Default Ledger Strip

Is this acceptable method using a ledger strip.

It seems to me the nails could easily pull away and joist hangers would be more secure.
Attached Thumbnails
ledger-strip-151009-018-small-.jpg.jpg
Views:	498
Size:	37.7 KB
ID:	33646  
Reply With Quote
Find an InterNACHI certified New Hampshire Home Inspector (and anywhere else in North America)
  #2  
Old 12/3/09, 10:30 AM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Ledger Strip

My first thought is that ledger should be continuous.



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #3  
Old 12/3/09, 10:40 AM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: Ledger Strip

Quote:
Originally Posted by bgraham View Post
My first thought is that ledger should be continuous.

That is a good point!! Thanks.

Doing inspection tomorrow. Did the exterior yesterday when I set up radon test.

Just thinking of some good report verbaige.
Reply With Quote
  #4  
Old 12/3/09, 12:27 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Ledger Strip

l would bet there is NO flashing behind the ledger board. Let us know.



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #5  
Old 12/3/09, 12:30 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: Ledger Strip

Quote:
Originally Posted by bhartley View Post
l would bet there is NO flashing behind the ledger board. Let us know.
It seems it is rare to find a flashing these days.
Reply With Quote
  #6  
Old 12/3/09, 2:21 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Ledger Strip

Quote:
Originally Posted by dmacy View Post
Is this acceptable method using a ledger strip.

It seems to me the nails could easily pull away and joist hangers would be more secure.
Is the ledger board bolted to the house? That's a must to help prevent pulling away from building.

Recommendation I use for ledger strips .....

Ledger strips can be used in lieu of hangers or wall bearing. Ledger strips
are to be 2” x 2” minimum and anchored with 3 - #16 nails * spaced 2” – 3”
apart under each joist location.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #7  
Old 12/4/09, 10:52 AM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,489
Default Re: Ledger Strip

The ledger is fine........
And just to let you know..... a typical 10d - 16d nail has 200 lbs of holding power....how man nails and ledger strips are needed to support each joist..........
it would have been nice to have the 2x2 ledger be continuous however it is not required.

There should be flashing behind the band joist and the band should be bolted with 5/8" galvanized bolts. (nails should be galvanized as well).
Reply With Quote
  #8  
Old 12/4/09, 11:02 AM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,489
Default Re: Ledger Strip

Quote:
Originally Posted by ccurrins View Post
Is the ledger board bolted to the house? That's a must to help prevent pulling away from building.

Recommendation I use for ledger strips .....

Ledger strips can be used in lieu of hangers or wall bearing. Ledger strips
are to be 2” x 2” minimum and anchored with 3 - #16 nails * spaced 2” – 3”
apart under each joist location.
Just for clarity since there are those who are not familiar with basic framing practices.......the 2x2 is the nominal size......which means the 2x2 is actually 1.5 inches x 1.5 inches.

One of the things I see more often are lack of bracing (deck over 48")........I think Nachi has a section on decks somewhere on the site.

Also look for screws being used to fasten joist hangers....these do not have the same shear strength approved nails.
Reply With Quote
  #9  
Old 12/5/09, 12:33 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Ledger Strip

National statdards call for flashiing OVER, not behind, the ledger board.

Hops this helps.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #10  
Old 12/5/09, 8:38 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Ledger Strip

I don't have a problem with it not being continuous. However, there are not enough nails. As someone has already said, there should be 3 nails beneath each joist. That one joist sitting on the edge of the ledge...I don't see how you could nail it substantially with 3 nails. I don't think the joist should sit on the edge of the ledger.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 12/5/09, 12:53 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Ledger Strip

The ledger strip should be continuous as a standard practice to distrubute the load evenly among the fasteners.

It seems odd that I don't see any toenailes in the framing members to the ledger and no fasterners visible in the ledger itself.


Floor joists should have a minimum of 1½" of bearing at each end. When joists butt into the side of a beam, a ledger strip can be nailed onto the beam to provide the necessary bearing surface. Ledger strips are typically 2" X 2" and are fastened to the beam with two 3Ό" nails at each joist.
Reply With Quote
  #12  
Old 12/5/09, 8:18 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Ledger Strip

You mean this is wrong?

ledger-strip-120409-063.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 12/5/09, 8:29 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Ledger Strip

Not back in those years Joe.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Ledger Board Flashing jevans Exterior Inspections 15 7/2/09 10:42 PM
Ledger board question pcoulter Exterior Inspections 2 4/18/09 8:09 PM
Max load allowed on 2x2 ledger bking Structural Inspections 4 12/23/07 2:05 PM


All times are GMT -4. The time now is 6:53 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts