Default What is this on this flat roof?

This roof has some issues but does anyone know what the staining is? The seller claims the roof is new as of 2004. There is pooling happening and there is excessice sealant around the base of all of the vents. This looks like a mess to me. What is the best way to report this?
Attached Thumbnails
flat-roof-roof-should-further-evaluated.jpg   flat-roof-hpim4635.jpg   flat-roof-hpim4634.jpg   flat-roof-hpim4633.jpg   flat-roof-hpim4632.jpg  

Reply With Quote
  #2  
Old 5/25/07, 2:28 PM
Ed Fako's Avatar
Ed Fako Ed Fako is offline
Active Poster
 
Join Date: Feb 2007
Location: NW Chicago Suburbs
Posts: 199
Please Note: Ed Fako is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this on this flat roof?

It looks as though you have an APP modified bitumen roof, which was once poorly coated with an aluminumous fibered coating, which has broken down and scaled away from the roof membrane for various unknown reasons. I will list the most common I have previously observed.

Reasons?:

1) Applied too soon after roof was installed prior to gaseous diffusion from the membrane.
2) Applied over a dirty surface.
3) Applied too sparingly or it was thinned out with a solvent to "stretch" out the coverage rate.
4) Applied too lightly, instead of with a 3-4 knot brush, by possibly a thin matt paint roller.
5) Applied over a moist/wet surface.
6) After application, the roof ponded water, which broke down the coating.
7) Wrong type of roof coating was used.

Just some theories off the top of my head.

Ed

Last edited by Ed Fako; 5/25/07 at 7:41 PM..
Reply With Quote
  #3  
Old 5/25/07, 2:40 PM
PAUL J. MAGRONE PAUL J. MAGRONE is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: ORLANDO, FL
Posts: 216
Default Re: What is this on this flat roof?

Thanks. How would you report it in your report. Itemized or generalized?
Reply With Quote
  #4  
Old 5/25/07, 3:03 PM
Ed Fako's Avatar
Ed Fako Ed Fako is offline
Active Poster
 
Join Date: Feb 2007
Location: NW Chicago Suburbs
Posts: 199
Please Note: Ed Fako is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this on this flat roof?

I am not an inspector, per-se. I am a licensed roofing contractor in Illinois.

If I had to write up a report on this visual non-destructive analysis, I would just mention the existing results, and not even the potential reasons for them, as I was not there during the degradation process.

I only write down what I know or feel for a certainty.

It also looks as though some of the perimeter edge details are slightly losing their adhesion to the perimeter edgings.

It looks as though the roof holds water for periods of time lasting longer than 48-72 hours, which define a troubling scenario of ponding water.

It needs additional slope if that is truly the case, to alleviate the ponding water.

Ed
Reply With Quote
  #5  
Old 5/25/07, 3:12 PM
PAUL J. MAGRONE PAUL J. MAGRONE is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: ORLANDO, FL
Posts: 216
Default Re: What is this on this flat roof?

Florida is just a hop, skip, and a jump away. I could refer you to further evaluate the roof! Just kidding. Thanks for your input. I appreciate the help.
Reply With Quote
  #6  
Old 5/25/07, 4:17 PM
Ed Fako's Avatar
Ed Fako Ed Fako is offline
Active Poster
 
Join Date: Feb 2007
Location: NW Chicago Suburbs
Posts: 199
Please Note: Ed Fako is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this on this flat roof?

Gladly.

Free Estimate with a minimum fee of $ 125.00 for a detailed non-destructive analysis report,.....





plus travel expenses.





Wish I were closer to help out.

Ed

Last edited by Ed Fako; 5/25/07 at 7:42 PM..
Reply With Quote
  #7  
Old 5/25/07, 5:15 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,846
Default Re: What is this on this flat roof?

Ed is absolutely correct. It really doesn't matter nor is it up to the home inspector to know exactly why something has become or is degraded. Report on "what you see". As he illustrated there could be numerous reasons or a combination of reasons why. How often have you heard the owners say "Its been like that for years and nothing happened". Just because something hasn't completely failed yet it is not an endorsement of quality. I see decks barely holdling up and the owner will proudly tell me it went thru Hurricanes Ivan and Dennis as if to say there is nothing wrong with it. I would simply state the obvious discrepancies, recommend repair by a licensed Roofing contractor. Even new cars break down due to inferior components or flawed designs. Good catch. Never go completely on the word of the sellers. Often an owner will tell a roof is only a couple of years old and to prove it go find the work order / receipt only to discover it has been more like 7 plus years ago.
Reply With Quote
  #8  
Old 5/25/07, 7:47 PM
Ed Fako's Avatar
Ed Fako Ed Fako is offline
Active Poster
 
Join Date: Feb 2007
Location: NW Chicago Suburbs
Posts: 199
Please Note: Ed Fako is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this on this flat roof?

I find one of the more ludicrous statements made by a home owner and even more-so, the sellers realtor, especially when they are putting the home up for sale, is the following:

It's a brand new roof! We just had it put on (pick one), 5 years or 10 years ago.

Well, in my book a 10 year old car is still a ten year old car. I must not have recieved the Realtors Blue Book on Roofs, as it MUST be saying that a 10 year old roof is still new.

Ed
Reply With Quote
  #9  
Old 5/28/07, 3:24 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this on this flat roof?

I believe the realtor's bible says "roof recently replaced"...with "recently" left undefined.
Reply With Quote
  #10  
Old 5/30/07, 4:29 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: What is this on this flat roof?

Yeah all the coating does is help protect the roof from UV deterioration so recommend a recoat,at least that is what I would do.
Sometimes we pass off too much.
Reply With Quote
  #11  
Old 5/30/07, 10:16 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,646
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this on this flat roof?

judging from those pictures, that roof looks like it may be older than 2004, especially with that repair in picture #3. Do they have any proof of age other than their word. I always advise my clients to seek a permit record from the county. Youd be surpirsed how many times that 3 year old roof turns out to be 8 or 9 years old.
Reply With Quote
  #12  
Old 5/30/07, 11:16 PM
Ed Fako's Avatar
Ed Fako Ed Fako is offline
Active Poster
 
Join Date: Feb 2007
Location: NW Chicago Suburbs
Posts: 199
Please Note: Ed Fako is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this on this flat roof?

That was probably not a repair you speak of.

Most likely, the utility company or the electrician showed up after the roof was installed. They erroneously patched in the electrical service pipe using plastic roofing cement and a common rubber sleeved pipe boot flashing. Both are no-no's per the roofing manufacturers warranty, which typically is only for the materials and not the labor any ways, on a residential application.

Good eyes. I never did expand the photos originally.

Ed
Reply With Quote
  #13  
Old 5/31/07, 6:51 AM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,646
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this on this flat roof?

I dont know about Orlando, but here in South Florida they require a pitch pan to be installed around the weatherhead.

Ed,

As you are a roofer I have a question. I have been told that (at least down here) a modified covering should not (or does not) need to be silvercoated. However it is a requirement that cap sheet is silvercoated to comply with fire regulations. What do you know about this?
Reply With Quote
  #14  
Old 5/31/07, 11:07 AM
Humberto Carvajal's Avatar
Humberto Carvajal Humberto Carvajal is online now
InterNACHI Member
 
Join Date: May 2005
Location: Homestead, FL
Posts: 819
Default Re: What is this on this flat roof?

William as I understand it the cap sheet is granulated hence complying with fire regulations and providding uv protection. Ive also been told there is a company or companies that will apply a special adhesive and later spread the granuals on the coating. And no the modified roof is not required to be silvercoated. Although it would definately be in the best interest of the homeowner to have it.
Reply With Quote
  #15  
Old 5/31/07, 11:13 AM
Ed Fako's Avatar
Ed Fako Ed Fako is offline
Active Poster
 
Join Date: Feb 2007
Location: NW Chicago Suburbs
Posts: 199
Please Note: Ed Fako is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is this on this flat roof?

From many of the manufacturers, by doing a proper job using either an approved density poundage of a fibered aluminum coating or an approved elastomeric coating, the warranty length will be slightly extended on commercial applications.

Most residential applications are for a materials only warranty and pro-rated anyways, from original cost of materials.

I advise it to be done, but to usually wait about 30 days for any gasses to bleed out of the membrane after it has been installed.

To ensure a proper amount of the coating gets applied, it is best to put one coat on in one brushing direction and then a second application in the perpindicular direction.

All seams should be carefully inspected prior to covering them up with any coating though.

All coatings should be inspected and recoated as necessary about every 3 to 5 years. They do do a very good job if done correctly, in prolonging the life of the roof materials and also of keeping the iterior of the building cooler.

Pitch pockets are sparingly approved. A better flashing detail is done prcisely with the actual membrane and a target patch instead.

Plastic roof cement is against the manufacturers reecomendations and could void the warranty, but some approve of a MB Cement, which is a modified bitumen roofing cement.

Pitch pockets are good for only one thing. That is the first place I look for a source of water entry when doing a leak inspection. The plastic cement or even some pitch pocket fillers settle down to a lower level that the height of the perimeter of the sheet metal pitch pocket and hold water until it finally migrates its way in through the sealant. They all do eventually.

Ed
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 8:10 AM
Ice Gaurd membrane dmacy Exterior Inspections 36 6/14/07 12:21 AM
Flat roof gurus.... jbreazeale Structural Inspections 0 5/17/07 11:55 PM
Roof Repair? Maybe NO jhagarty Exterior Inspections 9 2/15/07 1:19 AM
flat roof vent brepanshek Plumbing Inspections 2 10/13/06 7:36 PM


All times are GMT -4. The time now is 1:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts