Default Crawl space venting?

Can anyone tell me if a crawl space with a concrete slab that is under 100 sqr. feet need venting.

I looked in the code book and it says 1 sqr. foot per 150 sqr. feet.
Reply With Quote
  #2  
Old 11/15/07, 9:07 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Crawl space venting?

Quote:
Originally Posted by prussell
Can anyone tell me if a crawl space with a concrete slab that is under 100 sqr. feet need venting.

I looked in the code book and it says 1 sqr. foot per 150 sqr. feet.
The latest trend is to no longer vent crawl spaces to the out side and I agree with this trend . .
.... Cookie
Reply With Quote
  #3  
Old 11/15/07, 9:08 AM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 2,825
Default Re: Crawl space venting?

Roy, do you know if there is a code for this in the IRC?
Reply With Quote
  #4  
Old 11/15/07, 9:25 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Crawl space venting?

Sorry I do not and I do not think we use the same codes .
http://www.fpl.fs.fed.us/documnts/te...entilation.pdf

One of many that do not recommend Venting .
.... Cookie Canadian OBC 9.32.2.1

Last edited by rcooke; 11/15/07 at 9:28 AM..
Reply With Quote
  #5  
Old 11/15/07, 9:30 AM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 2,825
Default Re: Crawl space venting?

Thanks Roy, good article
Reply With Quote
  #6  
Old 11/15/07, 9:32 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Crawl space venting?

Quote:
Originally Posted by prussell
Roy, do you know if there is a code for this in the IRC?
Peter:

Sometimes we have to challenge the code with newer research and the code guys with tact!! Most codes allow for innovation or else nothing would ever change. Sometimes though, it's hard to affect change if the code folks are not up to the newest research.

See:

http://www.advancedhomeenergy.com/Fi...ot_to_Vent.pdf

http://www.buildingscience.com/bsc/

http://www.housingzone.com/article/CA6253710.html
Reply With Quote
  #7  
Old 11/15/07, 9:48 AM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 2,825
Default Re: Crawl space venting?

I'm with you guys, here's my problem, I am building a 10X10 attached breezeway with a 28X24 garage and the building inspector red flagged the crawl space. I have to talk to him but I would never put vents in something like this, plus, when I frame the floor I install 1" rigid foam insulation between the joists then fiberglass, then the sub-floor. Once this is sealed, and by the way we poured concrete for a slab, but once this is sealed why would you need venting?

IRC states 1 sqr. foot per evry 150 sqr. feet, my interpretation on that is anything under 150 sqr. feet does not need venting, per code.

Thanks for the help, when I talk to him I'm going to push the issue.
Reply With Quote
  #8  
Old 11/15/07, 10:09 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Crawl space venting?

Quote:
Originally Posted by prussell
I'm with you guys, here's my problem, I am building a 10X10 attached breezeway with a 28X24 garage and the building inspector red flagged the crawl space. I have to talk to him but I would never put vents in something like this, plus, when I frame the floor I install 1" rigid foam insulation between the joists then fiberglass, then the sub-floor. Once this is sealed, and by the way we poured concrete for a slab, but once this is sealed why would you need venting?

IRC states 1 sqr. foot per evry 150 sqr. feet, my interpretation on that is anything under 150 sqr. feet does not need venting, per code.

Thanks for the help, when I talk to him I'm going to push the issue.
Print off a couple of the sheets listed above and give them to him so he too can learn.
Give him directions to this BB (http://www.nachi.org/forum) and tell him he is welcome to come on and see what a great group we are and would love to have him visit.
Let him know we love to trade information with all to help the industry . Even give him a copy of this letter so he too can see we really are an International association.

.. Cookie
Reply With Quote
  #9  
Old 11/15/07, 10:21 AM
Richard A. Hetzel Richard A. Hetzel is offline
Active Poster
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 596
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Crawl space venting?

The IRC requirés ventilation unless the crawl space is conditioned, meaning insulated, heated and mechanically ventilated. Any crawl space under 150 square feet in area still requires one square foot of ventilation free area. Failing to ventilate the space, one way or the other, is simply asking for trouble, in the form of mold and/or structural decay.
Reply With Quote
  #10  
Old 11/15/07, 10:25 AM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,078
Default Re: Crawl space venting?

Peter,

Sounds like (as you describe building it) it's not needed...

another website that I like...

http://www.crawlspaces.org/



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #11  
Old 11/15/07, 10:36 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Crawl space venting?

Quote:
Originally Posted by Richard A. Hetzel
The IRC requirés ventilation unless the crawl space is conditioned, meaning insulated, heated and mechanically ventilated. Any crawl space under 150 square feet in area still requires one square foot of ventilation free area. Failing to ventilate the space, one way or the other, is simply asking for trouble, in the form of mold and/or structural decay.
Sorry I am on the other side of the fence have seen more mould in vented crawl spaces in my area then unvented .
I recommend to all my clients that I think and from what I have read Crawl spaces are better left unvented to the out side .

... Cookie
Reply With Quote
  #12  
Old 11/15/07, 11:14 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Crawl space venting?

[quote=Richard A. Hetzel]The IRC requirés ventilation unless the crawl space is conditioned, meaning insulated, heated and mechanically ventilated. Any crawl space under 150 square feet in area still requires one square foot of ventilation free area. Failing to ventilate the space, one way or the other, is simply asking for trouble, in the form of mold and/or structural decay.[/quote]

Richard:
Read the stuff from Advanced Energy. They found lower RH's with a properly prepared space. Why would we vent?? to make it wetter??

This new trend has been running through researched results not anectdotal based sections of code for 15-20 years now!!
Reply With Quote
  #13  
Old 11/15/07, 11:19 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,987
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Crawl space venting?

Have seen too many crawlspaces vented to exterior that had more problems as a result.

Not venting is the way to go.
Reply With Quote
  #14  
Old 11/15/07, 12:15 PM
Andrew MacDonald's Avatar
Andrew MacDonald Andrew MacDonald is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Elgin, IL
Posts: 166
Default Re: Crawl space venting?

Treat the crawl like a basement. (you wouldn't leave your basement windows open, would you?)



Andrew MacDonald
MacDonaldPropertyInspections.com
InsightThermalDiagnostics.com

ITC/FLIR Certified Building Science Thermographer
ITC/FLIR Certified Level 1 Thermographer


Reply With Quote
  #15  
Old 11/15/07, 1:32 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 2,825
Default Re: Crawl space venting?

Well my site contractor told me that the red sticker meant it was OK, first time with this inspector, so I told him to forget the vent and back fill it.

I'm on the side of not venting.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Return air from crawl space WHI HVAC 8 5/1/07 8:36 AM
Crawl space in under house dnasser Structural 15 2/27/07 8:12 PM
No Crawl Space Ventilation dmccormick Structural 11 2/5/07 11:34 AM
Strange Duct in Crawl Space jfunderburk Structural 3 1/11/06 1:02 AM


All times are GMT -4. The time now is 2:28 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts