  #1  
Old 11/18/09, 11:00 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,043
Default Requirements for 200 amp?

Wrong place sorry!




Fogarty Inspection Services Group of Knoxville TN
Sean Fogarty
Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.homeinspectionknoxville.com

Last edited by sfogarty; 11/18/09 at 11:28 PM..
Reply With Quote
Find an InterNACHI certified Delaware Home Inspector (and anywhere else in North America)
  #2  
Old 11/18/09, 11:03 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,801
Send a message via AIM to sstanczyk
Default Re: Requirements for 200 amp?

Didn't have 200 amp service. May have had a 200 amp panel but the 2/0 AL SEC would have made it 150 amp service.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #3  
Old 11/18/09, 11:20 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,043
Default Re: Requirements for 200 amp?

So why the 200 amp panel?




Fogarty Inspection Services Group of Knoxville TN
Sean Fogarty
Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.homeinspectionknoxville.com

Last edited by sfogarty; 11/18/09 at 11:28 PM..
Reply With Quote
  #4  
Old 11/18/09, 11:29 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Requirements for 200 amp?

Quote:
Originally Posted by sfogarty View Post
So why the 200 amp panel?
200 amp panel can be used up to 200 amp service.
Reply With Quote
  #5  
Old 11/18/09, 11:46 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,585
Default Re: Requirements for 200 amp?

If the panel has a 200 amp breaker would it be okay?
Reply With Quote
  #6  
Old 11/18/09, 11:55 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,801
Send a message via AIM to sstanczyk
Default Re: Requirements for 200 amp?

The meter can be 200, the panel can be 200, the main disconnect can be 200, and the SEC can be 2/0 aluminum.

You have 150 amp service. No defect.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #7  
Old 11/19/09, 12:31 AM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,043
Default Re: Requirements for 200 amp?

Wouldn't that be like saying its okay to put a 30 amp breaker on 14 awg wire. What would be the difference.




Fogarty Inspection Services Group of Knoxville TN
Sean Fogarty
Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.homeinspectionknoxville.com
Reply With Quote
  #8  
Old 11/19/09, 12:51 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,801
Send a message via AIM to sstanczyk
Default Re: Requirements for 200 amp?

Not the same thing at all. With the SEC, it is supplying the main breaker. A smaller rated wire cannot overload a higher rated breaker.

Now when a breaker supplies a conductor, that is different. It is supplying more amperage than the conductor can handle.

Home Inspection 101.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #9  
Old 11/19/09, 1:06 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Requirements for 200 amp?

In other words, the main disconect is not an overcurrent protection device for the SEC.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Florida Licensing Bill - Action Soon jburkeson1 Legislation, Licensing & Legal Issues for Inspectors 250 7/1/10 5:50 PM
Liability question jcahill Legislation, Licensing & Legal Issues for Inspectors 30 8/24/08 5:10 PM
Importance of the AHJ check mcyr General Inspection Discussion 6 2/21/07 9:18 PM


All times are GMT -4. The time now is 10:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts