Have this home, it was built in 2006. It is a zero lot line home. There is a foundation wall that appears will be filled at some point in the future. I have not seen this before. I think the foundation wall is built out of block that has been covered with a cementatious type product. My question is shouldn't the fill be gravel for proper drainage? There are a few cracks, should I call out for a structural engineer? And shouldn't the exterior wall itself be coated with something so that water can not eventually get through? Any help would be appreciated.
Attached Thumbnails
retaining-wall-picture-010.jpg   retaining-wall-picture-011.jpg   retaining-wall-picture-003.jpg   retaining-wall-picture-012.jpg   retaining-wall-picture-013.jpg  


Last edited by rchorey; 10/23/08 at 12:48 PM.. Reason: term change
Reply With Quote
  #2  
Old 10/23/08, 11:18 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,850
Default Re: Retaining Wall

I for one do not see a retaining wall for to me that implies that the wall is 1. holding back earth and 2. engineered.

I would call out the step cracks in the block wall and reccomend sealing and monitoring, and I would reccomend keeping and eye on (Monitoring) the fill when the house next door is built.

Lets see what others say.
Reply With Quote
  #3  
Old 10/24/08, 8:11 AM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,638
Default Re: Retaining Wall

When it is back filled the finish grade should not be within 4" of the cement type product it might just be stucco.



"I create controversy whether they like it or not"



Reply With Quote
  #4  
Old 10/24/08, 9:05 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: Retaining Wall

The pony/knee wall is there to avoid exterior finish contact with soil as Carl said. This used to be an 8" industry-wide requirement now it's up to the AHJ.
I'd advise implementation of a drainage system and that the portion of wall below grade be sealed before soil is placed against it.

Brian's right-on about the step cracks unless deflection was present that doesn't show up in the photo, then an engineer would be an appropriate call.

Another case of stucco without weep screed, I see...



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #5  
Old 10/24/08, 3:10 PM
scorcoran scorcoran is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: St. Catharines, Ontario
Posts: 194
Default Re: Retaining Wall

Gentleman, what is the cause of the step crack?
Reply With Quote
  #6  
Old 10/24/08, 5:37 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Retaining Wall

Quote:
Originally Posted by scorcoran View Post
Gentleman, what is the cause of the step crack?
Step Cracks in a Concrete Block Wall


Vertical movement in a concrete block or brick wall might appear as either vertical cracks but more often as step cracks in which the crack pattern follows the mortar joints between the masonry units in a stair stepping pattern.


Step cracks are very common in concrete block walls. It is not unusual for cracks to originate as horizontal cracks, and over time, begin to step down, or up, along the mortar joints.

Typically, there is a tremendous amount of pressure pushing from the outside, whether it be expansive soil, tree roots or other catalysts.
If there is no pressure coming from the exterior, sometimes the wall bearing the load of the house simply cannot handle the weight, and begins to fatigue.

Unlike horizontal or vertical cracks where the opposing sides of the crack are pulling away from each other, in a step crack your wall is pulling apart from itself in all four directions and needs to be stabilized accordingly.

At this point, there is very little structural integrity left in the wall, and it needs to be stabilized as soon as possible. If bowing of the wall has not already occurred, it will most likely begin soon thereafter.

Hope this helps

Marcel
Reply With Quote
  #7  
Old 10/24/08, 6:04 PM
Ronald G. Chorey II's Avatar
Ronald G. Chorey II Ronald G. Chorey II is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Las Cruces, NM
Posts: 495
Default Re: Retaining Wall

Foundation engineer looked at it today. Needs a couple weeks to see if there is still movement. Also the soil around the footer is being undercut by water. There were also cracks in the garage slab, on the rear patio slab, there was separation of the rock wall away from the home and there was a small crack in the stucco at the parapet wall. He felt that it was good that I recommend an engineer, prior to the seller filling in dirt up against the wall.

He also stated that the soil that is put in needs to go in in steps, so that it can be compacted properly.
Attached Thumbnails
retaining-wall-crack-garage-floor.jpg   retaining-wall-crack-rear-patio.jpg   retaining-wall-separation.jpg   retaining-wall-small-crack-parapet-wall.jpg   retaining-wall-under-cutting-footer.jpg  

Reply With Quote
  #8  
Old 10/24/08, 8:39 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,850
Default Re: Retaining Wall

Quote:
Originally Posted by rchorey View Post
Foundation engineer looked at it today. Needs a couple weeks to see if there is still movement. Also the soil around the footer is being undercut by water. There were also cracks in the garage slab, on the rear patio slab, there was separation of the rock wall away from the home and there was a small crack in the stucco at the parapet wall. He felt that it was good that I recommend an engineer, prior to the seller filling in dirt up against the wall.

He also stated that the soil that is put in needs to go in in steps, so that it can be compacted properly.

Nice job Ronald.
Reply With Quote
  #9  
Old 10/25/08, 10:06 AM
scorcoran scorcoran is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: St. Catharines, Ontario
Posts: 194
Default Re: Retaining Wall

Thanks Marcel, couple more questions:

Does the step crack follow the mortar joints because the block is stronger than the mortar?

Also, could you just touch on how you would report a step crack? (verbiage)

Thanks,

Sean
Reply With Quote
  #10  
Old 10/25/08, 1:27 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Retaining Wall

Quote:
Originally Posted by scorcoran View Post
Thanks Marcel, couple more questions:

Does the step crack follow the mortar joints because the block is stronger than the mortar?

Also, could you just touch on how you would report a step crack? (verbiage)

Thanks,

Sean
Hi. Sean;

There is no absolute way to properly report cracks in a block foundation or concrete wall.
It all depends on the observations at hand for the moment. Every one is different but similar in certain characteristics.

To be narrated properly, the information must be combined with specific on-site observations at the particular building in order to form a reliable opinion about the condition of that building's foundation. Anyone having concern regarding the structural stability, safety, or damage of a building, foundation or other components, should consult a qualified expert.

During a site inspection of cracked blocks, there are numerous variables to take into account and many unknowns.

Other than the fact that the crack relates to movement of some sort, the exact reason as to why it cracked is unknown to even the professionals to some extent.

In some cases, step cracking could be something as simple as the wrong type of mortar used when it was built. The stronger the mortar, the less adhering properties it has with the block work.
So basically, the safe way of reporting would be that there appears to be some movement in the block foundation based on the evidence of the step cracking.

I would recommend further evaluation by a foundation expert or engineer and move on.

Hope this helps.

Marcel
Reply With Quote
  #11  
Old 10/25/08, 3:00 PM
scorcoran scorcoran is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: St. Catharines, Ontario
Posts: 194
Default Re: Retaining Wall

Thank you Marcel. I have to say I very much value your contributions on this site. I've done a search of all your posts and they have added considerably to my knowledge base! Thank you for taking the time to answer my noobie questions!
Reply With Quote
  #12  
Old 10/26/08, 8:44 AM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,638
Default Re: Retaining Wall

If they were to put moisture barrier and lath on all CMU the cracks would be covered.

Unless they were so severe they cracked the stucco.

Moisture penetration and freeze and thaw cycles can really cause a lot of problems.



"I create controversy whether they like it or not"



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Moisture Management mcyr Exterior Inspections 15 9/8/08 1:11 PM
VIDEO--Bowed Basement Wall, Cracks etc john bubber Structural Inspections 75 7/21/08 6:25 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
egress window well retaining wall Ivor Findlay Structural Inspections 4 5/23/07 11:03 AM
Newbie here with a slab "standards" question Robert Young, #3 Structural Inspections 17 4/10/07 11:48 AM


All times are GMT -4. The time now is 5:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts