Default Gas fireplace exhaust

I see the safety issue in these being too close but is there a code stating this? I don't tthink these are a very good idea.
Attached Thumbnails
gas-fireplace-exhaust-1177-and-1178-report-012.jpg 1178 report 012.jpg
Views:	172
Size:	43.8 KB
ID:	46289   gas-fireplace-exhaust-1177-and-1178-report-017.jpg 1178 report 017.jpg
Views:	118
Size:	56.0 KB
ID:	46290   gas-fireplace-exhaust-1177-and-1178-report-013.jpg 1178 report 013.jpg
Views:	149
Size:	58.1 KB
ID:	46291  



J.Szczesny
4 Seasons Home Inspections
Washington State Inspector # 711
800 5th Ave #101-385
Seattle, Wa 98104
(206)391-0285

online @ www.4seasonsinspects.com
email @ info@4seasonsinspects.com
toll free cal @ 866-512-9972

"For the best protection,
get the right inspection"


Reply With Quote
Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/10/11, 3:37 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Gas fireplace exhaust

Hmm ...I do not see a issue.
What is your worry?

http://pmaoutdoor.com/Documents/ECS_...Clearances.pdf
Reply With Quote
  #3  
Old 7/10/11, 7:48 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Gas fireplace exhaust

No moisture cover on outlet, disconnect to close to the flue, IMO it is questionable about space from the condenser



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #4  
Old 7/10/11, 8:35 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Gas fireplace exhaust

I see no issue here except for the third pic where I agree with Wayne.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #5  
Old 7/10/11, 12:20 PM
James R. Szczesny's Avatar
James R. Szczesny James R. Szczesny is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Seattle,Wa
Posts: 332
Default Re: Gas fireplace exhaust

Quote:
What is your worry?
Disconnect is to close to Flue?
Go to pull plastic disconnect and box is too hot to touch or daily over heating of box from flue causes plastic parts inside to corrode faster. I'll write it up as I se it.
Thanks Peeps.



J.Szczesny
4 Seasons Home Inspections
Washington State Inspector # 711
800 5th Ave #101-385
Seattle, Wa 98104
(206)391-0285

online @ www.4seasonsinspects.com
email @ info@4seasonsinspects.com
toll free cal @ 866-512-9972

"For the best protection,
get the right inspection"


Reply With Quote
  #6  
Old 7/10/11, 1:08 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Gas fireplace exhaust

Then why bother asking for guidance from others?

I would avoid declaring that heat will cause plastic to corrode in your report.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #7  
Old 7/10/11, 2:19 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Gas fireplace exhaust

Direct Vent Clearances



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #8  
Old 7/10/11, 4:37 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Gas fireplace exhaust

Quote:
Originally Posted by jszczesny View Post
Disconnect is to close to Flue?
Go to pull plastic disconnect and box is too hot to touch or daily over heating of box from flue causes plastic parts inside to corrode faster. I'll write it up as I se it.
Thanks Peeps.
Too close to the flue?

Please notice that the disconnect is near the intake air side of the combination flue combustion air fitting.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #9  
Old 7/11/11, 7:43 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas fireplace exhaust

Quote:
Originally Posted by ccurrins View Post
Could those clearances be for Canada only?........ There is a reference to CGA (Canadian Gas Association) Installation Code "B149" in the last sentence?
Reply With Quote
  #10  
Old 7/11/11, 11:03 AM
James R. Szczesny's Avatar
James R. Szczesny James R. Szczesny is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Seattle,Wa
Posts: 332
Default Re: Gas fireplace exhaust

Quote:
Then why bother asking for guidance from others?
Chuck,,
Where do you see I am asking for guidance?

Just other opinions,

I Just simply stated that this box is too close to the fireplace exhaust.

Tha same 6 guys reply back. useally 2 with great replies, 2 with questions and 2 but heads.
Sometimes NACHI message boards suck.

Thanks for your input Mike and Wayne.



J.Szczesny
4 Seasons Home Inspections
Washington State Inspector # 711
800 5th Ave #101-385
Seattle, Wa 98104
(206)391-0285

online @ www.4seasonsinspects.com
email @ info@4seasonsinspects.com
toll free cal @ 866-512-9972

"For the best protection,
get the right inspection"



Last edited by jszczesny; 7/11/11 at 11:14 AM..
Reply With Quote
  #11  
Old 7/11/11, 1:43 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Gas fireplace exhaust

Quote:
Originally Posted by Brian A. MacNeish View Post
Could those clearances be for Canada only?........ There is a reference to CGA (Canadian Gas Association) Installation Code "B149" in the last sentence?
Keep reading.........or ANSI Z223.1
(American National Standards Institute)



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #12  
Old 7/11/11, 2:43 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas fireplace exhaust

Quote:
Originally Posted by ccurrins View Post
Keep reading.........or ANSI Z223.1
(American National Standards Institute)
Always thought NFPA or AGA wrote the gas code there. They make claims to it.

Work with the new basis for fuel gas safety nationwide and around the globe: the 2009 NFPA 54: National Fuel Gas Code. This is a joint publication by the National Fire Protection Association and the American Gas Association. It is designated both as NFPA 54 and ANSI/AGA Z223.1
Reply With Quote
  #13  
Old 7/11/11, 2:45 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Gas fireplace exhaust

They do Brian but ANSI either accepts them or not.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/11/11, 8:22 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas fireplace exhaust

Quote:
Originally Posted by mlarson View Post
They do Brian but ANSI either accepts them or not.
They even sell Canadian Standards.
Reply With Quote
  #15  
Old 7/14/11, 6:07 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is online now
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,055
Default Re: Gas fireplace exhaust

Yes I agree pics 1 and 3 are questionable at best.
http://www.bradfordwhite.com/images/...-48146-00A.pdf

Attachment 46419



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816

Last edited by ryoung7; 10/5/11 at 10:36 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas Fireplace Exterior Wall Exhaust aroncone Inspecting HVAC Systems 3 11/28/10 2:57 PM
The Importance of Bathroom and Kitchen Fans mkyriacou Interior Inspections 35 6/4/10 5:27 PM
Hearth size??? jcampbell Inspecting HVAC Systems 32 6/1/08 1:56 PM