Default Question about chimney flashing

This does not look right to me. Shouldn't there be some sort of counter flashing, maybe a step flashing grouted in to the mortar joints? This flashing flares out at the top and is just filled with different types of sealant. It kinda looks like upside down drip edge.
P6210032 (Small).JPG (65.7 KB)

P6210034 (Small).JPG (72.2 KB)

P6210033 (Small).JPG (63.1 KB)

P6210035 (Small).JPG (72.9 KB)

Last edited by waksell; 9/4/07 at 9:01 PM..
Reply With Quote
  #2  
Old 6/21/07, 8:27 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is online now
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Default Re: Question about chimney flashing

It'll come to me in a minute. I've seen that before.

It reminds me of an upside-down piece of aluminum fascia covering for a siding job.

Good eye. It is not done properly and should have some counter flashing.

Bruce
Reply With Quote
  #3  
Old 6/21/07, 9:02 PM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Question about chimney flashing

I think in some cases were the surface is smoother, it is acceptable to not have a counter flashing, but to depend on mechanically fastening the flashing and using sealant. But up against coarse brick with deep mortar joints, I think a step flashing is necessary. Am I wrong?
Reply With Quote
  #4  
Old 6/21/07, 9:18 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Question about chimney flashing

Did the one below recently on a house that had just been re-roofed.

I pointed it out to the client that caulk was being relied on to prevent leaking and that it should be monitored regulary. It appeared to be a good grade of butly caulk which is very tough stuff. Not the way I would want it done.
Attached Thumbnails
question-chimney-flashing-chim-flash.jpg  
Reply With Quote
  #5  
Old 6/21/07, 9:20 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is online now
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Default Re: Question about chimney flashing

Quote:
Originally Posted by waksell
I think in some cases were the surface is smoother, it is acceptable to not have a counter flashing, but to depend on mechanically fastening the flashing and using sealant. But up against coarse brick with deep mortar joints, I think a step flashing is necessary. Am I wrong?
Sure you can; however, if that is aluminum siding material or a piece of metal roofing material, there will not be any metal flashing under the shingles. It looks like it is sitting on top and caulked.

Step flashing should have been used or it could have been counter-flashed with a saw-cut into the masory and sealed. That's how they do it in my town. It looks better than step and seals better IMO.

Bruce
Reply With Quote
  #6  
Old 6/21/07, 9:22 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Question about chimney flashing

Hi Wesley..What everyone says about the flashing is correct.
Unfortunatly if you come to chicago you will find it is done this way all the time.
My own roof was done this way as the roofing contractors cover up the old flashing rather than tearing it off.Common practice ,Yes, is it Right No.
They keep the price low doing it that way and the municipalities do not seem to have a problem with it.So check the books it is a write up.
Check with a lot of roofers and it is considered ok.
Reply With Quote
  #7  
Old 6/21/07, 9:57 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Question about chimney flashing

Quote:
Originally Posted by mlarson
Did the one below recently on a house that had just been re-roofed.

I pointed it out to the client that caulk was being relied on to prevent leaking and that it should be monitored regulary. It appeared to be a good grade of butly caulk which is very tough stuff. Not the way I would want it done.
Michael, it looks like they applied the flashing on top of the shingles and then caulked the edge of the flashing where it ended at the shingles.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #8  
Old 6/21/07, 9:59 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Question about chimney flashing

That's what see too. It was a decent roof job except for that. I assume it also caulked where the shingle meets the brick but that of course is hidden.
Reply With Quote
  #9  
Old 6/21/07, 11:12 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Question about chimney flashing

If you save a couple grand it may be worth it to keep an extra eye on the chimney flashing,but may be a good idea to warn the client.
Reply With Quote
  #10  
Old 6/21/07, 11:29 PM
rcarley rcarley is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Goldendale, WA
Posts: 49
Default Re: Question about chimney flashing

Try this. http://service.govdelivery.com/docs/...0051013_en.pdf
or this.
http://www.rd.com/content/openConten...58&pageIndex=1



Randie L. Carley
Simcoe Inspection Services, LLC
(509)-250-2617 Cell
(509)-773-4864 Office

"It's not our differences that divide us,

it's our inablility to recognize, accept and

ultimately, celebrate those differences."

http://www.simcoeinspections.com/

Last edited by rcarley; 6/21/07 at 11:44 PM..
Reply With Quote
  #11  
Old 6/22/07, 4:04 AM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Question about chimney flashing

Ok, this is what I reported;

Quote:
The chimney appears to be improperly flashed. I have never seen it done like this before. The material they used looks like upside down drip edge. See where the top edge of the flashing tilts out and away from the chimney. This is just begging for water to run between the flashing and the chimney, and down into the roof structure, ceiling, and wall. You can see the different colors of sealants used. I suspect that this has been a problem area in the past. Maybe why there is water damage at the ceiling above the fireplace. The proper way to flash a chimney is to install a base flashing that goes beneath the shingles on the sides and back of the chimney and bends up on the vertical walls of the chimney. Step flashings are then recessed into the chimney at the the mortar joints and bend down over the base flashing. The step flashing is sealed at the mortar joints. Its actually more complex than I make it sound. They are called step flashings because they look like steps as they follow the mortar joints going down the roof.
Here is a link;
http://service.govdelivery.com/docs/STPAUL/STPAUL_DeptLIEP/STPAUL_270/STPAUL_270_20051013_en.pdf

With this method of flashing, I would expect regular maintenance to be necessary.
End Quote:



I expect to get calls from my client and both agents on this one!!!
Reply With Quote
  #12  
Old 6/25/07, 5:39 PM
afrost afrost is offline
Active Poster
 
Join Date: Jan 2007
Location: Conway, NH
Posts: 356
Please Note: afrost is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question about chimney flashing

Quote:
Originally Posted by waksell
This does not look right to me. Shouldn't there be some sort of counter flashing, maybe a step flashing grouted in to the mortar joints? This flashing flares out at the top and is just filled with different types of sealant. It kinda looks like upside down drip edge.
P6210032 (Small).JPG (65.7 KB)

P6210034 (Small).JPG (72.2 KB)

P6210033 (Small).JPG (63.1 KB)

P6210035 (Small).JPG (72.9 KB)
that's poor execution of an unacceptable detail. although counter flashing is sometimes surface applied and sealant applied, this is not a suitable application. and since the installer doesn't care about what is plainly visible display of his work, i'd question what what hidden -- underlayment, overnailing, crooked nailing, missing nails. the top view of the shingles may lay pretty, but pretty isn't going to keep the weather out or keep them on in high winds. bad form.
Reply With Quote
  #13  
Old 6/25/07, 7:02 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Question about chimney flashing

Andy, good point, Bob, if you guys get a couple grand to flash a chimney, I'll be moving my company out your way!!!!

The proper way to flash a chimney on a re roof is to take a 4" grinder, grind out the mortar in the courses of the brick and install new lead flashing and reseal, not a big deal!!!!!
Reply With Quote
  #14  
Old 6/25/07, 7:10 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Question about chimney flashing

Quote:
Originally Posted by prussell

The proper way to flash a chimney on a re roof is to take a 4" grinder, grind out the mortar in the courses of the brick and install new lead flashing and reseal, not a big deal!!!!!
Exactly, and it is worth doing correctly.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #15  
Old 6/25/07, 7:23 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Question about chimney flashing

As Bob indicated, standard yes, right no. I think that would apply to this.






CAD File

A. Flashing at Base of Chimney This detail shows a typical installation using individual copper base sheets, as described above.



CAD File


B. Alternate Step Flashing Methods These sections illustrate two methods of stepped flashing. The one on the left uses individual copper base flashing sheets, and a one-piece cap. The other one uses the single piece base flashing with a two-piece cap flashing. Note the hooked edge on the base flashing to prevent water from running under the roofing material. The water is conducted instead to the end of the base flashing, over the apron, and onto the roof below.



CAD File

C. Chimney Flashing – Alternate This detail shows a second method of stepped flashing as described above.



CAD File

D. Chimney Cricket Flashing This detail illustrates the use of a cricket to divert water above the chimney to either side. The cricket can be a one piece design or a two piece, joined by a standing seam at its ridge.



CAD File


E. Chimney Flashing – Flat Roof Copper base flashing is attached to the roof deck before installation of the roofing. It extends at least 8" up the wall and at least 4" onto the roof, on all sides of the chimney. Copper cap flashing then covers the upper edge. All joints between base flashing sheets are soldered.

Thanks Peter

Marcel
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Deck flashing question scosta Exterior Inspections 7 10/15/07 11:21 PM
Chimney flashing sfalvey Exterior Inspections 1 10/5/07 8:12 AM
Floating Chimney Syndrome mcyr General Inspection Discussion 8 7/24/07 11:49 PM
Fireplace Enclosure jpope Interior Inspections 19 10/25/06 5:08 PM


All times are GMT -4. The time now is 1:40 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts