  #1  
Old 6/12/07, 9:48 PM
Scott Falvey Scott Falvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Footings under PT landings

Todays inspection had 2 step landing combonations made from PT. The posts are 4x4 but none of them are on footings, just sitting in the dirt. The units are not attached to the house.

My question, I think they are OK because they are not attached to the structure and therefor will not harm anything when the frost heaves them around. Am I right in this thinking?

Thanks,
Attached Thumbnails
footings-under-pt-landings-img_03311.jpg  



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #2  
Old 6/12/07, 9:51 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,734
Default Re: Footings under PT landings

Well, in my opinion, no. The posts should be below frost on adequate footings and the railing should be of a graspable size.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #3  
Old 6/12/07, 11:00 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 2,825
Default Re: Footings under PT landings

The posts do not need to be below the frost line but a footing should be, if the deck/landing becomes unstable and someone walks out on to it, it could fall over injuring someone.

Larry's right about the handrails too, those don't appear to be grip able
Reply With Quote
  #4  
Old 6/12/07, 11:12 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,987
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Footings under PT landings

The only problem I can see with the frost heave is it could affect the landing in relation to the rise between the landing and the door threshold.
Reply With Quote
  #5  
Old 6/12/07, 11:14 PM
Scott Falvey Scott Falvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Footings under PT landings

Quote:
Originally Posted by lkage
Well, in my opinion, no. The posts should be below frost on adequate footings and the railing should be of a graspable size.
The handrail is a 2x4 on its side.



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #6  
Old 6/13/07, 6:57 PM
Richard A. Hetzel Richard A. Hetzel is offline
Active Poster
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 596
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Footings under PT landings

Often, steps such as that are based on 4" thich concrete slabs on the ground. I don't think deep footings are necessary, but the posts should not be in contact with the earth.
Reply With Quote
  #7  
Old 6/13/07, 8:43 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,734
Default Re: Footings under PT landings

Quote:
Originally Posted by sfalvey
The handrail is a 2x4 on its side.
Yes?



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #8  
Old 6/13/07, 8:46 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,734
Default Re: Footings under PT landings

Quote:
Originally Posted by Richard A. Hetzel
Often, steps such as that are based on 4" thich concrete slabs on the ground. I don't think deep footings are necessary, but the posts should not be in contact with the earth.
...and your reasoning?



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #9  
Old 6/13/07, 9:16 PM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Footings under PT landings

Quote:
Originally Posted by lkage
...and your reasoning?
Termite bait.
Reply With Quote
  #10  
Old 6/13/07, 9:20 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Rollinsford, NH
Posts: 2,825
Default Re: Footings under PT landings

Quote:
Originally Posted by tallen
Termite bait.

Not in NH, very rare in Scotts area! Too damm cold in the winter.
Reply With Quote
  #11  
Old 6/13/07, 9:34 PM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Footings under PT landings

Quote:
Originally Posted by prussell
Not in NH, very rare in Scotts area! Too damm cold in the winter.
Ok, then I go with dry rot.?
Reply With Quote
  #12  
Old 6/14/07, 11:51 PM
arussell arussell is offline
Active Poster
 
Join Date: May 2007
Location: Groveland, Ma
Posts: 175
Please Note: arussell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Footings under PT landings

These people are very smat ya know.

It's not permanently attached to the house, therefore they can't be taxed for a deck!
Reply With Quote
  #13  
Old 6/14/07, 11:57 PM
Ted Allen Ted Allen is offline
Active Poster
 
Join Date: Oct 2003
Posts: 3,156
Please Note: tallen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Footings under PT landings

Quote:
Originally Posted by arussell
These people are very smat ya know.

It's not permanently attached to the house, therefore they can't be taxed for a deck!
It is also not considered a safe exit point.
Reply With Quote
  #14  
Old 6/15/07, 2:21 AM
ekartal6 ekartal6 is offline
Active Poster
 
Join Date: Oct 2006
Location: Schaumburg, IL
Posts: 1,107
Please Note: ekartal6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Footings under PT landings

It is likely that the posts are not on concrete footings because the use of treated wood. Even treated they can still rot - just takes longer. IMO wood to earth contact should always be called out no matter where you live. Dry rot in Todd's hood and moist crud in the midwest.
Reply With Quote
  #15  
Old 6/15/07, 3:07 AM
Richard A. Hetzel Richard A. Hetzel is offline
Active Poster
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 596
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Footings under PT landings

Quote:
Quote:
Originally Posted by Richard A. Hetzel
Often, steps such as that are based on 4" thich concrete slabs on the ground. I don't think deep footings are necessary, but the posts should not be in contact with the earth.


...and your reasoning?
Items such as stairs that will not be materially affected by frost heave are not required to have deep footings. I have for decades been specifying concrete pads under the ends of the stairs, so that the wood will not contact the earth, and so that a natural point of wear is eliminated.

The former New York state building code had verbiage that supported this practice. It's too late at night to check the IRC for similar verbiage, but no code official has ever required footings under stair stringers, and I know of no problems arising from this practice.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
code for minimum floor space at top of stairs? areid Misc. Discussion 12 4/16/07 10:39 AM


All times are GMT -4. The time now is 3:11 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts