Fogarty Inspection Services Group of Knoxville TN Sean Fogarty Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.homeinspectionknoxville.com Last edited by sfogarty; 11/18/09 at 11:28 PM.. |
| Find an InterNACHI certified Delaware Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Didn't have 200 amp service. May have had a 200 amp panel but the 2/0 AL SEC would have made it 150 amp service.
Stephen Stanczyk Washington State Licensed Home Inspector # 221 President, Washington Association of Property Inspectors (WAPI) (253) 241-0602 calls answered until 10pm Pierce County -Thurston County - King County - Snohomish County |
|
#3
|
||||
|
||||
|
So why the 200 amp panel?
Fogarty Inspection Services Group of Knoxville TN Sean Fogarty Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.homeinspectionknoxville.com Last edited by sfogarty; 11/18/09 at 11:28 PM.. |
|
#4
|
||||
|
||||
|
Please Note:
rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
200 amp panel can be used up to 200 amp service.
|
|
#5
|
||||
|
||||
|
If the panel has a 200 amp breaker would it be okay?
|
|
#6
|
||||
|
||||
|
The meter can be 200, the panel can be 200, the main disconnect can be 200, and the SEC can be 2/0 aluminum.
You have 150 amp service. No defect. Stephen Stanczyk Washington State Licensed Home Inspector # 221 President, Washington Association of Property Inspectors (WAPI) (253) 241-0602 calls answered until 10pm Pierce County -Thurston County - King County - Snohomish County |
|
#7
|
||||
|
||||
|
Wouldn't that be like saying its okay to put a 30 amp breaker on 14 awg wire. What would be the difference.
Fogarty Inspection Services Group of Knoxville TN Sean Fogarty Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.homeinspectionknoxville.com |
|
#8
|
||||
|
||||
|
Not the same thing at all. With the SEC, it is supplying the main breaker. A smaller rated wire cannot overload a higher rated breaker.
Now when a breaker supplies a conductor, that is different. It is supplying more amperage than the conductor can handle. Home Inspection 101. Stephen Stanczyk Washington State Licensed Home Inspector # 221 President, Washington Association of Property Inspectors (WAPI) (253) 241-0602 calls answered until 10pm Pierce County -Thurston County - King County - Snohomish County |
|
#9
|
||||
|
||||
|
Please Note:
rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
In other words, the main disconect is not an overcurrent protection device for the SEC.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Florida Licensing Bill - Action Soon | jburkeson1 | Legislation, Licensing & Legal Issues for Inspectors | 250 | 7/1/10 5:50 PM |
| Liability question | jcahill | Legislation, Licensing & Legal Issues for Inspectors | 30 | 8/24/08 5:10 PM |
| Importance of the AHJ check | mcyr | General Inspection Discussion | 6 | 2/21/07 9:18 PM |