Inspection this morning. A wood stove located basement is connected to Selkirk stainless steel metalbestos flue pipe. The flue penetrates the block foundation wall BELOW GRADE and runs vertically about 2 feet before emerging from the ground. It then runs vertically at the side of the home with normal above roof termination. Does anyone here know of flue standards that apply to this unusual installation? Moisture, corrosion, leakage, etc are some of the potential issues.
![]() ![]()
|
| Find an InterNACHI certified Illinois Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Well to start with it is suposed have 2 inches from combustibles MULCH is wood . I would call a supplier and ask about being buried It is probably not designed or made for that. Just when you think you seen it all , Then poof another one pops up .
|
|
#3
|
||||
|
||||
|
Remember to contact your local code office before proceeding with your installation. Some counties have abnormal requirements for clearances, and even types required for your appliance.
Some clearances that may differ from county to county are: Clearance to windows/doors/air inlets Clearance from the ground Clearance from a sidewalk/path Minimum roof termination distance (How far the pipe is above) LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#4
|
||||
|
||||
|
What i am wondering if there is covering flue pipe being buried Marcel, No way of checking when it rust out. Then there would be a problem with carbon monoxide .
This should interesting in the different views . |
|
#5
|
||||
|
||||
|
Wayne, I would have a hard time to believe that this installation is right.
Someone would have to work hard to convince me also. It is just plain wrong, and don't care if it is made of stainless steel, but the joints are not waterproof, they are water resistant to proper above ground installation. LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#6
|
||||
|
||||
|
Yes i was thinking that myself. I never seen it before and i have seen some strange things around here.
|
|
#7
|
|||
|
|||
|
That is an odd one.
I'd just call it too close to combustibles, refer it out, and be on my way but I am curious what possessed them to install it like that. InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#8
|
||||
|
||||
|
I think I found it here;
http://rds.yahoo.com/_ylt=A0geu_YTH9...ia_install.pdf 12" ground clearance required. LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#9
|
||||
|
||||
|
Thanks Marcel
Just added that to the old collection. |
|
#10
|
||||
|
||||
|
Your more than welcome my friend. Just hope it helps others.
LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#11
|
|||
|
|||
|
It may be different for a wood burner than the corn/pellet stove info posted but it still isn't right the way it is buried.
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#12
|
||||
|
||||
|
Quote:
I have never seen a Wood Stove here, but that is certainly an odd configuration--- Dale Duffy Inspect Arizona Companies, Inc. Phoenix Commercial Building Inspectors, Inc. Phoenix Thermal Imaging, Inc. Infraspection Certified Thermographer 602.402.5305 Home Hints eNews
InterNACHI 2007 U.S.A Member of the Year National Association of Commercial Building Inspectors, Inc. |
|
#13
|
|||
|
|||
|
Marcel,
Thanks for the information. I had to release the report before your post, but I did refer the flue installation to a qualified stove or chimney installation company. I know there is a good chance that corrosion and/or leakage has occurred in the buried section. The original installation was at least 11 years ago according to the owner. Must have been an amateur installation. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Do you put polybutylene in the Summary? | jfunderburk | Plumbing Inspections | 41 | 4/5/12 6:43 AM |
| Pellet stove help | chellickson | General Inspection Discussion | 23 | 8/19/10 1:23 AM |
| Is this allowed? | belliott | Plumbing Inspections | 4 | 7/15/09 6:40 PM |
| Identify ABS defective pipe | mcyr | Plumbing Inspections | 6 | 1/29/09 6:39 PM |
| What's Inside A Chimney | mcyr | Inspecting HVAC Systems | 14 | 9/17/08 6:11 PM |