What would you say about this lack of flashing???
Thanks! Mid America Property Inspections, Inc. Shawnee, KS 66217 NACHI # 05110992 KS-Registration # 0110-0008 |
| Find an InterNACHI certified Idaho Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
I'm not sure what I'm looking at, but I see flashing atop the wood trim. The only other thing that should be done at this point is to seal the lower half of this trim with caulking.
|
|
#3
|
|||
|
|||
|
Please Note:
Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Well, this whole detail is a mess. I don't know how the same thing could be done with correct detailing. There needs to be flashing extending up behind the stucco and extending over the top of the stone, with weep holes. Ideally the face of the stucco and the face of the stone would be closer to the same plane. If the wood trim is absolutely required, I'd probably glue it to the stucco, and I'd make it 1 1/2 inches thick, to conceal more of the flashing, and hold its bottom edge up off the stone at least 1/4 inch.
|
|
#4
|
||||
|
||||
|
Caulk it. Caulking fixes everything!
Sean Fogarty Fogarty Home Inspection Services Providing home inspections, Mold Testing and Radon Testing for Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com |
|
#5
|
||||
|
||||
|
That wood is bound to rot, in direct contact with masonry materials.
Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#6
|
||||
|
||||
|
What's wrong with utilizing duct tape there?
|
|
#7
|
||||
|
||||
|
That is a detail for future problems.
This detail would apply better for longevity. http://www.onland.info/archives/2008...wlock_jm11.php Cyr Home and Commercial Property Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards Commercial Builder CertainTeed Master Shingle Applicator Shingle Technology Ouellet Associaties Inc. http://www.oaconstruction.com/ |
|
#8
|
|||
|
|||
|
If that's cultured stone, this is one recommended detail.
If you omit the water table the theory of the flashing system remains the same, you need a controlled exit form the stucco drainage plane above the cultured stone. Last edited by mthomas2; 10/5/09 at 11:41 AM.. |
|
#9
|
|||
|
|||
|
You have flashing on top of the wood trim.
There is no through wall flashing at the stucco / brick. Basically it looks like a code approved Kansas City Application. |
|
#10
|
|||
|
|||
|
Yep!!!
Mid America Property Inspections, Inc. Shawnee, KS 66217 NACHI # 05110992 KS-Registration # 0110-0008 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Ledger Board Flashing | jevans | Exterior | 15 | 7/2/09 11:42 PM |
| Graphic needed for flashing under stone work | lfoster | Exterior | 8 | 8/2/07 11:54 PM |
| Expansion/ contraction joints | jlybolt | Structural | 13 | 5/31/07 7:03 PM |
| no flashing; no inspection | Leanne Jowers | Exterior | 97 | 5/9/07 1:11 PM |