Default Deck Flashing

I found this on a new build. I did not observe any signs of traditional flashing. I have not seen anything like this behind a header board before.

Have any of you seen this before?
I
am wondering if it goes under siding to act as flashing?
I called it out and am waiting to see what the builder says.



Ashburn Inspections
724-516-1665

Last edited by mashburn; 2/6/08 at 6:29 AM..
Reply With Quote
  #2  
Old 2/4/08, 3:40 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Deck Flashing

Mike,

That's just wrong. I've seen many flashings installed the same exact way and it does nothing to protect the ledger board. I always red flag this type of install at the ledger board because moisture has a tendency to rot the ledger board which defeats the purpose of installing the flashing period, if it's installed behind the ledger.


It must tuck under the siding and then out and over the top of the ledger board. Being installed over the ledger will keep all moisture away from the house attachment to prevent rot. A rotted ledger will bring bad news.

See Image....
"click to enlarge"
deck-flashing-deck-ledger-flash.jpg

Last edited by dvalley; 2/4/08 at 3:43 PM..
Reply With Quote
  #3  
Old 2/4/08, 4:08 PM
mashburn's Avatar
mashburn mashburn is offline
InterNACHI Member
 
Join Date: May 2006
Location: Pittsburgh, PA
Posts: 286
Default Re: Deck Flashing

That is exactly what I wrote and thought. I just have never seen one like this. I am waiting for the builder to call and explain.



Ashburn Inspections
724-516-1665
Reply With Quote
  #4  
Old 2/4/08, 4:32 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Deck Flashing

Quote:
Originally Posted by mashburn
That is exactly what I wrote and thought. I just have never seen one like this. I am waiting for the builder to call and explain.
Michael,

When he calls you, ask him how the hell his flashing installation is going to convey moisture away from the top of the ledger board.
Name:  headbang.gif
Views: 5392
Size:  983 Bytes
I'm curious what his response is....
Reply With Quote
  #5  
Old 2/4/08, 4:42 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Deck Flashing

Looks like the bolts for the ledger to house connection might be lacking, too.

A couple of deck construction details are here and here



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #6  
Old 2/4/08, 5:04 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Deck Flashing

Here's a good graphic of what should be done. Just used it in a litgation case where, after only 8 months, an $800,000 house had severe rot in one wall facing horizontal rains off the North Atlantic ocean !!!

http://www.flash.org/resources/files/HGCC_Fact23.pdf
Reply With Quote
  #7  
Old 2/4/08, 5:05 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Deck Flashing

Quote:
Originally Posted by lkage
Looks like the bolts for the ledger to house connection might be lacking, too.

A couple of deck construction details are here and here
You could be correct, Larry. But how the hell would this deck without them?

And why the varied spacing on the floor joists?
Reply With Quote
  #8  
Old 2/4/08, 5:49 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Deck Flashing

I live in a secluded area where the contractors learn from the other contractors.
I have rarely (if ever) seen a properly flashed deck and nobody ever heard of kick-out flashing!!!
Reply With Quote
  #9  
Old 2/4/08, 6:26 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Deck Flashing

I think I like this better.







The sheithing is cut out to expose the box sill.










The Maine Deck Bracket is bolted to the sill With 1/2" bolts,washers on the inside.






A small slot is cut in the siding for the web of the bracket to go through.










The slot is small so as to leave no significant entry point for water or insects.










The slot is then caulked with silicone, caulking , sealing out moisture and insects.










The Maine Deck Brackets make a nice neat job on the building.










The brackets are ready to receive the deck framing.










The double ledger is used so that you can span the distance between brackets safely.








The deck is now framed and ready to cover.
1 1/2" spacing between decking and siding is recomended for an air space.

Yah, yah, I know, where are the joist hangers? ha. ha.
He is just not done yet.

Marcel

Reply With Quote
  #10  
Old 2/4/08, 6:51 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: Deck Flashing

What about attaching a deck structure to a home with brick veneer exterior walls? A free-standing deck structure is typically recommended for this type of wall construction. Also, with the newer treated lumber, standard metal flashing cannot be placed due to the copper treatment of the decking material. I believe a rubber membrane flashing is now available to be used as flashing for treated lumber ledgers.




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #11  
Old 2/4/08, 7:08 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Deck Flashing

Stay tuned, we are building some decks right now on some condos and I'll try to get some proper deck flashing pictures to post.

PS don't forget, with most PT today we need to use copper flashing.
Reply With Quote
  #12  
Old 2/5/08, 6:48 AM
mashburn's Avatar
mashburn mashburn is offline
InterNACHI Member
 
Join Date: May 2006
Location: Pittsburgh, PA
Posts: 286
Default Re: Deck Flashing

The Lags were there and OK. The guy just could not do the deck flashing or siding very well. Take a look see.

Thanks you gentleman for your prompt respones.



Ashburn Inspections
724-516-1665

Last edited by mashburn; 5/7/09 at 7:19 AM..
Reply With Quote
  #13  
Old 2/5/08, 7:12 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Deck Flashing

Quote:
Originally Posted by dvalley
You could be correct, Larry. But how the hell would this deck without them?
Well, as an example, this 16 foot long ledger had 4 bolts only and the joists were spanning 12 feet. That was insufficient but holding the deck up temporarily.


I forgot about those brackets, Marcel. I like that method too.
Attached Thumbnails
deck-flashing-example.jpg  



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #14  
Old 2/8/08, 8:43 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Deck Flashing

Well like I said I would post some pictures of deck flashing so here goes, sorry about the quality but this winter will not give us a break.

I'll post pictures of the front deck where the ledger board has to be connected directly to the foundation.
Attached Thumbnails
deck-flashing-dscn2891-small-.jpg.JPG
Views:	181
Size:	59.1 KB
ID:	18436   deck-flashing-dscn2892-small-.jpg.JPG
Views:	284
Size:	45.3 KB
ID:	18437   deck-flashing-dscn2893-small-.jpg.JPG
Views:	809
Size:	59.4 KB
ID:	18438  
Reply With Quote
  #15  
Old 2/12/08, 6:06 AM
mashburn's Avatar
mashburn mashburn is offline
InterNACHI Member
 
Join Date: May 2006
Location: Pittsburgh, PA
Posts: 286
Default Re: Deck Flashing

It would be kinda hard to miss that flashing. BTW the builder never contacted me. He told the buyer, "Well we had some problems with da subs on dat one, I'm gonna fix it." That was it, no problems. I wanted to speak with him, he never called.

Again, Thank you all!!



Ashburn Inspections
724-516-1665
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Max load allowed on 2x2 ledger bking Structural Inspections 4 12/23/07 2:05 PM
Deck flashing question scosta Exterior Inspections 7 10/15/07 11:21 PM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 8:10 AM
Deck flashing? wcruz General Inspection Discussion 1 7/21/06 10:37 PM


All times are GMT -4. The time now is 10:06 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts