  #61  
Old 1/18/09, 2:25 PM
Frank Albert's Avatar
Frank Albert Frank Albert is offline
Active Poster
 
Join Date: Oct 2007
Location: Richmond, Va.
Posts: 152
Please Note: Frank Albert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Please post questions about anything having to do with roofing

Quote:
Originally Posted by kshepard View Post
Do you have any theories about the source of the leakage?
I should have mentioned that I sometimes find the butt-joint leaks on dimensional shingles on 12/12 pitches too. The only common denominator there has been that there was a joint below where a dorma or other valley emptied onto the roof.
I now make sure no joints are in that area.
Reply With Quote
  #62  
Old 1/18/09, 2:48 PM
Frank Albert's Avatar
Frank Albert Frank Albert is offline
Active Poster
 
Join Date: Oct 2007
Location: Richmond, Va.
Posts: 152
Please Note: Frank Albert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Please post questions about anything having to do with roofing

BTW. Why do roofs get a 'Pass' when the starter course is a shingle that has been turned around instead of a shingle that had the tabs cut off and the sealer strip right on the bottom edge? Properly applied like that, and nailed all along that bottom edge, there is no way for the wind to damage the shingles.
Reply With Quote
  #63  
Old 1/18/09, 7:46 PM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,638
Default Re: Please post questions about anything having to do with roofing

Thanks Frank.

Good thread Kenton.



"I create controversy whether they like it or not"



Reply With Quote
  #64  
Old 1/18/09, 8:53 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,918
Default Re: Please post questions about anything having to do with roofing

Quote:
Originally Posted by Frank Albert View Post
BTW. Why do roofs get a 'Pass' when the starter course is a shingle that has been turned around instead of a shingle that had the tabs cut off and the sealer strip right on the bottom edge? Properly applied like that, and nailed all along that bottom edge, there is no way for the wind to damage the shingles.
To answer that question we need to go back here on this page; Architectural Graphic Standards
Copy right of 1970 Sixth Edition.




Now we can judge as to why methods are changing. Look at the weights of the material. Self-sealing tabs were not available in all brands.

Observe where the drip edge is, and the weight of the underlayment. Ice and water shield wasn't out yet.

Now explain to me why we have problems today without an ice and watershield underlayment.?

Explain why roofing today listed as 30 year will have seen it's better days in about 16-20 years opposed to shingles that I replaced on my own house that were 32 years old and still not leaking.

Food for thought.

Marcel
Reply With Quote
  #65  
Old 1/18/09, 11:07 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Please post questions about anything having to do with roofing

Quote:
Originally Posted by Frank Albert View Post
BTW. Why do roofs get a 'Pass' when the starter course is a shingle that has been turned around instead of a shingle that had the tabs cut off and the sealer strip right on the bottom edge? Properly applied like that, and nailed all along that bottom edge, there is no way for the wind to damage the shingles.
They shouldn't. It's common for the starter strip to be cut from shingles as opposed to using commercial starter strip, but that starter strip shouldn't measure more than 7"-8" wide. A full shingle as a starter strip is a defective installation.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #66  
Old 1/18/09, 11:20 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Please post questions about anything having to do with roofing

Quote:
Originally Posted by clawrenson View Post
I am considering re-roofing my home within the next year. It is currently a tar and gravel roof - reasonably flat with 2 roof drains and a scupper.

The tar and garvel roof is installed on an rigid insulation that is mechanically fastened to 5/8" t&g plywood roof sheathing. I was thinking about going to a single ply rubber self-adhesive system.

What are the comments - pros and cons regarding such a system?
Claude, I'm still trying to get through the asphalt shingle portion of this. I have seen some strident opinions on this and will do my best to address it which I reach the flat roof portion. If Frank or any other experienced roofers would like to jump in here, feel free!




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #67  
Old 1/19/09, 12:14 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Please post questions about anything having to do with roofing

Quote:
Originally Posted by Frank Albert View Post
Some appear to be a cause and effect of the self-sealing capabilities of the shingles. I've been in long discussions with other roofers. We 'believe' it's partially because water DOES wick under the shinlges at all joints/butts. Because of the shingles seal down capability, the water cannot run out from under the shingle. ( This is also why I fail any roof that used EG nails. They rot off in 6-8 years leaving holes.) The water works itself sideways until it finds relief in the form of a butt joint. It gets under the roof there. It will blister the roof and just flat find opening to leak into the home.
There are two fastening forces to understand.
1.The adhesive strips fasten the shingles to each other. These bonds are weaker with organic shingles, which may be an advantage when shingles need to expand and contract at a different rate than the plywood or OSB roof sheathing.

2.The fasteners (hopefully roofing nails rather than staples) fasten the shingles to the sheathing. The fasteners have certain corrosion-resistant properties depending on how they're made. Frank fails any shingles fastened with electro-galvanized coatings (the most common coating for roofing nails). Hot-dipped coated nails are better.

If you look at the adhesive strip of different brands of shingles, you'll see that some are a very solid strips and some are not so solid.

In preventing uplift (wind blow-off) this is not so important. What's important is that the wind not be able to break the tabs free to flap inthe wind, crease and break.

If you're depending on the adhesive strip to prevent moisture intrusion of the shingles from wind-driven rain, or considering that the adhesive strip may prevent moisture originating from the home interior beneath the shingles from drying to the outside, then the adhesive strip takes ona different purpose. I don't think the adhesive strip was designed as a moisture barrier, but to prevent uplift/wind blow-off.

If you assume that the adhesive strip cannot keep out wind-driven rain (which it won't, in every roof), then you have to assume that moisture will find its way past laps and through joints if the wind blows hard enough from the right direction.

In other words- Asphalt roofs are going to leak if the wind blows hard enough and there's enough rain. Yes, it depends on the design and maybe the installation. Some designs will leak easier than others.

The problem is.. there aren't always easy answers.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #68  
Old 1/19/09, 12:17 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Please post questions about anything having to do with roofing

Quote:
Originally Posted by mcyr View Post
To answer that question we need to go back here on this page; Architectural Graphic Standards
Copy right of 1970 Sixth Edition.




Now we can judge as to why methods are changing. Look at the weights of the material. Self-sealing tabs were not available in all brands.

Observe where the drip edge is, and the weight of the underlayment. Ice and water shield wasn't out yet.

Now explain to me why we have problems today without an ice and watershield underlayment.?

Explain why roofing today listed as 30 year will have seen it's better days in about 16-20 years opposed to shingles that I replaced on my own house that were 32 years old and still not leaking.

Food for thought.

Marcel
Marcel, we have the same edition, I'll be danged.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #69  
Old 1/19/09, 12:19 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Please post questions about anything having to do with roofing

Quote:
Originally Posted by mcyr View Post
To answer that question we need to go back here on this page; Architectural Graphic Standards
Copy right of 1970 Sixth Edition.




Now we can judge as to why methods are changing. Look at the weights of the material. Self-sealing tabs were not available in all brands.

Observe where the drip edge is, and the weight of the underlayment. Ice and water shield wasn't out yet.

Now explain to me why we have problems today without an ice and watershield underlayment.?

Explain why roofing today listed as 30 year will have seen it's better days in about 16-20 years opposed to shingles that I replaced on my own house that were 32 years old and still not leaking.

Food for thought.

Marcel
Actually Marcel, you would do us all a great favor if you would answer your own questions in your own words, please.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #70  
Old 1/19/09, 12:29 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Please post questions about anything having to do with roofing

Quote:
Originally Posted by Frank Albert View Post
I should have mentioned that I sometimes find the butt-joint leaks on dimensional shingles on 12/12 pitches too. The only common denominator there has been that there was a joint below where a dorma or other valley emptied onto the roof.
I now make sure no joints are in that area.
Again Frank, lots of us have not been roofers. I don't understand what you're describing. Are you making a point about butt joints in asphalt shingles in steep slope situations? Are you recommending avoiding any joints below valleys?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 1/19/09 at 12:33 AM..
Reply With Quote
  #71  
Old 1/19/09, 6:14 PM
Steven Woods's Avatar
Steven Woods Steven Woods is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: El Paso Tx
Posts: 167
Default Re: Please post questions about anything having to do with roofing

What causes these diagonal patterns with asphalt shingles?
Attached Thumbnails
please-post-questions-anything-having-do-roofing-roof-shingles.jpg  



Steven Woods
TREC Lic.# 9836

(915) 256-0615
swoods@hvinspections.com
Reply With Quote
  #72  
Old 1/19/09, 8:07 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Please post questions about anything having to do with roofing

Quote:
Originally Posted by swoods View Post
What causes these diagonal patterns with asphalt shingles?
Tha method of installation:



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #73  
Old 1/19/09, 10:14 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Please post questions about anything having to do with roofing

Some roofers call that a "racked" pattern. It's about speeding up the installation, so watch for other cost cutting measures (or lack of measures ).

John Kogel
www.allsafehome.ca

Kenton, I think he means no butt joints under the spot where water will splash from the eavestrough above.

Last edited by jkogel; 1/19/09 at 10:18 PM..
Reply With Quote
  #74  
Old 1/20/09, 12:01 AM
Frank Albert's Avatar
Frank Albert Frank Albert is offline
Active Poster
 
Join Date: Oct 2007
Location: Richmond, Va.
Posts: 152
Please Note: Frank Albert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Please post questions about anything having to do with roofing

Yes. If there is a joint, even on a dimensional shingle roof, below a valley, there is likely to be a leak. The 2" headlap will allow water in.
Reply With Quote
  #75  
Old 1/20/09, 12:06 AM
Frank Albert's Avatar
Frank Albert Frank Albert is offline
Active Poster
 
Join Date: Oct 2007
Location: Richmond, Va.
Posts: 152
Please Note: Frank Albert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Please post questions about anything having to do with roofing

I seldom do flat roofs anymore. And the fire hazard with APP is real.

I lean towards pitching the roof at least 1" per foot. I'm a firm believer in shedding the water.

I don't want to comment on what to use for the flat roof because I don't feel qualified to give a good answer. Other than 'Slope it some' with a rebuild or tapered insulation.
I do prefer EPDM. Loose laid, mechanically fastened on larger roofs, fully adhered on smaller ones.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
Asbestos jlybolt Exterior Inspections 38 7/17/07 2:13 AM
Ice Gaurd membrane dmacy Exterior Inspections 36 6/14/07 1:21 AM


All times are GMT -4. The time now is 12:17 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts