Post Efflorescence patterns to diagnose water intrusion

Around here, we have had 3 relatively warm and wet winters. Most masonry drying occurs during the windter months, when there are 10 - 15 days of single digit temps. This allows heat to flow out from the masonry, and the water in the masondy follows.

Because of this lack of drying time, we have a number of efflorescence teaching examples.

1) Three year old building. Brick veneer with cinder block structure. Notice how the efflorescence displays below the stone. No flashing under the stone cap. Water goes through the stone and vertical mortar joints.

2) Detail of proper single wythe CMU walls. Flashing must be in place above joist pockets with weep wicks. Above door and window lintals, similar flashing is needed with weep wicks. The lintal / brick space MUST NOT be grouted or caulked. It they are, this traps the water in the wall above the window and it leaks into the top of the window interior.

3) Notice how all the efflorescence is below the stone window sills and the stone parpet wall coping? Wonder why? Around here, mo one flashes properly. The result? Many buildings with water intrusion, mold and even rotting wooden floor trusses (the grout the joist pockets). Am involved with litigation inspections on 6 such buildings and 3 have already been torn down (rotted floor joists, mold) at the City's order. But hey, it's good money for me. Even have a new template for it, mostly boiler plate because the issues are almost always the same.

4) Lastly, got to see the spacing between the cinder block structural wall and the brick veneer. Where the efflorescence is, the required 1' gap between the walls was filled with mortar. The "masons" (and I use the term loosely) didn't bother to scrape the mortar off when laying the brick. Mortar bridges the gap between the walls. Any mositure going down the inside of the brick hits these bridges and seeps inward and outward. Moisture levels in the CMU, on the interior, was also elevated in these areas.

Put this together with themal imaging and mold sampling and you have a whole cottage industry for HIs.

Hope this helps;
Attached Thumbnails
efflorescence-patterns-diagnose-water-intrusion-dscf3467.jpg   efflorescence-patterns-diagnose-water-intrusion-cmu-single-wythe-flash-1.jpg   efflorescence-patterns-diagnose-water-intrusion-efflorescence-new-building.jpg   efflorescence-patterns-diagnose-water-intrusion-dscf2732.jpg  



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!

Last edited by wdecker; 4/24/09 at 8:30 PM.. Reason: Adding Detail
Reply With Quote
Find an InterNACHI certified West Virginia Home Inspector (and anywhere else in North America)
  #2  
Old 4/25/09, 1:54 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,486
Send a message via ICQ to kshepard
Default Re: Efflorescence patterns to diagnose water intrusion

Will, do you have any idea of what moisture migration rates are possible through stone or masonry?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #3  
Old 4/25/09, 10:12 AM
William J. Decker's Avatar
William J. Decker William J. Decker is online now
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,524
Default Re: Efflorescence patterns to diagnose water intrusion

Quote:
Originally Posted by kshepard View Post
Will, do you have any idea of what moisture migration rates are possible through stone or masonry?
I guess I don't understand the question.

In our area, masonry walls are, usually, double wythe. Cinder block structural wall with a brick or split faced block veneer. Many of them built in the last 15 years with improper or no flashing.

I do MATS testing for absorbancy. Also, many don't use the proper mortar for the split faced block.

Care to make your question more specific?



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #4  
Old 4/25/09, 12:15 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,486
Send a message via ICQ to kshepard
Default Re: Efflorescence patterns to diagnose water intrusion

Quote:
Originally Posted by wdecker View Post
Water goes through the stone and vertical mortar joints.
How fast can water move through stone or masonry?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #5  
Old 4/25/09, 2:31 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,350
Default Re: Efflorescence patterns to diagnose water intrusion

In order to be accurate with that question Kenton, tests would have to be performed.

Using this method and equipment as shown here;
http://www.prginc.com/Masonry/rilem.html

Vertical Rilem Tubes — Regular
Used to measure absorption of a vertical masonry surface.



Because masonry building materials are porous, they are all somewhat permeable to water. The interior structure of a masonry material is a system of fine interconnected pores. Wetting by liquid water involves capillary conduction (suction) through this pore system, proceeding along both vertical and horizontal pathways. Vertical transport occurs when water enters as ground water at the base of a structure or as rain water through leaking gutters. Penetration of driving rain into wall surfaces results in horizontal transport. (Under actual conditions, the amount of rain penetration depends on prevailing wind conditions as well as on the composition and condition of the exposed surface.)
When liquid water comes into contact with a masonry surface, wetting proceeds through the material as a front. Accurate measurements of the advance of this wetting front made on a variety of masonry building materials have demonstrated that the characteristic wetting rate and pattern of each material are directly related to its capillary structure and port size distribution. In fact, rate constants have been measured for brick, limestones and other masonry materials. RILEM Test Method 11.4 provides a simple method for measuring the volume of water absorbed by a material within a specified time period.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #6  
Old 4/25/09, 5:43 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,486
Send a message via ICQ to kshepard
Default Re: Efflorescence patterns to diagnose water intrusion

I guess so, Marcel. In addition to the porosity of the material, you 'd be dealing with moisture, temperature and pressure gradients.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #7  
Old 4/25/09, 7:55 PM
William J. Decker's Avatar
William J. Decker William J. Decker is online now
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,524
Default Re: Efflorescence patterns to diagnose water intrusion

What I did, when I first got my MATS tubes (same as Marcel's, but different name) was do sime test of my own. Got a selection of brick and stone and did my own tests. Also bought different types of mortar that are used around here (called a local mason for advice. BTW, he was VERY interested in the results!) and built some test walls (might be a good project for you Ken, I know that you are always messing around with Nick and Ben )

If anyone has some published results, please post.

One building I inspected (for the condo association) had problems. Built in 1929, three story courtyard building on the Lake. The east and south sides were directly exposed to the lake and wind driven rains. The building had recently had all their lintels replaced. The mason even installed metal flashing between the lintels and the overlying brick. The brick above the lintels were soldiers and were removed to replace the lintels, then reinstalled. The condo association was getting water entering the building at areas above the lintels (confirned by moisture meter and thermal imaging).

Did some MATS tests of areas where the original brick and mortar were and compared them to the replaced soldiers (they used the original bricks and just reinstalled them). The replaced brick absorbed moisture twice as fast. Seems that the original mortar was a lime putty mixture while the replaced brick was reinstalled using a standard N type mortar. The N type mortar was absorbing water much faster.

Had the mason's come back and showed them the results and how I did the test. They removed the soldiers from 3 of the window lintels and reinstalled them with like putty. Sure enough, those three windows didn't leak anymore.

It was fun to experiment, and to get paid to do so.

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #8  
Old 4/25/09, 10:22 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,350
Default Re: Efflorescence patterns to diagnose water intrusion

Sounds like you had some fun there Will.

If you look at this here;

M A S O N W O R K It denotes all types of Masonry Mortar Cements used today.
Going from strongest to weakest in strength.

A good article here on the different types of mortars, and interesting reading for those interested in Masonry.
http://irc.nrc-cnrc.gc.ca/pubs/fullt...tar/paper9.pdf

I also have a few comments on Initial Rate of Absorption (IRA);

The flexural bond strength of masonry cement mortar changes more with brick IRA than that of portland cement/lime and mortar cement mortars.

Mortar cements develop flexural bond strengths equivalent to those of portland cement/lime mortars with low IRA brick.

Flexural bond strength of low IRA brick improves as mortar water retention decreases.

Flexural bond strengths of very low IRA brick can equal or exceed those of higher IRA brick with proper selection of materials and Types.

Water penetration resistance is not related to flexural bond strength.

Walls of low IRA brick can be built to have not water penetration.

For walls of uncored brick and excellent workmanship water penetration resistance is directly related to brick density and inversely related to brick absorptions.

Any of this make sense to you?

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #9  
Old 11/10/09, 12:54 AM
William J. Decker's Avatar
William J. Decker William J. Decker is online now
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,524
Default Re: Efflorescence patterns to diagnose water intrusion

Ok. Published paper and here is the abstract.

http://deckerhomeservices.com/2009-082%20Decker.pdf

But, I had to do it myself.

Go figure



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #10  
Old 11/10/09, 1:38 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2009
Location: Chicago
Posts: 1,044
Default Re: Efflorescence patterns to diagnose water intrusion

Interesting article.
I am surprised about the lakeside building.
How far up did he place the metal flashing in relation to how far up new masonry was put in place.?

I would love to see that situation in a diagram.
Reply With Quote
  #11  
Old 11/10/09, 11:29 AM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,896
Default Re: Efflorescence patterns to diagnose water intrusion

Excellent paper Will. It was very educational. Thanks for sharing it with us!

BTW, on page 5 you reference photo 115, instead of photo 15.
Reply With Quote
  #12  
Old 11/10/09, 12:01 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,350
Default Re: Efflorescence patterns to diagnose water intrusion

Nice article Will, and this should add to what causes efflorescence;

http://rds.yahoo.com/_ylt=A0geu46vjP...otes/TN23a.pdf




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #13  
Old 11/12/09, 12:18 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,486
Send a message via ICQ to kshepard
Default Re: Efflorescence patterns to diagnose water intrusion

I swan... the more I learn, the less I know.

Portland Cement Association also says soluble salts

Salt chrystals... that's what I had thought all this time. Then today I was at a plant where they manufacture concrete tiles and was told something different by their engineer.

Calcium hydroxide. When the water and the cement mix together the result is calcium silicate hydrate. a by product is calcium hydroxide which is basically unhydrated cement.

Calcium hydroxide is leached to the surface by moisture moving through the porous masonry and upon coming into contact with carbon dioxide it turns white.


"The binding quality of portland cement paste is due to the chemical reaction between the cement and water, called hydration. Portland cement is not a simple chemical compound, it is a mixture of many compounds. Four of these make up 90% or more of the weight of portland cement: tricalcium silicate, dicalcium silicate, tricalcium aluminate, and tetracalcium aluminoferrite. In addition to these major compounds, several other play important roles in the hydration process. Different types of cement contain the same four major compounds, but in different proportions.

The cement in concrete needs water to hydrate and harden. Even though the chemical reactions may be complete at the surface of the concrete, the chemical reactions at the interior of the concrete take much longer to complete. The strength of the concrete keeps growing as long as the chemical reactions continue.

When water is added to cement, the chemical reaction called hydration takes place and contributes to the final concrete product. The calcium silicates contribute most to the strength of concrete. Tricalcium silicates are responsible for most of the early strength (first seven days)."

The original dicalcium silicate hydrates, which form more slowly, contribute to the strength of concrete at later stages.

http://chemistry.suite101.com/article.cfm/the_chemistry_of_concrete

http://www.cement.org/basics/concretebasics_lessonfive.asp

This one just calls it "minerals"




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289


Last edited by kshepard; 11/12/09 at 12:35 PM..
Reply With Quote
Find an InterNACHI certified West Virginia Home Inspector (and anywhere else in North America)
  #14  
Old 11/12/09, 2:28 PM
Neal L. Yacoub Neal L. Yacoub is offline
InterNACHI Member
 
Join Date: Aug 2009
Location: Brantford, Ontario
Posts: 16
Default Re: Efflorescence patterns to diagnose water intrusion

So when I see efflorescence what type of recommendation should I make to properly cover my butt?
Reply With Quote
  #15  
Old 11/12/09, 2:52 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,486
Send a message via ICQ to kshepard
Default Re: Efflorescence patterns to diagnose water intrusion

Quote:
Originally Posted by nyacoub View Post
So when I see efflorescence what type of recommendation should I make to properly cover my butt?
Since it's a sign of moisture intrusion you should comment on the fact that there has been intrusion and look for evidence that it's ongoing. If it appears that intrusion is ongoing you should recommend locating the source (if you can't locate it yourself) and recommend correction.

The potential probelms to mention are human health: from excessively high levels of mold spores in indoor air, rust of metal components, wood decay and foundation undermining.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Slab efflorescence jfunderburk Structural 4 2/2/09 2:35 PM
efflorescence in soil? Brad Muise Interior 4 1/2/08 10:43 PM
Do you call out efflorvesence gbrasseur Misc. Discussion 10 4/13/07 1:51 AM
Diagnosing Attic Performance by Snow- and Frost-Melt Patterns phinsperger Exterior 0 12/11/06 3:03 PM


All times are GMT -4. The time now is 10:51 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts