Default EIFS kick out flashing?

Anyone else think kick out diverts are necessary for these locations?

Note the exposed housewrap and bent copper and caulk joint, not good

If so help come up with an attractive (not butt ugly design) or link to prefabbed in matching copper would be my suggestion

Client wants help with this and I'm looking for solutions



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good

Last edited by badair; 9/30/08 at 8:59 PM..
Reply With Quote
  #2  
Old 12/8/07, 2:19 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,687
Default Re: EIFS kick out flashing?

Barry,

Any copper roofing contractor can make anything they might want using their Flashing Break.
Reply With Quote
  #3  
Old 12/8/07, 2:51 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: EIFS kick out flashing?

Quote:
Originally Posted by dduffy
Barry,

Any copper roofing contractor can make anything they might want using their Flashing Break.
See that's part of the problem is they nor I know what they want.

I was just wondering if somone had seen anything that just caught their eye.

$$$ aren't going to be an issue, 7 figure house, as they are tearing off the comps and doing slate along with the EIFS repair advisements I have already given them



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #4  
Old 12/8/07, 9:46 AM
Joseph Hagarty's Avatar
Joseph Hagarty Joseph Hagarty is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 3,434
Default Re: EIFS kick out flashing?

http://www.eima.com/pdfs/EIMA%20CGuide%20final.pdf



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #5  
Old 12/8/07, 10:06 AM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,747
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: EIFS kick out flashing?

Hi Barry,

these may not be applicable to your clients application, but these are the best kick-outs available in my opinion.

http://www.dryflekt.com/

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Last edited by gbeaumont; 12/8/07 at 10:27 AM..
Reply With Quote
  #6  
Old 12/8/07, 10:12 AM
Carl Brown's Avatar
Carl Brown Carl Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 9,378
Default Re: EIFS kick out flashing?

Barry,

You might have to get with the roofer and help them design one out of copper and charge your time to the owner.

As Gerry said we all know this one is the best for most applications.

http://www.dryflekt.com/

Just do not use the same one that made the hood for the bay window they do not know about them or they would have installed them from the get go.

Maybe Bob Givens know of a copper one.

bgivens@dryflekt.com



"I create controversy whether they like it or not"



Reply With Quote
  #7  
Old 12/8/07, 10:27 AM
cgoyette cgoyette is offline
Active Poster
 
Join Date: May 2007
Posts: 363
Please Note: cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: EIFS kick out flashing?

Barry,

The house looks like the folks can afford to BUY one sample from http://www.dryflekt.com/ that would match their color. This may be the simple way to get to what they want fast.

Copper although nice and last almost forever, ends up with a patina that some folks later don't like. I do allot of high end stuff here on the SC coast and have heard the copper doesn't look as good as it once did a few times...food for thought.

Doubt I add much to this thread but your always so helpful to others I thought I would try.
Curt
Reply With Quote
  #8  
Old 12/8/07, 10:36 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: EIFS kick out flashing?

Quote:
Originally Posted by badair
Anyone else think kick out diverts are necessary for these locations?
I forgot the emoticon or whatever they're called

I have the EIMA install guide, Dryflekt and numerous other links pre-embedded in my report comments whenever these situations are present. It makes for an easier client read and identification of my actual inspection versus the protocols and solutions I try and offer.

I'll have client contact Bob

Thanks to all



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #9  
Old 12/8/07, 10:39 AM
cgoyette cgoyette is offline
Active Poster
 
Join Date: May 2007
Posts: 363
Please Note: cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: EIFS kick out flashing?

If the ? is are kickouts necessary ...you know the answer...ABSOLUTLY. That whole bay window would be subject to water damage if it has not already occurred.

Curt
Reply With Quote
  #10  
Old 12/8/07, 10:43 AM
Carl Brown's Avatar
Carl Brown Carl Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 9,378
Default Re: EIFS kick out flashing?

Bobs #

865-771-3654



"I create controversy whether they like it or not"



Reply With Quote
  #11  
Old 12/8/07, 11:13 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: EIFS kick out flashing?

Carl,

I'll add to my phonebook, thanx

Just received a PM from an esteemed member offering to send me a sample diverter.

How cool is that? NACHI rocks!



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #12  
Old 12/8/07, 11:20 AM
Carl Brown's Avatar
Carl Brown Carl Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 9,378
Default Re: EIFS kick out flashing?

The sad thing is Barry all claddings need diverters not just EIFS and Stucco.



"I create controversy whether they like it or not"



Reply With Quote
  #13  
Old 12/10/07, 2:00 PM
Bob Givens Bob Givens is offline
New User
 
Join Date: Apr 2005
Posts: 12
Send a message via AIM to Bob Givens
Please Note: Bob Givens is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: EIFS kick out flashing?

www.doli.state.mn.us/pdf/bc_webroofing_06_07.pdf

Hey NACHI Inspectors,

Now look who is listening.


Bob Givens
Reply With Quote
  #14  
Old 12/10/07, 3:14 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: EIFS kick out flashing?

Quote:
Originally Posted by Bob Givens
www.doli.state.mn.us/pdf/bc_webroofing_06_07.pdf

Hey NACHI Inspectors,

Now look who is listening.


Bob Givens
Bob,

Kudos to you.
Too bad you couldn't get in a plug (link) for your product, but it's a start. When's the IPO?



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #15  
Old 12/10/07, 5:42 PM
wkish wkish is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Palm Bay, Fl
Posts: 15
Default Re: EIFS kick out flashing?

Hi dont know if to late for a reply , Im retired rooftech. My suggestion is carefully remove shingles and flashing, the with a four inch diamond blade score the stucco straight as possible and remove the lower porching you scored care fully and with accurate prying ,pry the stucco lose,and slide the flashing behind the stucco. tou want to be atleast 3" up of the roof.Make a new kick out at the edge of roof,let it hang past the drip edge 1" and a flap fo 2"s and before you fasten the bottom edge of flashing you want a new starter, if you take your time the only debry youll have is stucco dust. Its a slow pitch so its needed , I would suggest gutter and daown spout
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior 6 10/13/07 9:10 AM
Question about chimney flashing waksell Exterior 16 6/26/07 1:25 AM
no flashing; no inspection Leanne Jowers Exterior 97 5/9/07 1:11 PM
exposed step flashing Rafael Exterior 9 5/8/06 1:25 AM
Step flashing at vertical wall? jlybolt Exterior 31 2/12/06 12:40 PM


All times are GMT -4. The time now is 4:31 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts