Default Deck supports

Would you say these supports were proper for this deck? 4X4 post 2X 12 toed nail in? Large notch in ledger board.
Attached Thumbnails
deck-supports-improper-support-deck-1.jpg   deck-supports-improper-support-deck-2.jpg   deck-supports-ledger-board-notched.jpg  
Reply With Quote
  #2  
Old 2/16/09, 6:26 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,172
Default Re: Deck supports

Without more info, or pictures...

No, no, hmmm... no!
Reply With Quote
  #3  
Old 2/16/09, 6:36 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,607
Default Re: Deck supports

I agree Jeffrey, no and no.


http://www.cbchomeinspect.com/upload...on%20Guide.pdf Start with page 7.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 2/16/09, 6:39 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,172
Default Re: Deck supports

Quote:
Originally Posted by ccurrins View Post
I agree Jeffrey, no and no.


http://www.cbchomeinspect.com/upload...on%20Guide.pdf Start with page 7.
Cool beans... glad you posted the link to the guide. I was searching, but was interrupted.
Reply With Quote
  #5  
Old 2/16/09, 7:20 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Deck supports

House is eight years old, in Johnson County, KS, it sure was not built to the Johnson County guidelines.
Reply With Quote
  #6  
Old 2/17/09, 9:43 AM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Deck supports

There are other acceptable post to beam connections besides the one on Page 7, so don't be thinking that's the ONLY acceptable connection.
Reply With Quote
  #7  
Old 2/19/09, 9:51 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Deck supports

Post/girder connection is poor, recommend correction.

I don't have a problem with the notch. Those are 1/2" lag screws through the ledger into the home rim joist. If they're on 24" centers, as is typical, it's not going anywhere. You could cut that ledger all the way through and as long as it had 2 solid lags supporting no more than two joists (and no point loads), it wouldn't go anywhere.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #8  
Old 2/26/09, 6:30 AM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: Deck supports

The 2x horizontal support beam is not properly secured to the 4x4 posts to prevent lateral movement.




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #9  
Old 2/26/09, 6:43 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Deck supports

Quote:
Originally Posted by kshepard View Post
Post/girder connection is poor, recommend correction.

I don't have a problem with the notch. Those are 1/2" lag screws through the ledger into the home rim joist. If they're on 24" centers, as is typical, it's not going anywhere. You could cut that ledger all the way through and as long as it had 2 solid lags supporting no more than two joists (and no point loads), it wouldn't go anywhere.
I agree with Kenton.

http://buildingcodes.jocogov.org/doc...eck%20Book.pdf
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Check The Deck wdevries Canadian Inspectors 1 7/9/08 2:00 PM
Another deck Collapse rcooke Canadian Inspectors 11 3/30/08 8:03 AM
Illinois State Chapter of InterNACHI DECK FRAMING/CONSTRUCTION COURSE ksitzes General Inspection Discussion 6 3/4/08 5:48 PM
Max load allowed on 2x2 ledger bking Structural Inspections 4 12/23/07 2:05 PM


All times are GMT -4. The time now is 10:09 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts