Default Is inadequate roof or attic ventilation a defect?

I've been running across many homes during the past several weeks that have ventilation issues. I use the 1 sq foot of free venting for every 300 sq feet of attic space. Usually the vents should be split 1/2 on the high side and 1/2 on the low side.

I was asked why inadequate venting is a "defect" and my response is
  1. Inadequate ventilation can significantly reduce the life of the roof due to the excessive heat
  2. Inadequate ventilation can lead to moisture build-up in the attic which can reduce the effectiveness of the insulation and/or lead to possible mold/mildew issues
Also, whenever I see a bathroom fan of kitchen fan directly into the attic, I call it out as a significant problem

I'm looking for some feedback on this issue. Is it a defect the seller should take care of or is it a maintenance item the home buyer needs to deal with?



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowlege will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.4squarehi.com
Follow Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #2  
Old 7/19/07, 8:35 PM
Dennis R. Goudreau Dennis R. Goudreau is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Nashua, NH
Posts: 1,212
Default Re: Is inadequate roof or attic ventilation a defect?

correct on 1&2 & vent fan as for me I would just write it up in the report & leave it to the buyer & seller
Reply With Quote
  #3  
Old 7/19/07, 8:42 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 483
Default Re: Is inadequate roof or attic ventilation a defect?

I guess I was a little unclear on how I would write it up. If I classify it as a "maintenance" item, the seller doesn't have to do anything. If I classify it as a "defect", then the buyer can ask for something to be done about it. That's the way it works in Wisconsin.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowlege will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.4squarehi.com
Follow Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #4  
Old 7/19/07, 8:47 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,845
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is inadequate roof or attic ventilation a defect?

For a typical sloped roof attic you are correct. I would call it out as you would.

I know when you see the same thing many times you may start to second guess yourself.

One of the things I see in my area is a lot of century homes where there is no sofit (or low side) venting. Originally the houses would have had shakes on 1" roof deck boards. There was enough spaces through the boards and the shakes to allow ventilation. Now they have ashphalt shingles and often with an added layer of OSB. Sure the have static or ridge vents but noe means of providing intake air.
Reply With Quote
  #5  
Old 7/19/07, 8:53 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,845
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is inadequate roof or attic ventilation a defect?

AI would not write it as a maintenance item. To me maintenance means something that has to be done regularily. Once you install the proper venting that should be it.
Reply With Quote
  #6  
Old 7/19/07, 8:55 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,726
Default Re: Is inadequate roof or attic ventilation a defect?

I would note the type of ventilation and recommend aditional venting if it needed it...that's all.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #7  
Old 7/20/07, 1:37 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is inadequate roof or attic ventilation a defect?

The idea of grease being vented into an attic bothers me.
Reply With Quote
  #8  
Old 7/20/07, 2:16 AM
Paul Dickerson Paul Dickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 327
Default Re: Is inadequate roof or attic ventilation a defect?

Inadequate ventilation in the attic is a defect, not a maintenance item.

So in Wisconsin, if your house was built correctly, and then you did absolutely no maintenance for 20 years, you would not be obliged to address any of the maintenance items identified on an inspection report? It seems silly that the state should get in the middle of the negotiation between the buyer and the seller.
Reply With Quote
  #9  
Old 7/26/07, 1:27 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 433
Default Re: Is inadequate roof or attic ventilation a defect?

Are you required by your state SOP to seperate defect and maintenance? We are not, and I don't, I just note all found items and bring major items to the summary , all noted items are up for negotiation.
Reply With Quote
  #10  
Old 7/26/07, 3:21 PM
Richard A. Hetzel Richard A. Hetzel is offline
Active Poster
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 596
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is inadequate roof or attic ventilation a defect?

Attic ventilation requirements and good practice changed over the years, so that an attic that once represented the state of the art could be thought of as deficient by modern standards. If I were an inspector, I think I would write it up in something like that way, saying that it once might have been normal practice but that standards have changed, and thought might be given to upgrading to current standards. It's certainly worth noting, but my own humble opinion is that it shouldn't be noted in such a way as to force any party to take action.
Reply With Quote
  #11  
Old 7/28/07, 4:16 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,486
Send a message via ICQ to kshepard
Default Re: Is inadequate roof or attic ventilation a defect?

Quote:
Originally Posted by Richard A. Hetzel
Attic ventilation requirements and good practice changed over the years, so that an attic that once represented the state of the art could be thought of as deficient by modern standards. If I were an inspector, I think I would write it up in something like that way, saying that it once might have been normal practice but that standards have changed, and thought might be given to upgrading to current standards. It's certainly worth noting, but my own humble opinion is that it shouldn't be noted in such a way as to force any party to take action.
Good point, Richard. It's building science, it's looking at the home as a system and Greg, the people who want you to make the decision on who pays don't always get what they want. It appears that the laws of physics and the laws of Wisconsin may be in conflict here.

Our job as home inspectors is to describe the conditions as best we can. It may be handy for those who stand to benefit to have a title slapped on a certain condition, but conditions don't always lend themselves to handy legal descriptions. What are your options?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #12  
Old 7/28/07, 8:59 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Is inadequate roof or attic ventilation a defect?

I'm finding roof ventilation issues every day. Roofers are slapping on shingles in one day and not even bothering with vent installations whatsoever. Or they'll even install the ridge vent, but not even bother with the lower soffit/drip edge vent. I guess they consider this to be a Carpenter's job. I've even found many ridge vents that were installed at the ridgeline, but the plywood under this fake vent was not even cut back. These roofers are absolutely hilarious....

I see this defect so much, I had to design a web page for proper attic ventilation, in order to make it easier for my client's to comprehend proper attic ventilation. I simply note the defect, and add the link to their report.
Reply With Quote
  #13  
Old 7/29/07, 5:07 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 621
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is inadequate roof or attic ventilation a defect?

David: Is the article on attic ventilation your own? Can I get your permission to tweak it and put it on my website?
Reply With Quote
  #14  
Old 7/29/07, 6:44 AM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is inadequate roof or attic ventilation a defect?

http://www.buildingscience.com/bsc/

Read this one http://www.buildingscience.com/docum...bly/main_topic

............ Cookie
Reply With Quote
  #15  
Old 7/29/07, 7:37 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Is inadequate roof or attic ventilation a defect?

Quote:
Originally Posted by jbreazeale
David: Is the article on attic ventilation your own? Can I get your permission to tweak it and put it on my website?
Jimmy,

Yes, I designed that page myself. You can help yourself, but please re-configure the information a bit in order to make your web page content different from mine.

Roy,

Nice article but I like to see vented roof cavities (Ridge & Soffit) on many applications. The only unvented roof cavity I'd let roofers get away with (in my area) is the blown-in foam. One excellent foam insulation is Icynene.


And keep in mind, some roofing manufacturer's will not warranty their shingles with improper ventilation. Always check with the manufacturer's installation instructions.

Here's another nice read on attic ventilation.

http://www.airvent.com/pdf/literatur...ellingTips.pdf

Last edited by dvalley; 7/29/07 at 7:40 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


LinkBacks (?)
LinkBack to this Thread: http://www.nachi.org/forum/f16/inadequate-roof-attic-ventilation-defect-19078/
Posted By For Type Date
Debating Attic Ventilation Pros and Cons - Contractor Talk - Professional Construction and Remodeling Forum This thread Refback 9/28/08 5:25 PM
should a gable dormer roof be vented? - JLC-Online Forums This thread Refback 9/18/08 6:19 AM
seal gable vents after ridge vent installed? - Contractor Talk - Professional Construction and Remodeling Forum This thread Refback 9/18/08 12:10 AM

Similar Threads
Thread Thread Starter Forum Replies Last Post
A little on the Commercial side of things. mcyr General Inspection Discussion 457 8/1/09 11:50 AM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior 6 10/13/07 9:10 AM
Spray Foam to the Rescue ? mcyr Structural 3 3/27/07 8:29 PM
Roof Repair? Maybe NO jhagarty Exterior 9 2/15/07 2:19 AM


All times are GMT -4. The time now is 3:27 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts