Default Re: Roof help ?

I would never leave a job that way, even if the old flashing is still there, water will get trapped behind the new flashing and will rot the siding. Tomorrow when we get that Nor Easter think about where the water is going, it will go behind the flashing then where? As an inspector I would call this out, as a contractor I would be ashamed of myself.
Reply With Quote
  #17  
Old 4/14/07, 9:26 AM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Roof help ?

PS Not to mention, it looks terrible.
Reply With Quote
  #18  
Old 4/14/07, 9:50 AM
Garry Fowler Garry Fowler is offline
New User
 
Join Date: Apr 2007
Location: Maine
Posts: 5
Please Note: Garry Fowler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof help ?

Thanks and yes it does look terrible.
Reply With Quote
  #19  
Old 4/15/07, 8:11 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,788
Default Re: Roof help ?

Hi. Gary, and it is unfortunate to see people paying for the type of work depicted in the photos you share to us.

Where in Maine are you from?

In looking at your pictures the siding on the sidewall gable should have been cut up about 4" above the roof in order to apply the sidewall flashing properly.

The flashing would have been bent metal of at least 22 gauge and not 26 like it appears to be. The vertical leg of the flashing would be 6" and then run 4"-5" horizontal, 45 degrees back down and 2" horizontal on the roof where it would be fastened.

In your picture of the sidewall, is the house crooked or is the roof metal crooked? There appears to be quite a differential in alignment with the side wall?

I would reccommend that you consult with a Prominent roofing Contractor with expertize in metal roofing and flashings.

I think you will find that you are being taken over the coals with this type of shoddy work.

Marcel
</IMG>
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
A little on the Commercial side of things. mcyr General Inspection Discussion 457 8/1/09 10:50 AM
Cracked shingles pwigle Exterior Inspections 54 4/23/09 11:52 PM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 8:10 AM
Ice Gaurd membrane dmacy Exterior Inspections 36 6/14/07 12:21 AM
Roof Repair? Maybe NO jhagarty Exterior Inspections 9 2/15/07 1:19 AM


All times are GMT -4. The time now is 1:46 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts