  #16  
Old 5/16/07, 6:49 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 4,318
Default Re: Egress code

Peter...

This may satisfy the AHJ...

http://www.fireescapesystems.com/products.asp

And help your wallet.

Jeff



"You cannot depend on your eyes when your imagination is out of focus"...Mark Twain


Jeffrey R. Jonas
Critical Eye Property Inspections
JRJ Consultants
Owatonna, Minnesota

NACHI07013103
IAC2-01-1567


Reply With Quote
  #17  
Old 5/16/07, 6:51 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,347
Default Re: Egress code

I'd say the original plans examiner dropped the ball on this and approved your plans in error. Or, the framing inspector is interpreting the AHJ revised rules differently than the plans examiner did. You might be able to appeal your case and get a variance but it will likely be easier just to change or add the window. I'd definitely obtain a copy of the ordinance modifying that egress requirement just to make sure of the wording.
Reply With Quote
  #18  
Old 5/16/07, 9:06 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 3,117
Default Re: Egress code

Thanks Jeff and Mike.
Mike your probably right but I like to understand why my plans can be approved but not acceptable after the fact. In most cases these battles are rarely won but I do like to professionally challenge building inspectors and debate the pros's and con's of the subject. I think they like the challenge as well when it's done in a professional manner.
Reply With Quote
  #19  
Old 5/16/07, 11:28 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,347
Default Re: Egress code

Peter, you're exactly right. BTW, I looked at your town's website and realized it's pretty small place. Is the building inspection dept a one man operation? Also, did you have the plans drawn up by an architect? Isn't his stamp on the drawings? Doesn't he share some of the blame here? What's he going to do to help correct the problem?
Reply With Quote
  #20  
Old 5/17/07, 1:19 PM
jking2 jking2 is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Troy, MI
Posts: 183
Default Re: Egress code

I would love to see photos of that house without windows. Who lives there, Count Dracula?

Jim King
Reply With Quote
  #21  
Old 5/17/07, 6:08 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 3,117
Default Re: Egress code

Well they shot me down on all counts. they have adopted a life safety code that says every habitable room in the house must have two forms of egrees, So I'm installing a egrees window in the gable end wall.

Anybody want to buy a new 60x52 double hung/double mulled window with 6/6 grids and low e glass?

The funny thing is that these folks can go into their house go to bed without a single egrees window but when they want to use their new bonus room they have to have it. The house next door just got completely renovated, new roof, new windows, new siding, kitchen, flooring ETC, but guess what! because they did not exceed 50% of the buildings value in renovations they are exempt from bringing it up to code.

This is by the way a crock of you know what. The guy that bought it is a contractor, it was foreclosed on, I'm sure he pulled the permit as the homeowner doing the renovations at a low balled price to avoid the codes and still had his crew do the job.

So my clients have to have an egress window to watch TV and the house next door does not have a single egress window in it, not even the bedrooms. Go figure!!
Reply With Quote
  #22  
Old 5/18/07, 8:27 AM
Richard A. Hetzel Richard A. Hetzel is offline
Active Poster
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Egress code

I presume the previous poster is a design professional. The building codes are quite clear on what must be done in new construction, and what must be done in repairs, renovations, rehabilitations, and reconstruction. One must do a lot more than cosmetic work in order to exceed the maximums of the code. Also, even if all windows are being replaced, the code states in "AJ102.4 Replacement windows. Regardless of the category of work, when an entire existing window, including frame, sash and glazed portion is replaced, the replacement window shall comply with the requirements of..." the energy code section of the code. No mention is made of a requirement to meet the egress window requirements in a renovation. Had the neighbor constructed an addition to the house, then any room in the addition would have been required to conform fully to the code.

The municipal supplement to the building code should be read for any exemtions having to do with existing buildings or any requirement that it applies to new construction only. It is always possible that a code official "blew the call".
Reply With Quote
  #23  
Old 5/27/07, 1:13 PM
Eric Bethel Eric Bethel is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Ofallon, MO
Posts: 16
Default Re: Egress code

I am a fireman and a home inspector, the rules generally are that you need 2 forms of egress from any living area. Bedrooms and living area's need a window ( correct dimensions ) and a door. The second story living area needs a window due to the fact,that if fire is at or around the stairs how would you get out without a window. Remember most city inspectors when called to inspect something you open yourself up to everything for them to inspect.
Reply With Quote
  #24  
Old 5/27/07, 1:21 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 21,042
Default Re: Egress code

http://www.nachi.org/emergencyegress...leased2007.htm



Nick Gromicko, CMI, CPI, IAC2, Infrared Certified
Founder, InterNACHI
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #25  
Old 5/27/07, 5:51 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 841
Default Re: Egress code

Quote:
Originally Posted by ebethel
I am a fireman and a home inspector, the rules generally are that you need 2 forms of egress from any living area. Bedrooms and living area's need a window ( correct dimensions ) and a door. The second story living area needs a window due to the fact,that if fire is at or around the stairs how would you get out without a window. Remember most city inspectors when called to inspect something you open yourself up to everything for them to inspect.
My mothers house has a walk out basement with a basement level garage.
The garage has 2 single car bay doors, 1 side entrance door & 1 entrance door to the basement.
The basement has the staircase, a rear entrance and 2, 12'x5' windows. One on each side of the rear door.

She rents rooms out in her home. She lives in the basement. She had a tenant who called the fire dept. to inspect her home... (Tennant was upset that my mother gave her eviction papers.)

Long story short, the firemen told the tenant to put the batteries back in the smoke alarms that she removed, (They found them in her room on her desk) and after checking the entire house saw nothing wrong.

Note: In the basement they said that the back door & the stairs were my mothers egresses. They said that the door leading to the garage is not an acceptable egress. Just thought I would throw that in the pot here. I just thought it was strange that the stairs (with a door at the top of the stairs) was OK but, the door to the garage was not... Either way you would need to go through two doors to exit the house.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #26  
Old 5/29/07, 9:05 AM
Richard A. Hetzel Richard A. Hetzel is offline
Active Poster
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Egress code

A required exit path of travel may not be through a garage.

"R311.4.1 Exit door required. Not less than one required exit door conforming to this section shall be provided for each dwelling unit. The required exit door shall provide for direct access to the exterior without requiring travel through a garage." (2003 IRC)

If your mother's house were to be built under current codes, a second means of egresss (Emergency Escape And Rescue Opening) would also be required in the basement, in the sleeping room.
Reply With Quote
  #27  
Old 5/29/07, 9:23 AM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 841
Default Re: Egress code

Quote:
Originally Posted by Richard A. Hetzel
A required exit path of travel may not be through a garage.

"R311.4.1 Exit door required. Not less than one required exit door conforming to this section shall be provided for each dwelling unit. The required exit door shall provide for direct access to the exterior without requiring travel through a garage." (2003 IRC)

If your mother's house were to be built under current codes, a second means of egresss (Emergency Escape And Rescue Opening) would also be required in the basement, in the sleeping room.
Yes, when I finished her basement for her I built the bed room at the opposite end of the house of the garage at the rear of the house. One of the two large windows is her bed room legal egress. The basement living space is over 1800 sq ft. The upstairs is a ranch home with 5 bedrooms and 2 full baths and a laundry. Two bed rooms & one bath are above the garage. The basement is only one bedroom, full bath, kitchen & laundry.

Like I said a big house.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #28  
Old 6/1/07, 12:33 AM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Egress code

Quote:
Originally Posted by mboyett
Peter, some times the AHJ looks at the proposed room not as what you call it but rather how it might be used by future occupants. I suspect he is surmising the Family Room could potentially be a sleeping room in the future therefore he wants to see an egress window. What's the issue?
Michael Boyett has got the right call on this one.

The IRC section R310 has stated since 2000 that all 'sleeping rooms' require 'emergency escape and rescue openings' and a bonus room above a garage with no other way out ought to be considered a 'sleeping room' and should should have an emergency escape and rescue opening..
Reply With Quote
  #29  
Old 6/1/07, 12:43 AM
homebild homebild is offline
Active Poster
 
Join Date: Nov 2006
Location: Pennsylvania
Posts: 195
Please Note: homebild is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Egress code

Quote:
Originally Posted by mboyett
I'd say the original plans examiner dropped the ball on this and approved your plans in error. Or, the framing inspector is interpreting the AHJ revised rules differently than the plans examiner did. You might be able to appeal your case and get a variance but it will likely be easier just to change or add the window. I'd definitely obtain a copy of the ordinance modifying that egress requirement just to make sure of the wording.
[quote=prussel]Thanks Jeff and Mike.
Mike your probably right but I like to understand why my plans can be approved but not acceptable after the fact. In most cases these battles are rarely won but I do like to professionally challenge building inspectors and debate the pros's and con's of the subject. I think they like the challenge as well when it's done in a professional manner.[quote]

While the original plans examiner may hve missed this one, building codes are pretty much uniform on such issues and require the builder to build to code no matter what was 'approved' or 'disapproved' or 'ignored'.

Ultimately it is not the building code official that must comply with the Code, but the builder and the owner.
Reply With Quote
  #30  
Old 6/1/07, 8:14 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 13,994
Default Re: Egress code

[quote=homebild While the original plans examiner may hve missed this one, building codes are pretty much uniform on such issues and require the builder to build to code no matter what was 'approved' or 'disapproved' or 'ignored'.

Ultimately it is not the building code official that must comply with the Code, but the builder and the owner.[/quote]

Homebuild, I have to agree with you on this one.
I wish you could post with your real name though. I do not like to communicate with slang and fictional references.

I am faced with Building to Code on a daily basis, and the type of work I do is usually in the $6 million plus and designed by Engineers and Architects that are paid to design and make sure that it is up to Code Nationally and Locally.
The Specifications always have this clause included that says Contractor is liable to adhere to Local Codes and Regulations.

They are the Designers and the high paid White Collars, why should the Contractor be liable to make sure things are up to Code?? This is another one of those clauses or disclaimers that try to put the blame on someone else. Who can the Builder blame it on?

Everything gets brushed on to the shoulders of the Builder in this scenario, and between the Local Jurisdiction and the Engineers, they wipe their A#ss with silk cloth.

In too many ways have I had change orders in the Commercial World to correct deficient designs that do not uphold Code Compliance, that it is scary.
What happens when a Project gets built and the Superintendant is 25 years old or it is a sidewalk Inspector that is controlling the Quality Control?

It must be or turn out as a disaster.

To get back to the egress Code.

Commen Sense and NFPA 101 Chapter 24 which equals the same.

Marcel



http://www.themainehomeinspector.com/
Serving all of Kennebec County and Central Maine
Cyr Home and Commercial Property Inspections

IAC2 Certified
http://co.nachi.org/inachiawards
Inachi 2009 US Member of the Year




Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
No "H" clips? jbreazeale Structural 7 5/17/07 2:28 PM
Newbie here with a slab "standards" question Robert Young, #3 Structural 17 4/10/07 10:48 AM
Importance of the AHJ check mcyr General Inspection Discussion 6 2/21/07 8:18 PM