Default Roof ventilation (or lack there of)

House built in '71. Gable & Hip roof. 2' wooden soffits around the perimeter of home. There were only roof vents. No gable or soffit vents whatsoever. Attic looked great with no history/signs of trapped moisture whatsoever (plywood sheathing/ 2 x 6 rafters, built well). The insulation was 12 or so inches of loose fill cellulose. Electric ceiling heat.

Can someone please try and enlighted me on why there's no soffit or additional vents to work with roof vents?

I've seen plenty of attics with obvious ventilation concerns, but I am a bit curious about this. Would you suggest additional ventilation?


Any help/insight is always appreciated!
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/7/10, 11:00 AM
John E. Mullarkey John E. Mullarkey is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: Sarasota, Fl
Posts: 349
Default Re: Roof ventilation (or lack there of)

I have 2 houses that are similarly vented. Dry as a bone and no problems in a sub tropical climate. That type of roof venting was very common down here.
Reply With Quote
  #3  
Old 2/7/10, 12:43 PM
Bobby G. Michael Bobby G. Michael is offline
InterNACHI Member
 
Join Date: Jan 2010
Posts: 187
Default Re: Roof ventilation (or lack there of)

I agree with John.



Alabama Home Inspections
www.thebirminghamhomeinspector.com
Home Inspections in Birmingham, Montgomery, Huntsville, and Tuscaloosa.
Reply With Quote
  #4  
Old 2/7/10, 4:17 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Roof ventilation (or lack there of)

Quote:
Originally Posted by jmullarkey View Post
I have 2 houses that are similarly vented. Dry as a bone and no problems in a sub tropical climate. That type of roof venting was very common down here.
With asphalt shingles?

Anyone up north?
Reply With Quote
  #5  
Old 2/7/10, 5:39 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Roof ventilation (or lack there of)

I admit I have seen homes with lack of ventilation that had no damage and would like to know myself.

My first thought is life of shingles is reduced form over heating in the summer.

It is still recommended.
Reply With Quote
  #6  
Old 2/8/10, 6:22 PM
Sonny C. Shipler Sonny C. Shipler is offline
InterNACHI Member
 
Join Date: May 2007
Location: Beloit, WI
Posts: 79
Default Re: Roof ventilation (or lack there of)

Was there a vapor barrier under the insulation?
Reply With Quote
  #7  
Old 2/8/10, 7:08 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Roof ventilation (or lack there of)

Ventilation means air movement, what happens when air moves ???
Reply With Quote
  #8  
Old 2/8/10, 7:18 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Roof ventilation (or lack there of)

Quote:
Originally Posted by sshipler View Post
Was there a vapor barrier under the insulation?
No VB.
Reply With Quote
  #9  
Old 2/8/10, 7:43 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Roof ventilation (or lack there of)

The ceiling electric heat is a factor. That is your thermal barrier and will produce sufficient "ventilation" as well as a lack of humidity loss through the ceiling.

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #10  
Old 2/9/10, 7:07 AM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Roof ventilation (or lack there of)

Insulating exterior wall top plate from attic

This is from the site Kevin recommended in another thread.
Reply With Quote
  #11  
Old 2/17/10, 12:12 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Roof ventilation (or lack there of)

Quote:
Originally Posted by jfrederick View Post
House built in '71. Gable & Hip roof. 2' wooden soffits around the perimeter of home. There were only roof vents. No gable or soffit vents whatsoever. Attic looked great with no history/signs of trapped moisture whatsoever (plywood sheathing/ 2 x 6 rafters, built well). The insulation was 12 or so inches of loose fill cellulose. Electric ceiling heat.

Can someone please try and enlighted me on why there's no soffit or additional vents to work with roof vents?

I've seen plenty of attics with obvious ventilation concerns, but I am a bit curious about this. Would you suggest additional ventilation?


Any help/insight is always appreciated!
If you see a house that's almost 40 years old and has no problem in the area in which you have a question... it's been working well for a long time... don't recommend changes.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #12  
Old 2/17/10, 5:25 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof ventilation (or lack there of)

Quote:
Originally Posted by wdecker View Post
The ceiling electric heat is a factor. That is your thermal barrier and will produce sufficient "ventilation" as well as a lack of humidity loss through the ceiling.

Hope this helps;

"That is your thermal barrier"

Wouldn't the thermal barrier be the 12" of cellulose and any airsealing done on the ceiling beneath the insulation?


will produce sufficient "ventilation"

How does does the radiant electric heat in the ceiling produce ventilation?


"a lack of humidity loss through the ceiling."

How does does the radiant electric heat in the ceiling reduce humidity transfer through the ceiling?

Last edited by Brian A. MacNeish; 2/17/10 at 8:31 PM..
Reply With Quote
  #13  
Old 2/17/10, 5:46 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof ventilation (or lack there of)

Quote:
Originally Posted by kshepard View Post
If you see a house that's almost 40 years old and has no problem in the area in which you have a question... it's been working well for a long time... don't recommend changes.
This house with electric radiant ceiling heat may benefit from the addition of more cellulose depending on the electric rates for the area.

Radiant heat panels operate at 95-100 deg F which raises the Delta T (temperature difference from indoors to outdoors) which drives heat to the exterior. We usually use 68-72 deg F as the indoor temp when calculating heat loss from a building when determining HVAC heating equipment size and individual room heat needs at design temps. The Delta T is now raised by about 30 degrees!!

An economic analyses of heat $$ saved by the extra insulation versus the cost of the extra insulation should be done before adding any insulation. If the payback is within 6-10 years, its a pretty good deal.

Last edited by Brian A. MacNeish; 2/17/10 at 8:32 PM..
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/21/10, 1:55 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof ventilation (or lack there of)

Originally Posted by wdecker
"The ceiling electric heat is a factor. That is your thermal barrier and will produce sufficient "ventilation" as well as a lack of humidity loss through the ceiling.

Hope this helps;"






Quote:
Originally Posted by Brian A. MacNeish View Post

"That is your thermal barrier"

Wouldn't the thermal barrier be the 12" of cellulose and any airsealing done on the ceiling beneath the insulation?


will produce sufficient "ventilation"

How does does the radiant electric heat in the ceiling produce ventilation?


"a lack of humidity loss through the ceiling."

How does does the radiant electric heat in the ceiling reduce humidity transfer through the ceiling?

BUMP!!!
Reply With Quote
  #15  
Old 2/21/10, 11:47 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Roof ventilation (or lack there of)

Quote:
Originally Posted by Brian A. MacNeish;623165

Originally Posted by [B
wdecker[/B]
"The ceiling electric heat is a factor. That is your thermal barrier and will produce sufficient "ventilation" as well as a lack of humidity loss through the ceiling."



]"That is your thermal barrier"

Wouldn't the thermal barrier be the 12" of cellulose and any airsealing done on the ceiling beneath the insulation?


will produce sufficient "ventilation"

How does does the radiant electric heat in the ceiling produce ventilation?


"a lack of humidity loss through the ceiling."

How does does the radiant electric heat in the ceiling reduce humidity transfer through the ceiling?

BUMP
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Vegetation Roof Systems Educational by NRCA mcyr Miscellaneous Discussion for Inspectors 0 10/14/08 4:11 PM
Is inadequate roof or attic ventilation a defect? gliebig Exterior Inspections 85 1/16/08 6:56 PM
Ice Gaurd membrane dmacy Exterior Inspections 36 6/14/07 12:21 AM
Moss growing on roof ecox1 Exterior Inspections 45 1/19/06 9:57 PM


All times are GMT -4. The time now is 1:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts