Whats the spacing requirements for brick ties?
Foxe Smothers ( Owner / Inspector ) Pelican State Inspection Your Best Choice for Home Inspection in the Shreveport & Bossier City Area! www.PelicanState.Net www.ShreveportHomeInspector.net www.BossierCityHomeInspector.net foxe@pelicanstate.net LSBHI #10399 |
|
#2
|
||||
|
||||
|
|
|
#3
|
||||
|
||||
|
Hi to all,
I believe that the spacing minimum is every 18 inch vertical and 32 inch horizontal, or a minimum of every 2 3/4 sqft of area. The requirement is for more ties in areas of high wind or siesmic activity. Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#4
|
||||
|
||||
|
Table 1 in the above website shows for wood stud (and steel) 18 inches vertical and 32 inches horizontal (maximum) spacing. Sounds reasonable as you would want brick ties to be installed on wall studs, in this case every other stud (using a 16in. O.C. spacing for studs.) Gerry beat me to it but...out of the mouths of two or three witnesses....
|
|
#5
|
||||
|
||||
|
Brick tie spacing, Hmmm.
I believe it is 16" vertical and 24" horizontal or 24" vertical and 16" horizontal. Locate anchor sections to allow maximum verticall differential movement of ties up and down. Install additional anchors within 12" of openings and at intervals, not exceeding 8 inches, around perimeter. 24" horizontal spacing of anchors would occurr on 24" o. c. spacing of wall framing, and equally, 16" spacing would occurr on 16" framing. Marcel |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Why do brick spall? | mbryan | Exterior Inspections | 68 | 9/1/11 10:10 PM |
| Brick-Veneer Inspection Guide | jbowman | Exterior Inspections | 12 | 1/8/07 9:20 AM |
| Brick go boom??? | ccarrington | Exterior Inspections | 11 | 4/24/06 1:25 PM |
| No Brick Ties - Wall Buldge | Stew | Structural Inspections | 1 | 4/22/06 6:56 AM |
| Massachusetts Clay Brick Education | ajalowsky | Miscellaneous Discussion for Inspectors | 2 | 2/22/06 6:34 PM |