Default EIFS question

I'm inspecting EIFS as it is being installed on a small apatment building. The balconies have a short EIFS wall instead of railings with balusters. The top of the wall is curved/rounded. Technically, parts of the EIFS is installed horizontally (the top) so it is wrong but since it is curved, water will flow off and not set on the surface. Never seen this attempted before and I can't find anything that specifically prohibits a curved surface. Any thoughts?



Keith Runquist, CMI
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/10/10, 8:07 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: EIFS question

As long as the water drains off, typically, it isn't problematic but following the particular manufactures installation instructions of what is being installed is warranted.

What brand is it?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.

Last edited by lkage; 4/10/10 at 8:11 AM..
Reply With Quote
  #3  
Old 4/10/10, 11:38 AM
Keith Runquist, CMI Keith Runquist, CMI is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Rapid City, SD
Posts: 605
Send a message via AIM to krunquist
Default Re: EIFS question

The brand is Sto. They specifially say no horizontal surfaces (or low slope) I've never seen an installer create rounded tops on EIFS before and this may be open to some interpretaion. I'll try to get a picture today.



Keith Runquist, CMI
Reply With Quote
  #4  
Old 4/10/10, 4:31 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: EIFS question

Quote:
Originally Posted by krunquist View Post
The brand is Sto. They specifially say no horizontal surfaces (or low slope) I've never seen an installer create rounded tops on EIFS before and this may be open to some interpretaion. I'll try to get a picture today.
Minimum slope is 1:2, or 27 degrees (never less), according to:

http://stodistributor.com/webfiles.n...installers.pdf



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 4/12/10, 4:15 PM
Keith Runquist, CMI Keith Runquist, CMI is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Rapid City, SD
Posts: 605
Send a message via AIM to krunquist
Default Re: EIFS question

Found the answer to this from the manufacturer. Fisrt, they couldn't imagine why the installer would go to the kine of trouble he did to shape the EIFS that way, that's why I couldn't find a specific yes or no. They have never seen anyone do this either. Second, they said no. ANY horizontal surface, even a small one will allow water to sit longer than recommended and the top coat will start to emulsify and eventually flake away. The Mfg was very helpful and gave me a good reason to say no to this.



Keith Runquist, CMI
Reply With Quote
  #6  
Old 4/13/10, 12:50 AM
Ronald W. Huffman's Avatar
Ronald W. Huffman Ronald W. Huffman is offline
InterNACHI Member
 
Join Date: Apr 2008
Location: Parker, CO
Posts: 27
Default Re: EIFS question

Keith,
You have the definitive answer from Sto, the manufacturer; they always call for a 6 in 12 slope. I have seen one manufacturer call for a 3 in 12 slope for EIFS; all others have been 6 in12.

One additional thing to keep in mind is the climate. In South Dakota, the top surface will be subjected to freeze thaw which can also damage the finish coat. I have seen many bull nose bands on wall surfaces; they have the same concern on the top where they level out to meet the vertical wall above on a recent case the tops of the north facing bull noses were loosing their finish.

If you have a Hard Coat Stucco or Traditional Stucco the slope requirements vary considerably from 6 in 12 down to "slope" with the sketch showing the top surface almost flat.
Reply With Quote
  #7  
Old 4/13/10, 11:34 AM
Keith Runquist, CMI Keith Runquist, CMI is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Rapid City, SD
Posts: 605
Send a message via AIM to krunquist
Default Re: EIFS question

Thanks everyone. The rest of this project is an unbelievable mess to boot. I'm tempted to walk away from it unless they get some trained/certified installers and a competent supervisor. They look at me with blank stares when I talk about back wrapping. None of this can turn out well and I'm not going to teach then to do their job. Ron, do you offer a class for installers too or just inspectors? I took your inspection class when you held it at the NACHI TV studios. Good class. I'd take it again as a refresher.



Keith Runquist, CMI
Reply With Quote
  #8  
Old 4/13/10, 12:16 PM
Ronald W. Huffman's Avatar
Ronald W. Huffman Ronald W. Huffman is offline
InterNACHI Member
 
Join Date: Apr 2008
Location: Parker, CO
Posts: 27
Default Re: EIFS question

Keith,
Glad you found the Home Inspector class on stucco inspections useful. The full stucco inpsection certification class is offered by EDI at www.exterior-design-inst.com/ This class is also good for installers.

However; all Stucco manufacturer's also have training classes for their applicators and all applicators should be trained and certified by the manufacturer; bad news if they do not understand backwrapping.

Since you have taken the class you should have access to the on-line class for a reference and refresher class.
Ron
Reply With Quote
  #9  
Old 4/13/10, 2:54 PM
Keith Runquist, CMI Keith Runquist, CMI is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Rapid City, SD
Posts: 605
Send a message via AIM to krunquist
Default Re: EIFS question

Didn't know I'd have access. Scary thought, I might be in it. Uff Da. I'll check it out. I am AWCI certified. EIFS is just starting to be popular around here so inspections for it are slow. I'll recommend the EDI course to thse guys.



Keith Runquist, CMI
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
There are over 12 types of stucco and EIFS bgromicko Exterior Inspections 0 12/19/09 7:04 PM
EIFS/Stucco mmerino Exterior Inspections 16 8/6/09 7:41 AM
Sump Pit/Pump Question Joey D'Adamo Plumbing Inspections 4 11/26/08 1:04 PM
EIFS Assistance Please thance Exterior Inspections 7 2/2/08 12:39 AM
Question for all... Bob Hopton-Jones General Inspection Discussion 9 4/6/07 7:43 AM


All times are GMT -4. The time now is 6:29 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts