Default Deck Inspection Contradiction

For those with Inachi Deck Inspection Book, should recommendations be made to deem this ledger attatchment unaceptable;



When the 2009 IRC says it is one of the accepted methods?



Washer spacers is widely used around here and people frequently ask me if this is the way.
I usually tell them that my preferred method is the lag screw method with flashing.

I just want to make sure that these calls don't get anyone in trouble.
Should not be called out as a defect.
But in lieu, just a recommendation that differs from what is acceptable to the minimum standards of the code.
Reply With Quote
Need a home inspection in Connecticut? Check out InterNACHI's listing of Connecticut certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/14/11, 4:27 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Deck Inspection Contradiction

Marcel, I virtually never see the "washer/spacer" method. Personally I never cared for it. My preferred method is the lag/flashing method also. Thanks for the reminder. It's been a long time since seeing the washers. Good reminder.
Reply With Quote
  #3  
Old 5/14/11, 4:55 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Deck Inspection Contradiction

Good advice Marcel.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 5/14/11, 5:04 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Deck Inspection Contradiction

What bothers me more is when attached to brick veneer you are not supposed to over tighten the lag bolts which to me is almost the same deal as the washers in that you are not getting as secure a connection to the wall.
Am I wrong to think that ?
Reply With Quote
  #5  
Old 5/14/11, 5:09 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Deck Inspection Contradiction

Although allowed by the Code, they also recommend adding a deck beam closes to the connection to take care of exactly what you are saying Bob.
So pretty much, it is only holding the deck stable and the deck is basically free standing. That is in the 2009 update also.
Reply With Quote
  #6  
Old 5/14/11, 5:25 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Deck Inspection Contradiction

Must be why I see the words below in Prescriptive Residential Wood
Deck Construction Guide
Based on the 2006 International Residential Code (PDF)


PROHIBITED LEDGER ATTACHMENTS
Attachments to exterior veneers (brick, masonry, stone)
and to cantilevered floor overhangs or bay windows are
prohibited (see Figures 17 and 1. In such cases the
Figure 17: No Attachment to or Through
Exterior Veneers (Brick, Masonry, Stone)
deck shall be free-standing (see FREE-STANDING
DECKS).
Reply With Quote
  #7  
Old 5/14/11, 6:23 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Deck Inspection Contradiction

Unless the washers are hot dip galvanized and protected with flashing
corrosion will occur and therefore regardless of the "2009 building code" rust will penetrate all the way through to the hot dipped leg screws or bolts.

Here we go again with the recommendations that will compromise safety.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #8  
Old 5/14/11, 6:27 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Deck Inspection Contradiction

Bingo, you can now collect your prize.

That is exactly why the Code is the bear minimum of standards.
I would never recommend that attachment.
And that is why Inachi did not either in their book of How to Inspect Decks.
Now we know the whole story.
Reply With Quote
  #9  
Old 5/14/11, 6:31 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Deck Inspection Contradiction

What is my prize!



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #10  
Old 5/14/11, 6:36 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Deck Inspection Contradiction

Well typically when someone wins a prize, I let Jeff Jonas show them what they won, But my recommendation would be to just be content with the fact you won.
Reply With Quote
  #11  
Old 5/14/11, 6:49 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Deck Inspection Contradiction

Speaking of decks I was talking to a contractor today and he said one of the city inspectors is recommending new decks to have 4 inches from the center of spindle to the center of the next spindle. That is why I see some new decks with spacing less than a 2 inch ball can fit through.
Say it isn't so.
I think he just doesn't know or miss read the RBC.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #12  
Old 5/14/11, 6:59 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Deck Inspection Contradiction

Quote:
Originally Posted by kwood View Post
Speaking of decks I was talking to a contractor today and he said one of the city inspectors is recommending new decks to have 4 inches from the center of spindle to the center of the next spindle. That is why I see some new decks with spacing less than a 2 inch ball can fit through.
Say it isn't so.
I think he just doesn't know or miss read the RBC.
Talking through his hat, but the AHJ has the final word. I would ask to see the written code or amendment to the code that he is basing his decision on for the jurisdiction he is in.
Reply With Quote
  #13  
Old 5/14/11, 8:28 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Deck Inspection Contradiction

Quote:
Originally Posted by mcyr View Post
Well typically when someone wins a prize, I let Jeff Jonas show them what they won, But my recommendation would be to just be content with the fact you won.
You're no fun Marcel!
Reply With Quote
Need a home inspection in Connecticut? Check out InterNACHI's listing of Connecticut certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/14/11, 8:32 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Deck Inspection Contradiction

Reply With Quote
  #15  
Old 5/14/11, 11:20 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: Deck Inspection Contradiction

InterNACHI is correct. The IRC is incorrect.

The reasoning is quite simple: Using a lag bolt to hold a ledger board away from the band joist is, in essence, using the lag bolt as a cantilever. Lag bolts are not designed to be used as cantilevers. They simply don't have the "shear" strength to be misused like the IRC depicts.

Too few washers... and the washers simply squish between the wood leaving no space for water to pass. At the point where you have enough washers to create space between the wood... you're relying on the cantilevered shear strength of the lag bolt to carry the load of the deck and it's occupants.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17

Last edited by gromicko; 5/14/11 at 11:38 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Using the Prescriptive Residential Deck Construction Guide mcyr Exterior Inspections 0 7/21/09 7:10 PM
Check The Deck wdevries Canadian Inspectors 1 7/9/08 2:00 PM
Another deck Collapse rcooke Canadian Inspectors 11 3/30/08 8:03 AM
Illinois State Chapter of InterNACHI DECK FRAMING/CONSTRUCTION COURSE ksitzes Miscellaneous Discussion for Inspectors 6 3/4/08 5:47 PM
Max load allowed on 2x2 ledger bking Structural Inspections 4 12/23/07 2:05 PM


All times are GMT -4. The time now is 6:19 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts