Can someone help me out, I would like to know exactly how the 2000 IBC code reads for egress windows.

I was under the assumption that all bedrooms require egress window, my question is, is it limited to bedrooms or all habitable rooms?
Reply With Quote
  #2  
Old 5/16/07, 1:43 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,352
Default Re: Egress code

Are you sure you mean the IBC? I don't know that the IBC addresses this particular topic. Wouldn't the IRC be more applicable?
Reply With Quote
  #3  
Old 5/16/07, 1:44 PM
afrost afrost is offline
Active Poster
 
Join Date: Jan 2007
Location: Conway, NH
Posts: 356
Please Note: afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Egress code

Quote:
Originally Posted by prussell
Can someone help me out, I would like to know exactly how the 2000 IBC code reads for egress windows.

I was under the assumption that all bedrooms require egress window, my question is, is it limited to bedrooms or all habitable rooms?
sorry, i don't know the answer pete, but if you publicly thank someone you will probably get 4 pages of response. yikes-o-pizza!
Reply With Quote
  #4  
Old 5/16/07, 2:14 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 3,118
Default Re: Egress code

Quote:
Originally Posted by mboyett
Are you sure you mean the IBC? I don't know that the IBC addresses this particular topic. Wouldn't the IRC be more applicable?
Yes, the IRC
Reply With Quote
  #5  
Old 5/16/07, 2:21 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,352
Default Re: Egress code

Well, I don't have the 2000 IRC but would the 2003 IRC suffice?
Reply With Quote
  #6  
Old 5/16/07, 2:29 PM
ckratzer ckratzer is offline
Active Poster
 
Join Date: Mar 2005
Posts: 256
Please Note: ckratzer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Egress code

Quote:
Originally Posted by prussell
Can someone help me out, I would like to know exactly how the 2000 IBC code reads for egress windows.

I was under the assumption that all bedrooms require egress window, my question is, is it limited to bedrooms or all habitable rooms?
Just some of what it says but enough to answer your question...

R310.1 Emergency escape and rescue required.Basements with habitable space and every sleeping room shall have at least one openable emergency escape and rescue opening.Where basements contain one or more sleeping rooms,emergency egress and rescue openings shall be required in each sleeping room,but shall not not be required in adjoining areas of the basement.

It goes on to give spec.s on demension minimums.
Reply With Quote
  #7  
Old 5/16/07, 2:39 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,352
Default Re: Egress code

Here's a scan of 2003 IRC R310:
Egress.PDF
Reply With Quote
  #8  
Old 5/16/07, 3:04 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 3,118
Default Re: Egress code

Thanks guys, I am building a attached 2 car garage with a family room above it and the inspector want a egress window up there. I have never come across a situation where a family room needs egress window.

Could there be something I'm missing in the life saftey codes?
Reply With Quote
  #9  
Old 5/16/07, 3:19 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 197
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Egress code

Quote:
Basements with habitable space and every sleeping room shall have at least one openable emergency escape and rescue opening.Where basements contain one or more sleeping rooms,emergency egress and rescue openings shall be required in each sleeping room,but shall not not be required in adjoining areas of the basement.
My unfinished basement has small windows painted shut. But it does have two doors: one up the stairs to my kitchen, and another directly out to my back garden.

If I finish the basement, are there any restrictions on what types of rooms I can have in this current state i.e. are bedrooms allowed? or a living area? or a utility room?

From the quote, I assume that I would be allowed a bedroom if this room is built around the door out to the garden. Other habitable (non-bedrooms) could then be around this.

Last edited by Ian Gills; 5/16/07 at 3:23 PM..
Reply With Quote
  #10  
Old 5/16/07, 3:37 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,352
Default Re: Egress code

Peter, some times the AHJ looks at the proposed room not as what you call it but rather how it might be used by future occupants. I suspect he is surmising the Family Room could potentially be a sleeping room in the future therefore he wants to see an egress window. What's the issue?
Reply With Quote
  #11  
Old 5/16/07, 3:41 PM
ckratzer ckratzer is offline
Active Poster
 
Join Date: Mar 2005
Posts: 256
Please Note: ckratzer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Egress code

Quote:
Originally Posted by prussell
Thanks guys, I am building a attached 2 car garage with a family room above it and the inspector want a egress window up there. I have never come across a situation where a family room needs egress window.

Could there be something I'm missing in the life saftey codes?
Might be a municipality issue.
Without being argumentative, and using your best people skills,ask your inspector what code he/she is refering to and have him/her read it with you.
Some code inspectors are quite cooperative.
Also pay attention to code about how you are to finish the garage to conform with fire separation.
Reply With Quote
  #12  
Old 5/16/07, 3:47 PM
ckratzer ckratzer is offline
Active Poster
 
Join Date: Mar 2005
Posts: 256
Please Note: ckratzer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Egress code

Quote:
Originally Posted by Ian Gills
From the quote, I assume that I would be allowed a bedroom if this room is built around the door out to the garden. Other habitable (non-bedrooms) could then be around this.
That is how I read it.
To be sure you should also check with local code.

You may have any of those rooms as long as they are code compliant with your AHJ.

Last edited by ckratzer; 5/16/07 at 3:51 PM..
Reply With Quote
  #13  
Old 5/16/07, 6:11 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 3,118
Default Re: Egress code

OK this is what I'm up against, it appears they have amended the 2000 IRC code to include that every habitable room in a home must have 2 means of egress. Their definition of a habitable room is any room occupied within a dwelling unit.

My contention with this is what about a bathroom, laundry room, walk in closet?
Reply With Quote
  #14  
Old 5/16/07, 6:27 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,352
Default Re: Egress code

The IRC defines a "Habitable Space as a space in a building for living, sleeping, eating or cooking. Bathrooms, toilet rooms, closets, halls, storage or utility spaces and similar areas are not considered habitable spaces." If your local AHJ has amended the IRC requirement to add 2 means of egress and done so legally, i.e. by city ordinance, then you will likely have to abide by it. Ask the AHJ to provide that ordinance to you to ensure the AHJ is interpreting the requirement as you would.

Last edited by mboyett; 5/16/07 at 6:31 PM..
Reply With Quote
  #15  
Old 5/16/07, 6:36 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 3,118
Default Re: Egress code

Quote:
Originally Posted by mboyett
The IRC defines a "Habitable Space as a space in a building for living, sleeping, eating or cooking. Bathrooms, toilet rooms, closets, halls, storage or utility spaces and similar areas are not considered habitable spaces." If your local AHJ has amended the IRC requirement to add 2 means of egress and done so legally, i.e. by city ordinance, then you will likely have to abide by it. Ask the AHJ to provide that ordinance to you to ensure the AHJ is interpreting the requirement as you would.
Thanks for the clarification on that, I know this is all about safety but I just want to understand the difference. I don't have a problem with changing the window, though I do have a problem with the building department issuing a permit and approving my plans, then they come out for the frame inspection and tell me I need an egress window.

I might add the house next door got completely gutted and remodeled and there isn't a single window in the entire house. I don't want to make a big deal about it, I just want to understand the logic.

Thanks to everyone for the help.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
No "H" clips? jbreazeale Structural 7 5/17/07 2:28 PM
Newbie here with a slab "standards" question Robert Young, #3 Structural 17 4/10/07 10:48 AM
Importance of the AHJ check mcyr General Inspection Discussion 6 2/21/07 8:18 PM


All times are GMT -4. The time now is 9:37 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts