Default Roof question

I did an inspection of a 2/12 roof today with my thermal camera and moisture meters. The current owner found 4 leaks, and I found 6 or so places of water intrusion.
The roof coverings are owens corning 50 yr with Sure-nail. They put ice guard on entire roof surface before shingle installation according to manufacturers installation. Entire roof replaced in Sept 07. Previous roof was old 3-tab that never leaked.

The problem appears to be the water is going under the shingles, due to low slope, and running into nail space to drain onto sheathing.

Has anyone seen this issue before?



Ashburn Inspections
724-516-1665
Reply With Quote
  #2  
Old 12/15/07, 2:41 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Roof question

A leak in a low-slope roof? Yes. Nails punch holes in Ice and Weather Shield, nails expand and contract until the gap around the nail is big enough to admit water. There's your leak.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #3  
Old 12/15/07, 2:43 PM
mashburn's Avatar
mashburn mashburn is offline
InterNACHI Member
 
Join Date: May 2006
Location: Pittsburgh, PA
Posts: 286
Default Re: Roof question

I just thought maybe there was some other explanation other than nail expansion.

thank you Kenton



Ashburn Inspections
724-516-1665
Reply With Quote
  #4  
Old 12/15/07, 2:55 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,611
Default Re: Roof question

Quote:
Originally Posted by mashburn
I just thought maybe there was some other explanation other than nail expansion.

thank you Kenton
The nail expansion on Ice and water shied is new to me .
I would have though that there could be some other concern causing this difficulty .
http://www.na.graceconstruction.com/...2693-RCCMC.pdf


...Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #5  
Old 12/15/07, 3:08 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Roof question

Quote:
Originally Posted by mashburn
The problem appears to be the water is going under the shingles, due to low slope, and running into nail space to drain onto sheathing.

Has anyone seen this issue before?
Michael,

Sounds like ice damming to me. Are you sure that the ice and water shield was installed properly or are you guessing?

Reply With Quote
  #6  
Old 12/15/07, 3:10 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Roof question

Hi to all,

I also very much doubt that the problem is nails through the ice and water shield, especialy on a new roof, the product is designed to have a "memory" so that it closes back around nials and screws, thats the whole point of it.

My guess would be either a very poor installation of the Ice and water layer, or that it is missing in some key areas like flashing locations.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #7  
Old 12/15/07, 3:12 PM
mashburn's Avatar
mashburn mashburn is offline
InterNACHI Member
 
Join Date: May 2006
Location: Pittsburgh, PA
Posts: 286
Default Re: Roof question

When I got to the inspection they were removing some of the shingles to replace. The owner showed me the Owens Corning installation instructions that he printed for his roofer to install. He made sure that the roofer, his friend, followed his instructions.

The leaks were coming form all over the roof surface not any areas with flashing, only 3 terminations on this affected side of roof. Ice damming has not hapened as we have not had snow yet.



Ashburn Inspections
724-516-1665

Last edited by mashburn; 12/15/07 at 3:20 PM..
Reply With Quote
  #8  
Old 12/15/07, 5:24 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Roof question

Now you've got me curious.

What was the roofers verdict? Did you speak to him?
Reply With Quote
  #9  
Old 12/15/07, 5:42 PM
mashburn's Avatar
mashburn mashburn is offline
InterNACHI Member
 
Join Date: May 2006
Location: Pittsburgh, PA
Posts: 286
Default Re: Roof question

Roofer has no idea. They all like the idea of expanding nails.
I cannot wrap my head around this issue.



Ashburn Inspections
724-516-1665
Reply With Quote
  #10  
Old 12/15/07, 5:44 PM
mashburn's Avatar
mashburn mashburn is offline
InterNACHI Member
 
Join Date: May 2006
Location: Pittsburgh, PA
Posts: 286
Default Re: Roof question

They owner just called and he told me he is going to cover the entire roof with metal standing seam. Quite a $$$. not sure who is going to pay.
I'll update when I get more info.
Thank you all for your help.



Ashburn Inspections
724-516-1665
Reply With Quote
  #11  
Old 12/15/07, 6:52 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,608
Default Re: Roof question

Quote:
Quote:
Originally Posted by mashburn
The roof coverings are owens corning 50 yr with Sure-nail. They put ice guard on entire roof surface before shingle installation according to manufacturers installation. Entire roof replaced in Sept 07. Previous roof was old 3-tab that never leaked.
Was this applied over the old 3-tab or was it a tear-off?
Also, is there any ventilation under the roof deck?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #12  
Old 12/15/07, 9:10 PM
ckratzer ckratzer is offline
Active Poster
 
Join Date: Mar 2005
Posts: 256
Please Note: ckratzer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof question

It is risky to put shingles on any pitch under 4/12.

A roll roofing product would have been a better choice to prevent leaks.
Reply With Quote
  #13  
Old 12/15/07, 9:26 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,846
Default Re: Roof question

What he just said. Ive always heard and have read on bundles anything less than a 3 on 12 pitch is not recommended using shingles. I have seen a bunch of them too and they almost always leaked.
Reply With Quote
  #14  
Old 12/16/07, 12:19 AM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,091
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof question

Quote:
Originally Posted by mashburn
Roofer has no idea. They all like the idea of expanding nails.
I cannot wrap my head around this issue.
Now that is interesting. A licensed roofer with no idea where the leaks are originating? Time to get another roofer, maybe one who is not a personal friend of the owner.

Two more questions? Is the current roofing contractor licensed in that field of expertise? Was a permit pulled and finaled on the existing comp shingle roofing system?

Somethings not kosher when the homeowner has to provide roof installation instructions to the roofing contractor.
Reply With Quote
  #15  
Old 12/16/07, 12:21 AM
mashburn's Avatar
mashburn mashburn is offline
InterNACHI Member
 
Join Date: May 2006
Location: Pittsburgh, PA
Posts: 286
Default Re: Roof question

It was a tear off.
Ventilation was supplied by ridge/soffit vents & small gabels.

In my county PA requires no licensing for contracting. Even though a barber and nail manicurist need a license if you can believe that.



Ashburn Inspections
724-516-1665
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Roof Repair? Maybe NO jhagarty Exterior Inspections 9 2/15/07 1:19 AM
Vaulted Ceiling Insulation rcooke Canadian Inspectors 4 1/22/07 12:24 PM
Wood shake roof question jclark1 Exterior Inspections 4 9/11/06 9:23 PM
Ladder safety by Rick Bunzel gbeaumont Miscellaneous Discussion for Inspectors 9 3/24/06 5:24 PM


All times are GMT -4. The time now is 1:46 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts