Buck, the main problem is that it's nailed with roofing nails. You are allowed to use hangers one size under the dimension, so you can use 2x6 hangers with 2x8 material.
What you can't do is use fasteners that aren't designed for the purpose. Hanger nails are designed with metal alloys that are strong in shear (like cutting something with tin snips) . Roofing nails are weak in shear but designed with big heads to keep shingles from pulling out (withdrawal). The size of the hangers isn't the issue, it's the type of fasteners used. That's a defective installation. Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#20
|
|||
|
|||
|
Hey Ken
I thought that you fell of the face of the earth...... hope things are going welling in CO. Jeff |
|
#21
|
||||
|
||||
|
Hi Jeff,
I'm trying to get this roofing course complete and it's really about all I focus on these days. When I first got into the inspection business I took a correspondence course from (I won't say it). The tapes were was sooo boring that I had to fight to stay awake. The series of about 12 tapes took so long to make that the narrator had a full head of hair in the first tape and by the end of the last tape... he was bald! Anyway, I decided that if I ever had the chance to make educational videos, they were going to keep the viewer awake! I never thought that I'd have the opportunity, but now that I do... let's just say that most inspectors have never seen some of this stuff before. Lots of location shooting, lots of dealing with experts, lots and lots of research. It's been almost all I've worked on for 14 months and we're finally about to start shooting. I had a full head of hair when this project started, but I'm afraid that by the time it's finished... I'll be bald! Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#22
|
||||
|
||||
|
Well I am ready to accept a bald Ken, for I know it will be a good performance.
Thanks Ken and anxious to see it. LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#23
|
|||
|
|||
|
Here is a deck attached to a deck. Nice tie in between decks
They also knocked out all the support post on old deck. Found architects drawing on site, it was not followed. |
|
#24
|
||||
|
||||
|
Kenton,
Thanks! There has been some good discussion on the hanger, as planned. Thanks! again. Mid America Property Inspections, Inc. Shawnee, KS 66217 www.mapii.com NACHI # 05110992 KHIRB # 0110-0008 KS-Radon Cert.# KS-MS-0035 KS-Termite Cert. # 18933 M0-Termite Cert. # N 5033 |
|
#25
|
||||
|
||||
|
Thanks, Jeff, Marcel and Buck. It's always nice to hear from you guys. I miss participating on the boards, 'cause it's always nice to talk to old friends and meet new ones. Plus... I learn a lot from you all that I can pass on!
Except Marcel... bad comment on me going bald. Fie... Fie... Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
Last edited by kshepard; 2/17/10 at 11:30 PM.. |
|
#26
|
||||
|
||||
|
Quote:
Chuck Evans (TREC #7657) Level III Infraspection Institute Certified Infrared Thermographer (#8402) HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook Houston Thermal Inspections & Infrared Imaging Find us on Facebook Houston Home Inspector Houston, TX |
|
#27
|
||||
|
||||
|
The heads are too big and thin, Chuck, and 10d hanger nails would have the number "10" visible on the head. The heads on 8d and 10d hanger nails are real thick. These are thin heads. These are roofing nails.
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#28
|
||||
|
||||
|
Sorry Kenton,
LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
| Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#29
|
||||
|
||||
|
Just kiddin' Marcel. Always good to hear from you!
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Nice View of Heat Exchanger | bhamilton | Inspecting HVAC Systems | 2 | 3/2/09 2:28 PM |
| Nice loop and air gap | iniquette | Plumbing Inspections | 5 | 2/12/09 12:07 AM |
| Nice Job... nawt... | jcampbell | Electrical Inspections | 14 | 9/29/08 7:04 AM |
| New I-joist Hanger from Simpsons | mcyr | Structural Inspections | 6 | 9/18/07 7:51 PM |