InterNACHI


Go Back   InterNACHI Inspection Forum > Specific Inspection Topics > Exterior Inspections

Notices

Exterior Inspections Contains discussions about the exterior portion of a home inspection. This includes roofs, gutters, downspouts, decks, patios, windows, etc.

 
Reply
 
LinkBack Thread Tools
  #1  
Old 11/14/07, 8:36 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Dryer vents through roofs

Often, when I see a dryer vent vertically out the roof, the vent termination cap has a wide grill and a cap over it. Often, they are clogged or partially clogged.

The 2006 IRC states: "Exhaust duct terminations shall be equipped with a backdraft damper. Screens shall not be installed at the duct termination."

If you are familiar with what I'm talking about, those vents through roofs, do you think they meet the definition above? (To me a damper is a flap device and I don't think they have them.)

Photo: Dryer vent is right side of plumbing vent.

dryer-vents-through-roofs-111407-017-small-.jpg.jpg
Views:	1028
Size:	36.3 KB
ID:	16066



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #2  
Old 11/14/07, 9:17 PM
Ed Fako's Avatar
Ed Fako Ed Fako is offline
Active Poster
 
Join Date: Feb 2007
Location: NW Chicago Suburbs
Posts: 199
Please Note: Ed Fako is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dryer vents through roofs

Did it look similar to this?



It happens frequently, when the vent does not get cleaned. I would imagine that this could be a hazard due to gasses or fire.

Ed
Reply With Quote
  #3  
Old 11/14/07, 10:33 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dryer vents through roofs

Quote:
Originally Posted by Ed Fako
Did it look similar to this?



It happens frequently, when the vent does not get cleaned. I would imagine that this could be a hazard due to gasses or fire.

Ed
Ed:

I use this in the appendix of my report:

The exhaust duct for the dryer should be metal. Be sure to clean the lint from the duct on a regular basis as it can restrict exhaust air flow leading to overheating in the dryer. Recent statistics from one year in the United States are instructive as to how important the two previous items can be:

DRYERS- Fires caused by: 14,600 ________Deaths: 20 __________Damage: $87 millions

Last edited by Brian A. MacNeish; 11/14/07 at 10:39 PM..
Reply With Quote
  #4  
Old 11/14/07, 10:35 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dryer vents through roofs

Quote:
Originally Posted by jfunderburk
Photo: Dryer vent is right side of plumbing vent.
That vent looks like it was made as a bathroom roof vent and has a mis-applied use!!
Reply With Quote
  #5  
Old 11/14/07, 10:49 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,611
Default Re: Dryer vents through roofs

http://www.rd.com/content/openConten...ontentId=17536

http://www.greatinspector.com/faq-clothes-dryer.html

Some info .
...... Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #6  
Old 11/14/07, 10:59 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dryer vents through roofs

Quote:
Originally Posted by rcooke
From this site:

Dryer vent pipes vented out through the roof must be vented through a special "dryer roof vent". (make certain that the screen has been removed) Dryers cannot be vented through the regular square type roof vent. These vents due to their design, get clogged with lint and are considered a fire hazard.

If it was a "special" dryer roof vent, why would it have a screen to remove in the first place or is the unit a converted sidewall kit?
Reply With Quote
  #7  
Old 11/15/07, 9:59 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Dryer vents through roofs

If it's got a screen and lint is moving through the dryer vent, the screen is likely to get clogged whether it's on the roof or wall. Seems like accessiblity for cleaning purposes is the issue.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #8  
Old 11/17/07, 1:08 PM
dhelm's Avatar
dhelm dhelm is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Bellingham, Wa
Posts: 704
Default Re: Dryer vents through roofs

Dryer vents should not go vertical at all. Dryer blower motors aren't designed to force exhaust upward and will have a shortened life. Most manufacturers, that I have seen, are pretty clear about this.



Helm Home Inspection
David Helm, Owner/Inspector
http//www.helmhomeinspections.com
Reply With Quote
  #9  
Old 11/17/07, 2:24 PM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dryer vents through roofs

Quote:
Originally Posted by dhelm
Dryer vents should not go vertical at all. Dryer blower motors aren't designed to force exhaust upward and will have a shortened life. Most manufacturers, that I have seen, are pretty clear about this.
Can you give me an example of a manufacturer with this requirement?

Thanks
Reply With Quote
  #10  
Old 11/17/07, 2:56 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,611
Default Re: Dryer vents through roofs

Quote:
Originally Posted by dhelm
Dryer vents should not go vertical at all. Dryer blower motors aren't designed to force exhaust upward and will have a shortened life. Most manufacturers, that I have seen, are pretty clear about this.
I can not find any information regarding this .
Some of the corcerns with roof venting is to make sure you insu;ate it in the attic if you live in a cold area .
Through the roof could be harder to clean the pipes
( We all of course clean our pipe yearly Correct ) you need a proper spring vent no screen on it .
Remember support the vent pipe in the attic.
.....Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #11  
Old 11/17/07, 10:48 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dryer vents through roofs

Quote:
Originally Posted by dhelm
Dryer vents should not go vertical at all. Dryer blower motors aren't designed to force exhaust upward and will have a shortened life. Most manufacturers, that I have seen, are pretty clear about this.
Ther vast majority of dryers in our area are located in full 8' deep basements. to get to the rim joist they all have to blow air up at least 7-8 feet to vent to the outdoors.

My own dryer (almond colour) has been blowing up the 7'-8' for 23 of its 33 years!! And it doesn't seem to want to break badly enough that I can't repair it!! The joke with my wife is that when I die she can buy a new dryer with the insurance $$$; until then we're using what works. (so Scottish!!)
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dryer sheets potential hazard badair Miscellaneous Discussion for Inspectors 15 7/9/11 2:39 PM
What is a 'condenser' dryer ?? rcooke Canadian Inspectors 9 9/9/07 7:02 PM
dryer and bathroom vents aweston Miscellaneous Discussion for Inspectors 4 10/22/06 11:12 AM
Dryer lint filter senomoto Miscellaneous Discussion for Inspectors 6 5/14/06 10:01 AM
Bad Dryer and Bath Fan Venting Jkrt00 Inspecting HVAC Systems 3 3/13/06 11:07 PM


All times are GMT -4. The time now is 1:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts