Default Need help flashing top of replacement window on brick wall !!!

I recently replaced a window in a basement room on the end of our house. The outside wall is brick veneer over 10" block. The window is set in where it is flush with the outside wall. The window opening is not original to our 1960's ranch house (crudely chiseled out) and there is no steel lintel above the window ... we reinforced the top with dimensional lumber. Anyway, I want to trim the outside of the window and don't know how to flash above the top trim to keep rain from getting in behind it. This was a problem with the single pane aluminum window we took out ... the top of the window opening on the inside was a mess from water penetration. Simply caulking between the trim and the brick is unsightly (our brick has a very rough and uneven texture) and seems to be something that is only temporary with questionable success. Is there a more permanent way to retro flash above the window where you can totally eliminate any chance of water penetration and not have to constantly monitor the window to make sure water is not getting inside the window opening? It would really be great if it also looked professional and not like some yahoo like myself didn't know what he was doing. I'd provide a photo but I've got the window covered with plastic until I figure this out. Thanks for your help in advance!
Reply With Quote
  #2  
Old 3/30/08, 1:35 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: Need help flashing top of replacement window on brick wall !!!

"Let in" head flashing with sill pan would be the best way to go.
Don't forget the sides, also.

http://www.buildingscienceconsulting...gs_Windows.pdf



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 6/2/09 at 1:56 AM..
Reply With Quote
  #3  
Old 3/30/08, 8:23 PM
Bill Featherstone Bill Featherstone is offline
New User
 
Join Date: Nov 2007
Location: NW Arkansas
Posts: 39
Please Note: Bill Featherstone is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need help flashing top of replacement window on brick wall !!!

Quote:
Originally Posted by badair
"Let in" head flashing with sill pan would be the best way to go.
Don't forget the sides, also.

http://www.buildingscienceconsulting...gs_Windows.pdf
Thanks, Barry.

Excellent instructions for new construction. Unfortunately, I'm looking for a retro fit. The window in question is behind the black plastic in the attached photo.
Attached Thumbnails
need-help-flashing-top-replacement-window-brick-wall-house-shed-roof-1.jpg  
Reply With Quote
  #4  
Old 6/24/10, 8:41 PM
wbradbury wbradbury is offline
InterNACHI Member
 
Join Date: Jun 2010
Posts: 3
Default Re: Need help flashing top of replacement window on brick wall !!!

Bill, the way to retrofit flashings is to make a 1/2" deep saw kerf with a diamond blade either in your skil saw or 4" angle grinder, fill that with caulk and press in a standard head flashing that has a 3/8" lip bent at 90 degrees. To make the lip, go to the local hvac supply house and ask for a 3/8" folding bar. This will be about $25. Since the folding bar isn't going to be long enough, bend a 30 and move down overlapping 1" then 60 the same way and then 90. You can repair all the flashings on your house with this system.
Reply With Quote
  #5  
Old 6/24/10, 9:22 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,918
Default Re: Need help flashing top of replacement window on brick wall !!!

This might help.

http://www.coastalcontractor.net/cgi...icle.pl?id=149
Reply With Quote
  #6  
Old 6/26/10, 11:25 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,038
Default Re: Need help flashing top of replacement window on brick wall !!!

Well... it's been over two years! I wonder if Bill ever figured it out?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Poly being applied to Basement walls dvalley Interior Inspections 40 11/24/09 11:49 PM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 9:10 AM
Newbie here with a slab "standards" question Robert Young, #3 Structural Inspections 17 4/10/07 11:48 AM
No Brick Ties - Wall Buldge Stew Structural Inspections 1 4/22/06 7:56 AM


All times are GMT -4. The time now is 9:37 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts