Default Bulge in stucco

Buldge in stucco is observed just above the bottom plate the entire lenth of the two exterior walls. Shotty framing? A horizontal crack is also observed above and below the buldge...see photos. The stucco is also very poor quality, basically disintigrates between my fingers, blows off wall in high winds, "stucco pellets" found all over the deck after wind storms...
Attached Thumbnails
bulge-stucco-dscn0218.jpg   bulge-stucco-dscn0217.jpg  

Last edited by kgrabowski; 6/22/11 at 3:37 PM.. Reason: no pics
Reply With Quote
Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/23/11, 3:00 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Bulge in stucco

You have stucco in Manitoba! There's 90% of the problem.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #3  
Old 6/23/11, 2:48 PM
Kerri L. Grabowski Kerri L. Grabowski is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Winnipeg, Mb
Posts: 32
Default Re: Bulge in stucco

Very funny..are you referring to our climate?
Reply With Quote
  #4  
Old 6/23/11, 4:10 PM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: Bulge in stucco

crumbling

sounds like it froze before it dried, and might have been painted before it was cured.



"I create controversy whether they like it or not"



Reply With Quote
  #5  
Old 6/25/11, 12:50 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Bulge in stucco

Settling of framing.
In multi-story buildings, at each floor structure you have a conjunction of framing members...studs from the floor below meeting top plate, plywood/OSB sub-floor, and a bottom plate meeting studs from the floor above. When they're framed, there is a small gap between each of these framing members. That's 4 gaps. As the framing members dry to an in-service condition, they each shrink a little. If they each shrink 1/16 inch, that's a total of 1/4-inch in about 16 inches. Stucco doesn't shrink at that rate.

So you have two different material systems that are attached firmly to each other with nails or staples that are moving (or not moving) at different rates and that's going to cause problems. When you look at the exterior of a multi-story stucco structure, always look at where you estimate the floor structure to be for this problem.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #6  
Old 6/25/11, 7:36 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Bulge in stucco

Quote:
Originally Posted by kgrabowski View Post
Very funny..are you referring to our climate?
I would say "Yes".

Stucco was developed and widely used in hot climates. From Wiki:

"In some parts of the United States (California, Arizona, New Mexico and Florida), stucco is the predominant exterior for both residential and commercial construction."
Reply With Quote
  #7  
Old 6/25/11, 2:49 PM
Kerry Kelly Kerry Kelly is offline
InterNACHI Member
 
Join Date: Aug 2005
Posts: 2
Default Re: Bulge in stucco

First I would determine if the system is "Hardcoat, Traditional Wire Lath",or is it EIFS or DEFS. The bulge could be caused by more than one action depending on the system. i.e. If it's EIFS or DEFS, was it meshed across the board, if DEFS was it meshed at the seams How old is the system and when did the bulge appear. It takes more than a surface view to determine the cause, suggestion; "A bulge was noted in the surface of the Stucco system at (where?), unable to determine the cause during a home inspection, suggest a Stucco Moisture-Scan be performed by a qualified Stucco Inspector."
Reply With Quote
  #8  
Old 6/25/11, 9:07 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: Bulge in stucco

Mr.Kelly is making good sense here.
#1 your hypothesis on the system.
#2 your hypothesis on the framing.
I see a gutter near by. I would be try to draw a conclusion from the 2 sides, interior and exterior..
Framing and exterior envelope.
A small crack in a hardcoat system would allow moisture in behind the framing.
Did you see evidence of moisture staining on the plaster inside the unit?
If not other conclusions can be drawn.
Good luck.
Not enough to go on.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #9  
Old 6/26/11, 7:59 PM
Kerri L. Grabowski Kerri L. Grabowski is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Winnipeg, Mb
Posts: 32
Default Re: Bulge in stucco

Nice try, but the stucco was installed in the middle of summer when it was blazing hot. Temperature was around 32C.
Reply With Quote
  #10  
Old 6/26/11, 8:02 PM
Kerri L. Grabowski Kerri L. Grabowski is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Winnipeg, Mb
Posts: 32
Default Re: Bulge in stucco

98% of all stucco here is hardcoat, and this one is hardcoat. No water penetration or evidence of moisture to interior of home. I believe it is the framing...
Reply With Quote
  #11  
Old 6/26/11, 8:04 PM
Kerri L. Grabowski Kerri L. Grabowski is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Winnipeg, Mb
Posts: 32
Default Re: Bulge in stucco

Downspout is not leaking. Bulge runs entire length of both walls. No evidence of moisture into interior of home.
Reply With Quote
  #12  
Old 6/26/11, 9:21 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: Bulge in stucco

Any more photos Mr.Grabowski?
Just a hypothesis.
Vertical load is causing the fasteners to fail and the plywood is coming away from the wall studding. There would have to be several factors at work.
#1: the ply wood laid horizontally. No staggering heights..
#2: fastener's breaking.
In the first photo it looks like that section of wall is also beginning to budge along a straight line. or is it my and or the photo?
Did you notice and truss uplift? Any door or window frames out of square on the side of the home?
Where the eve square, saw-fitting pulled away or compressed?
Any way to get a bore-scope in a whole?
Any more photos?



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #13  
Old 6/26/11, 10:01 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Bulge in stucco

Quote:
Originally Posted by kgrabowski View Post
Downspout is not leaking. Bulge runs entire length of both walls. No evidence of moisture into interior of home.
Did you see the same problem all the way around the building? Does it rain there during the summer?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 6/27/11 at 10:34 AM..
Reply With Quote
Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 6/26/11, 11:26 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: Bulge in stucco

Didn't see the expansion / control joint at the floor line.

Not important why as much as refer to a competent stucco contractor for repair.
Reply With Quote
  #15  
Old 6/27/11, 8:56 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: Bulge in stucco

Quote:
Originally Posted by kshepard View Post
Did you see the same problem all the way around the building? At other floors? Does it rain there during the summer?
Post #11 Kenton.
You seen this before?



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
There are over 12 types of stucco and EIFS bgromicko Exterior Inspections 0 12/19/09 7:04 PM
EIFS/Stucco mmerino Exterior Inspections 16 8/6/09 7:41 AM
Stucco Issues jfunderburk Exterior Inspections 19 3/7/09 8:15 AM
Bulge in stucco at 2nd story sspradling Structural Inspections 18 4/6/06 8:45 PM


All times are GMT -4. The time now is 6:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts