent manufacturered by Broan last fall......a bit expensive but if you want quality, be prepared to pay for it. I tell clients now that if they want a decent bath fan system,(powerful, quiet, controlled by a timer on a circuit different from the bath lights,and vented to the outside) be prepared to pay at least $325-$350 upwards +taxes.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Basement Bathroom Venting Question Sean M. Jeric Plumbing Inspections 4 3/20/07 11:56 PM
Venting a bathroom in a highrise condo Mark Ellison Inspecting HVAC Systems 1 10/8/06 11:00 PM
Bad Dryer and Bath Fan Venting Jkrt00 Inspecting HVAC Systems 3 3/13/06 11:07 PM
Bathroom Venting msimmons Inspecting HVAC Systems 7 2/21/06 6:12 PM


All times are GMT -4. The time now is 6:07 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts