Default Metalbestos flue pipe

Inspection this morning. A wood stove located basement is connected to Selkirk stainless steel metalbestos flue pipe. The flue penetrates the block foundation wall BELOW GRADE and runs vertically about 2 feet before emerging from the ground. It then runs vertically at the side of the home with normal above roof termination. Does anyone here know of flue standards that apply to this unusual installation? Moisture, corrosion, leakage, etc are some of the potential issues.


metalbestos-flue-pipe-metalbestos-001.jpg

metalbestos-flue-pipe-metalbestos-002.jpg

metalbestos-flue-pipe-metalbestos-003.jpg



Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
Find an InterNACHI certified Massachusetts Home Inspector (and anywhere else in North America)
  #2  
Old 10/13/09, 6:30 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,442
Default Re: Metalbestos flue pipe

Well to start with it is suposed have 2 inches from combustibles MULCH is wood . I would call a supplier and ask about being buried It is probably not designed or made for that. Just when you think you seen it all , Then poof another one pops up .
Reply With Quote
  #3  
Old 10/13/09, 9:08 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: Metalbestos flue pipe

Remember to contact your local code office before proceeding with your installation. Some counties have abnormal requirements for clearances, and even types required for your appliance.

Some clearances that may differ from county to county are:

Clearance to windows/doors/air inlets

Clearance from the ground

Clearance from a sidewalk/path

Minimum roof termination distance (How far the pipe is above)





Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #4  
Old 10/13/09, 9:13 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,442
Default Re: Metalbestos flue pipe

What i am wondering if there is covering flue pipe being buried Marcel, No way of checking when it rust out. Then there would be a problem with carbon monoxide .
This should interesting in the different views .
Reply With Quote
  #5  
Old 10/13/09, 9:24 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: Metalbestos flue pipe

Wayne, I would have a hard time to believe that this installation is right.
Someone would have to work hard to convince me also.

It is just plain wrong, and don't care if it is made of stainless steel, but the joints are not waterproof, they are water resistant to proper above ground installation.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #6  
Old 10/13/09, 9:30 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,442
Default Re: Metalbestos flue pipe

Yes i was thinking that myself. I never seen it before and i have seen some strange things around here.
Reply With Quote
  #7  
Old 10/13/09, 9:37 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: Metalbestos flue pipe

That is an odd one.

I'd just call it too close to combustibles, refer it out, and be on my way but I am curious what possessed them to install it like that.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #8  
Old 10/13/09, 9:50 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: Metalbestos flue pipe

I think I found it here;

http://rds.yahoo.com/_ylt=A0geu_YTH9...ia_install.pdf

12" ground clearance required.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #9  
Old 10/13/09, 9:58 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,442
Default Re: Metalbestos flue pipe

Thanks Marcel
Just added that to the old collection.
Reply With Quote
  #10  
Old 10/13/09, 10:04 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,356
Default Re: Metalbestos flue pipe

Your more than welcome my friend. Just hope it helps others.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #11  
Old 10/13/09, 10:07 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: Metalbestos flue pipe

It may be different for a wood burner than the corn/pellet stove info posted but it still isn't right the way it is buried.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #12  
Old 10/14/09, 1:23 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,687
Default Re: Metalbestos flue pipe

Quote:
Originally Posted by jevans View Post
Inspection this morning. A wood stove located basement is connected to Selkirk stainless steel metalbestos flue pipe. The flue penetrates the block foundation wall BELOW GRADE and runs vertically about 2 feet before emerging from the ground. It then runs vertically at the side of the home with normal above roof termination. Does anyone here know of flue standards that apply to this unusual installation? Moisture, corrosion, leakage, etc are some of the potential issues.


Attachment 32592

Attachment 32593

Attachment 32594
Hi John,

I have never seen a Wood Stove here, but that is certainly an odd configuration---
Reply With Quote
  #13  
Old 10/14/09, 6:11 AM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 519
Default Re: Metalbestos flue pipe

Marcel,
Thanks for the information. I had to release the report before your post, but I did refer the flue installation to a qualified stove or chimney installation company. I know there is a good chance that corrosion and/or leakage has occurred in the buried section. The original installation was at least 11 years ago according to the owner. Must have been an amateur installation.



Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Is this allowed? relliott Plumbing 4 7/15/09 7:40 PM
Identify ABS defective pipe mcyr Plumbing 6 1/29/09 7:39 PM
What's Inside A Chimney mcyr HVAC 14 9/17/08 7:11 PM
Pellet stove help chellickson General Inspection Discussion 22 8/10/08 5:41 PM
Do you put polybutylene in the Summary? jfunderburk Plumbing 36 11/27/07 12:56 AM


All times are GMT -4. The time now is 3:17 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts