Here is the resommend verbiage for manufactured stone issues that are from the NC HI board website at http://www.ncdoi.com/OSFM/Engineerin...d_language.asp

Do you see anything wrong with it?


Recommended language for comments related to incorrect installation of artificial stone siding.

Approved by Standards of Practice/Rules/Interpretations Committee 10/30/09
Submitted for Board consideration at Regular Meeting 11/20/09


Background:
In recent years artificial stone has been used with increased frequency on the exteriors of buildings. In many cases the installation has been found to be improper and not in compliance with the installation instructions of the stone manufacturers. Incorrect installation can result in water penetration, structural damage, and mold growth. The following language is recommended for use by home inspectors with regard to incorrectly installed artificial stone siding. The bulleted items should be used as deemed appropriate for the building inspected.

Recommended Language:
Manufactured stone veneer has been installed on the (list areas) of this house. An inspection of the visible components has revealed that the stone veneer has not been installed in compliance with installation guidelines provided by the Masonry Veneer Manufacturer’s Association (MVMA). A PDF copy of the installation guidelines is available at http://www.masonryveneer.org/pdf/mvma030909.pdf.

Specific problems noted with the visible components include, but may not be limited to: (list all that apply)  Weep screeds are missing at the base of the wood frame walls. Weep screeds are missing at the tops of window and door openings. There is no caulk between other materials and the masonry veneer at windows, doors, and adjacent trim. The masonry veneer is in contact with the ground. The masonry veneer is in contact with paved surfaces. The masonry veneer is in contact with roofing materials. Kick-out flashings are missing where roof eaves meet the masonry veneer. Metal lath is visible between stones, indicating that the proper base coats of mortar were not applied prior to installation of the stone.

The lack of proper detailing and flashing may result in water penetration behind the siding, resulting in structural damage. The installation of the manufactured stone veneer should be evaluated, compared to the specific installation requirements of the stone manufacturer and the MVMA, and repaired or replaced as deemed necessary by a licensed general contractor or masonry contractor experienced with installation requirements for manufactured stone veneer.

Please note that because the water resistive barrier , metal lath, and base coat(s) of cement stucco are completely concealed behind the manufactured stone veneer, they cannot be evaluated by a visual inspection.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/31/10, 11:39 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: manufactured stone verbiage

Nice reference document. Wish I knew about it last week when I inspected a 10yo house that had adhered stone veneer installed down to a brick ledge (along with all of the other typical installation issues at windows, flashings, etc.)

For some reason my pictures don't quite match the diagrams in the installation guide.

I don't see anything wrong with the verbiage except that the stone veneer can be too close to the ground, paved areas and roof without being in contact with it. I would probably say inadequate clearance to...
Attached Thumbnails
manufactured-stone-verbiage-copy-p1340982.jpg   manufactured-stone-verbiage-copy-p1340989.jpg   manufactured-stone-verbiage-copy-p1340986.jpg  



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 1/31/10 at 11:45 AM..
Reply With Quote
  #3  
Old 2/1/10, 11:34 AM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,487
Default Re: manufactured stone verbiage

Bruce, I go with the exact verbiage that the board requires (not that I always agree with their verbiage)....... deviating from same may land you in hot water with the board in the event an incident does happen. The verbiage is there to 1.) protect the board, 2.) the public and 3.) you. (pretty much in that order).


If you are going to add anything to it, then simply find out who the manufacturer is and attach their instruction manual / guidelines to the report.

regards

Jeff
Reply With Quote
  #4  
Old 2/1/10, 12:20 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: manufactured stone verbiage

Jeff,

The state has a page with "recommended" verbiage but I am not aware of any that is "required".

I like the stone one ok but the PB pipe one is old, incomplete and just plain weak so I use my own for that.

The state is now working on new rules/sop to integrate the new bill that passed into law.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #5  
Old 2/2/10, 10:34 AM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: manufactured stone verbiage

I used some of the verbiage on this $900,000 10 month house yesterday.
Attached Thumbnails
manufactured-stone-verbiage-covered-stone-front.jpg   manufactured-stone-verbiage-img_0318.jpg   manufactured-stone-verbiage-img_0324.jpg   manufactured-stone-verbiage-img_0325.jpg   manufactured-stone-verbiage-img_0326.jpg  




Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #6  
Old 2/2/10, 5:08 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: manufactured stone verbiage

Bruce, have you seen this.



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #7  
Old 2/2/10, 5:11 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: manufactured stone verbiage

Sorry the file was to big.



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #8  
Old 2/2/10, 5:37 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: manufactured stone verbiage

post a link or email it, thanks



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #9  
Old 2/2/10, 7:21 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: manufactured stone verbiage

Is this stone installed correctly anywhere in the US???



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #10  
Old 2/2/10, 7:24 PM
Larry J. Michael Larry J. Michael is offline
InterNACHI Member
 
Join Date: Nov 2009
Location: Greensboro, N. C.
Posts: 732
Default Re: manufactured stone verbiage

I to use NC's recommended verbiage. I am interested in seeing what they will make mandatory.



Greensboro Home Inspection
Providing home inspections in Greensboro, High Point, Burlington and the surrounding areas.
greensboro-home-inspection.html

Raleigh Home Inspection
Home inspections in Raleigh, Durham, Cary, Chapel Hill, Apex and surrounding areas.
Raleigh-home-inspection.html

BassRumors.com
Providing a blog, news, and forum dedicated to bass fishing.
Reply With Quote
  #11  
Old 2/2/10, 7:36 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: manufactured stone verbiage

Quote:
Originally Posted by bhartley View Post
i used some of the verbiage on this $900,000 10 month house yesterday.
$900,000 Fubar



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 2/2/10, 9:15 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: manufactured stone verbiage

Yes SIR! and guess who the bad guy is?



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #13  
Old 9/21/10, 6:17 AM
Vince Santos's Avatar
Vince Santos Vince Santos is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Canton, MI - Serving Souteast Michigan
Posts: 1,786
Default Re: manufactured stone verbiage

This was brought to my attention a while ago. Apparently enough problems are arising due to improper install and I have yet to see it installed correctly. Yesterday I came across it again with missing flashing, no weep screeds. At least this time it was well caulked.

Has anyone seen it installed per manufactures requirements?



Vince Santos
StepByStep Home Services LC
(734) 748-9584
Providing Home Inspection Services to Southeast Michigan
facebook
ITA Trained and Certified

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
FEMA finds mold in some of its manufactured homes dplummer Ancillary Inspection Services & Additional Topics 1 7/22/08 10:25 PM
AFCI in manufactured housing sfalvey Electrical Inspections 2 6/12/07 11:25 PM
Expansion/ contraction joints jlybolt Structural Inspections 13 5/31/07 6:03 PM


All times are GMT -4. The time now is 11:45 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts