  #1  
Old 1/3/09, 9:08 AM
J. Christopher Weise J. Christopher Weise is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Woodstock, GA
Posts: 169
Default Roof design

Client not at inspection. New home with no current leaks. Large roof area channeled to small area.

Would you mention it in report?
If you report it, what might you say?
Is it shingled OK for the design condition?
What might be done differently?
Attached Thumbnails
roof-design-img_0684-440.jpg   roof-design-img_0680-440.jpg  
Reply With Quote
  #2  
Old 1/3/09, 9:47 AM
Bobby Hamilton's Avatar
Bobby Hamilton Bobby Hamilton is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Austintown, OH
Posts: 1,223
Default Re: Roof design

Something just doesn't look right, but I've only had one cup of coffee this morning. I don't think I would have chosen the basket weave method of shingling in this area as it looks alright on the right side of the photo but the left side is messed up. Is that the tar strip showing on the left valley?
roof-design-img_0680-440-1-.jpg

I would rather see the straight cut line in this situation as it looks like water may go under some of the shingles the way it was put together.

Just curious, do you have a farther away shot of the house?



Bobby Hamilton
Bloodhound Home Inspection Services
Youngstown Home Inspection
Austintown Ohio Home Inspection


Providing home inspections, state licensed termite inspections and radon testing in Youngstown, Boardman, Canfield, Poland, Howland, Warren and surrounding Northeast Ohio areas.
Reply With Quote
  #3  
Old 1/3/09, 9:58 AM
J. Christopher Weise J. Christopher Weise is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Woodstock, GA
Posts: 169
Default Re: Roof design

I believe that is the tar strip. Roofer did not quite get the lap right. My concern is the amount of drainage channeled into such a small area and then dumped horizontally onto the adjacent roofing.
Attached Thumbnails
roof-design-img_0683-440.jpg  
Reply With Quote
  #4  
Old 1/3/09, 10:09 AM
Bobby Hamilton's Avatar
Bobby Hamilton Bobby Hamilton is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Austintown, OH
Posts: 1,223
Default Re: Roof design

I see your point, but unfortunately, due to its design, there doesn't appear to be any other way to route it. I would just mention that "Due to design in the roof this area may wear faster than other parts of the roof as more water will come across this area" If you get ice down there (I'm in Ohio so it's a given for me) this would be an area where I would probably see an ice dam form and roll up the roof.



Bobby Hamilton
Bloodhound Home Inspection Services
Youngstown Home Inspection
Austintown Ohio Home Inspection


Providing home inspections, state licensed termite inspections and radon testing in Youngstown, Boardman, Canfield, Poland, Howland, Warren and surrounding Northeast Ohio areas.
Reply With Quote
  #5  
Old 1/3/09, 11:52 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Roof design

"A new home has no "history" and its inspection can be difficult as many defects have not had time to reveal themselves. During the first year of occupancy the home should be monitored for deficiencies such as, but not limited to, plumbing leaks, cracking, condensation, and water penetration. Attic areas, windows, doors and foundation areas should be monitored seasonally and after periods of rain or storms."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 1/3/09, 12:04 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof design

When the snow builds up there (and subsequently melts) it may cause a mess.

Thinking out loud....would a cricket help there? Least the water would have some direction, rather than pooling there? Hope they have ice and water shield all over that area.

My guess is that gutter will overflow during any significant rain.
Reply With Quote
  #7  
Old 1/3/09, 12:07 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,708
Send a message via Yahoo to jfunderburk
Default Re: Roof design

I say give it time and don't make a big deal out of it unless you have concrete evidence or experience to rely on. The home is under warranty. Any issue should reveal itself within the first year.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 1/3/09, 3:30 PM
J. Christopher Weise J. Christopher Weise is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Woodstock, GA
Posts: 169
Default Re: Roof design

Thanks all. I'm sure that 6' gutter won't handle much rain and will spill even in the smallest summer storm. Not much worry about snow and ice here. Just wasn't sure, since we don't predict the future, what to mention in report. No current leaking and all. Basically said to monitor for possible leaking and excessive wear in that area. Not sure how the buyer handled it with the builder.

Thanks again.
Reply With Quote
  #9  
Old 1/3/09, 5:03 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,899
Default Re: Roof design

I might mention that the outlet tube in the first picture terminates at the shingles, this may cause the shingles in this area to age faster than the rest of the roof.

Hard to tell with such a small picture but you might recommend an addition section of downspout be installed to control the water in this area so it terminates inside the lower gutter.
Reply With Quote
  #10  
Old 1/3/09, 5:36 PM
Scott Widick's Avatar
Scott Widick Scott Widick is offline
InterNACHI Member
 
Join Date: Sep 2007
Location: Pueblo West, CO
Posts: 313
Send a message via MSN to swidick
Default Re: Roof design

In our area a roof design like this would have Ice and Water shield installed in these areas for added protection.
Reply With Quote
  #11  
Old 1/12/09, 12:09 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,407
Send a message via ICQ to kshepard
Default Re: Roof design

If that area is less than 2&12 the slope is too low and should not have asphalt shingles installed.
Even if it's not low-slope, it has two extreme changes in pitch which are vulnerable to leakage and which should have extra underlayment or metal flashing installed. Unless I could confirm that it was installed with other than the usual underlayment system, I would call it out as an area with the potential for leakage.
That whole area should have had a waterproof membrane installed. Polymer modified bitumen.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 1/14/09 at 7:36 PM..
Reply With Quote
  #12  
Old 1/12/09, 5:57 AM
J. Christopher Weise J. Christopher Weise is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Woodstock, GA
Posts: 169
Default Re: Roof design

Thanks Kenton, I did follow up with the client's agent and the builder pulled the shingles and laid some sort of metal flashing. How it was done I have no idea but at least the potential for leaks was reduced. I"m sure, due to the poor design, that future problems will occur. At least the buyer is aware of it and hopefully, but not likely, will monitor the area for excessive wear and possible leaks. The pitch was over 2/12.
Reply With Quote
  #13  
Old 1/12/09, 7:08 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof design

[quote=jweise;463400]Client not at inspection. New home with no current leaks. Large roof area channeled to small area.

Would you mention it in report?
If you report it, what might you say?
Is it shingled OK for the design condition?
What might be done differently? [/quote]

Bring the architect back to the house and rub his nose in it!! They work way to much on the "art" design side of the building and not enough on the technical/practical/commom sense side. There should have been a design note about building a slope (or "cricket" as someone mentioned) to drain water from under the gable dormer window and the 2 slopes that appear to meet in the valley there with no grade/slope to it.
Reply With Quote
  #14  
Old 1/12/09, 1:04 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof design

I notice the downspout from the upper roof is cut short and facing sideways.

Those tiles will be pushed up.

What a dumb design.
Reply With Quote
  #15  
Old 1/12/09, 3:52 PM
J. Christopher Weise J. Christopher Weise is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Woodstock, GA
Posts: 169
Default Re: Roof design

Yep. My brother graduated from Kent back in the shooting 60's as an architect. Only learned to draw pretty houses. Nothing at all about practical or working design. I don't think I ever built a house off a plan that did not have to be redesigned in some way in order to work efficiently or at all.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 9:10 AM


All times are GMT -4. The time now is 3:45 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts