Default Roof Ventilation ??

Hi Inspectors,

I just looked at this house, which is Brand new construction. I am puzzled on something. There are no soffit vents, and there are no roof vents on the house! Also, there are no gable vents.

Am I COMPLETELY missing something,or is this just plain bad construction. I was under the assumption that you needed 1sq foot of ventilation for every 150sq feet of attic.

The house is a rancher with a finished basement. I looked in the attic and did not see any kind of venting system? I do not know what code is in this area on this, but it just seems wrong any way you slice it.

What are your thoughts on this, I would appreciate your input!
Attached Thumbnails
roof-ventilation-100_3423.jpg   roof-ventilation-100_3426.jpg  
Reply With Quote
  #2  
Old 12/27/06, 2:59 PM
lcapaul's Avatar
lcapaul lcapaul is offline
Active Poster
 
Join Date: Jun 2005
Location: Rathdrum, ID
Posts: 1,581
Please Note: lcapaul is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof Ventilation ??

Quote:
Originally Posted by gbrasseur
Hi Inspectors,

I just looked at this house, which is Brand new construction. I am puzzled on something. There are no soffit vents, and there are no roof vents on the house! Also, there are no gable vents.

Am I COMPLETELY missing something,or is this just plain bad construction. I was under the assumption that you needed 1sq foot of ventilation for every 150sq feet of attic.

The house is a rancher with a finished basement. I looked in the attic and did not see any kind of venting system? I do not know what code is in this area on this, but it just seems wrong any way you slice it.

What are your thoughts on this, I would appreciate your input!
Is it a "Sealed Attic"?

http://www.michigancodes.com/module13.htm

http://www2.dupont.com/Tyvek_Constru...AWSBK14127.pdf
Reply With Quote
  #3  
Old 12/27/06, 3:49 PM
gbrasseur's Avatar
gbrasseur gbrasseur is offline
Active Poster
 
Join Date: Mar 2006
Location: Colorado Springs, CO
Posts: 418
Please Note: gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof Ventilation ??

Lewis,

I don't think it would fall in the "sealed attic" catagory because there is no ridge vent? It seem from what you sent (and thank you), there would need to be a ridge vent.
Reply With Quote
  #4  
Old 12/27/06, 4:45 PM
lcapaul's Avatar
lcapaul lcapaul is offline
Active Poster
 
Join Date: Jun 2005
Location: Rathdrum, ID
Posts: 1,581
Please Note: lcapaul is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof Ventilation ??

Then how about an unvented attic system, SIPS, or one of the foams?

http://www.lsuagcenter.com/en/family...iespage-16.htm

http://www.amvic-pacific.com/Downloa...tics-Roofs.pdf

http://www.buildingscienceseminars.c...entilation.pdf
Reply With Quote
  #5  
Old 12/27/06, 9:02 PM
ekartal6 ekartal6 is offline
Active Poster
 
Join Date: Oct 2006
Location: Schaumburg, IL
Posts: 1,094
Please Note: ekartal6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof Ventilation ??

Greg,

Could it be the home has a continuous open vent under the drip edge?
Reply With Quote
  #6  
Old 12/27/06, 9:11 PM
gbrasseur's Avatar
gbrasseur gbrasseur is offline
Active Poster
 
Join Date: Mar 2006
Location: Colorado Springs, CO
Posts: 418
Please Note: gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof Ventilation ??

Erol,

I didn't see any "daylight" when I was viewing the attic.
Reply With Quote
  #7  
Old 12/27/06, 9:25 PM
ekartal6 ekartal6 is offline
Active Poster
 
Join Date: Oct 2006
Location: Schaumburg, IL
Posts: 1,094
Please Note: ekartal6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof Ventilation ??

I've only seen this vent system once and it was not nearly as easy to see light as we do soffit vents with baffles around the insulation.

Just a thought:

http://www.airvent.com/homeowner/pro...ventedDE.shtml

However it still doesn't explain why there's no roof ventilation unless somehow you may have accidentally missed the vents because they are on one side of the house only. But like you had mentioned, no visible daylight...

Erol
Reply With Quote
  #8  
Old 12/27/06, 9:30 PM
gbrasseur's Avatar
gbrasseur gbrasseur is offline
Active Poster
 
Join Date: Mar 2006
Location: Colorado Springs, CO
Posts: 418
Please Note: gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof Ventilation ??

Erol,

Actually I walked the house 3 times looking everywhere, and did not see any Roof vents or soffit vents. I walked it 3 times because I think I was in disbelief.
Reply With Quote
  #9  
Old 12/27/06, 9:33 PM
ekartal6 ekartal6 is offline
Active Poster
 
Join Date: Oct 2006
Location: Schaumburg, IL
Posts: 1,094
Please Note: ekartal6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof Ventilation ??

I believe you, just one last shot at it.
Reply With Quote
  #10  
Old 12/28/06, 2:36 AM
gbrasseur's Avatar
gbrasseur gbrasseur is offline
Active Poster
 
Join Date: Mar 2006
Location: Colorado Springs, CO
Posts: 418
Please Note: gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof Ventilation ??

Any other "takers" on this one?
Reply With Quote
  #11  
Old 12/28/06, 6:43 AM
scosta's Avatar
scosta scosta is offline
Active Poster
 
Join Date: Oct 2005
Location: North Royalton, Oh
Posts: 186
Please Note: scosta is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof Ventilation ??

Ive seen this type before, you can see any of the "holes" unless you get up on a ladder.

http://www.craftsmansiding.com/chartsof.htm

Steve
Reply With Quote
  #12  
Old 12/28/06, 9:20 AM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof Ventilation ??

Quote:
Originally Posted by scosta
Ive seen this type before, you can see any of the "holes" unless you get up on a ladder.

http://www.craftsmansiding.com/chartsof.htm

Steve
possible...however, without any outlet venting toward the top of the structure, i hardly see how it could be affective in this application.
Reply With Quote
  #13  
Old 12/28/06, 11:18 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Roof Ventilation ??

A few years ago I did an inspection on a eleven year old home the roof was done ,curling most granule's gone .
I went into attic and saw no roof vents .
Wondered how I could be so stupid to walk the roof completely and not notice no vents .
Went back out side and looked from the ground and counted 4 roof vents went back into attic they had not cut holes four vents and no ventilation .
Shingles gone completely in 11 years no leaks yet that I could see.

Roy Cooke . Royshomeinspection.com



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #14  
Old 12/28/06, 1:40 PM
gbrasseur's Avatar
gbrasseur gbrasseur is offline
Active Poster
 
Join Date: Mar 2006
Location: Colorado Springs, CO
Posts: 418
Please Note: gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof Ventilation ??

Wow Roy,

That is what I see this roof doing if not corrected to proper ventilation.
Thanks for sharing that.
Reply With Quote
  #15  
Old 1/2/07, 8:52 AM
John J. Passailaigue, Jr.'s Avatar
John J. Passailaigue, Jr. John J. Passailaigue, Jr. is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Auburn, AL
Posts: 409
Send a message via AIM to jpassailaigue
Default Re: Roof Ventilation ??

Greg,

I have seen an attic in town that has nor roof ventilation as well. There was insulation (spray in) on the plywood on the ceiling in the attic. Believe it or not, the city inspectors made this builder run a bigger air conditioner to condition the attic area. YES. The city would not give a C.O. until this attic was heated and cooled. First I've ever seen or heard of but thought I would share.



John J. Passailaigue Jr.
NACHI05062580
Auburn Home Inspection
Auburn, Alabama
WAR EAGLE!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
A little on the Commercial side of things. mcyr General Inspection Discussion 457 8/1/09 10:50 AM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 8:10 AM
Ice Gaurd membrane dmacy Exterior Inspections 36 6/14/07 12:21 AM
Roof Repair? Maybe NO jhagarty Exterior Inspections 9 2/15/07 1:19 AM