Default Brick veneer lintel

OK, maybe I am having a brain fart but why does the lintel appear short as in not going across the top of the door and window frame at this turn buckle balcony and continuing into the surrounding brick for support ?
No end dam either.

2006 build and from what I can tell the others are the same.

This is a Bank Owned Condo Building and obviously if this is an an issue the client is not about to pay for an SE ,so any suggestions? or am I being over concerned here?
[ATTACH][ATTACH]brick-veneer-lintel-lintel-brick-veneer-1024x768-.jpg[/ATTACH][/ATTACH]
Attached Thumbnails
brick-veneer-lintel-dsc004251-1024x768-.jpg   brick-veneer-lintel-lintel-brick-veneer2-1024x768-.jpg  
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/7/11, 3:28 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Brick veneer lintel

What type of construction is this Bob? Wood-frame, steel-frame, CMU or (as it appears) is the brick/masonry actually the wall, and not a veneer? Also, why would you refer an SE for a masonry issue?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 8/7/11, 4:06 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Brick veneer lintel

At first thought, a steel hanging lintel came to mind, but even those will have a typical 4" of bearing on each side of the opening.
The next possibility is a steel beam with a flat plate welded to the underside of it that extends out to pick up the brick, it's thickness might not have allowed it to bear on the brick.
Further information would be required and Jeff said.
Reply With Quote
  #4  
Old 8/7/11, 4:17 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Brick veneer lintel

Sorry out and about but as title states it is Brick veneer.
CONDO UNIT inspection.
I think Marcel has the right idea but look at this flashing
Most likely CMU behind it.
Reply With Quote
  #5  
Old 8/7/11, 4:40 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Brick veneer lintel

Bob, most brick veneers with CMU back up have loose steel lintels that bear on the brick on each side.
Some steel brick angle lintels are also bolted, but again bear on the brick on each side of the opeing.
I guess this one is wrong or a design that I have never encounter in commercial building to date.
Something has to support that angle.

Hanging steel lintel
Bolted steel lintel to CMU back-up
Loose steel lintel

How old was this building. Most codes now require a steel relieving angle every 24' in height.

Curious on this one Bob as to what supports it.
The flashing extends beyound the angle in one picture and not visible in the other. Was that the same window opening.?
Don't see weep holes in the soldier course either.
Reply With Quote
  #6  
Old 8/7/11, 4:43 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Brick veneer lintel

shelf angle



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #7  
Old 8/7/11, 4:49 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Brick veneer lintel

This might help also.

http://www.masonrysystems.org/inform...-shelf-angles/

Reply With Quote
  #8  
Old 8/7/11, 5:17 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Brick veneer lintel

Thanks guys, out e. Joying fests and as also in first post it is 2006.
Will add more tonight as I am still on it.
Reply With Quote
  #9  
Old 8/7/11, 5:24 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Brick veneer lintel

Missed the 2006, wow, would be interesting to see the design drawing on that one.
Reply With Quote
  #10  
Old 8/7/11, 10:09 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Brick veneer lintel

Quote:
Originally Posted by jpope View Post
What type of construction is this Bob? Wood-frame, steel-frame, CMU or (as it appears) is the brick/masonry actually the wall, and not a veneer? Also, why would you refer an SE for a masonry issue?
You are correct it would be a masonry issue.
Typed too fast to get the question posted on my way out.
Reply With Quote
  #11  
Old 8/7/11, 10:11 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Brick veneer lintel

Quote:
Originally Posted by mcyr View Post
Missed the 2006, wow, would be interesting to see the design drawing on that one.
There are a number that appear this way after going through building exterior shots.

Marcel it must be your first thought as far as lintel extension goes but wanted to hear it from someone else.
They must be using the CMU to hold up the lintel as if it was a shelf.

Do not always get enough wall structure or structure access during a condo examination as most of you guys know.The interior public garage was CMU with brick veneer which actually means nothing but supports that the entire building may be CMU as it is only 3+stories.

Last edited by belliott; 8/7/11 at 10:20 PM..
Reply With Quote
  #12  
Old 8/7/11, 11:18 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: Brick veneer lintel

That lintel should have carried over 4 inches in both directions.
Support the load and bond the brick plains.
It might be anchored into a metal beam work to carry the loads above it .
http://www.nachi.org/forum/f16/bridge-too-far-35125/
Attachment 47179
Ether or that situation should have been addressed.
Sometimes you can not carry the lintel over.
Foam doweling and expansive caulk are used to adsorb the expansions, contractions.
My 2 cents.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816

Last edited by ryoung7; 10/5/11 at 10:36 PM..
Reply With Quote
  #13  
Old 8/7/11, 11:26 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: Brick veneer lintel

Could not put a bore scope in the opening Bob?
Expansion joint.
Typical on iron work setup.
Could be a iron beam retro fit just for the baloney section.
If not then bad window installers.

Attachment 47180



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816

Last edited by ryoung7; 10/5/11 at 10:36 PM..
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/7/11, 11:55 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Brick veneer lintel

Robert that is not an expansion joint but is part of the turnbuckle support.
Also I have never seen an expansion joint near a corner before unless it served as a transition to face brick for instance.

I think this is covered with the information I have so far.
Reply With Quote
  #15  
Old 8/8/11, 8:31 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Brick veneer lintel

Being only a unit inspection I am going to suppose that the lintels are supported by something other than the window and door frames as there would be damage much worse than the mortar cracks Observed .
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Why do brick spall? mbryan Exterior Inspections 68 9/1/11 10:10 PM
Wind Mit? Brick Veneer rwelch Florida Inspectors 15 5/4/11 1:29 PM
Backfill on brick veneer bpaull Exterior Inspections 4 7/12/07 7:40 AM
Massachusetts Clay Brick Education ajalowsky Miscellaneous Discussion for Inspectors 2 2/22/06 6:34 PM