Default Roof/wall stucco flashing incorrect

Well here's a basic question. $1.5 million home. Any water running down the wall will run under the tile and depend on the underlying membrane for protection. Thing is, I don't remember what this should look like.
Stucco terminated above tile with couterflashing and flashing directing runoff across upper surface of tile?

-Kent

Last edited by kshepard; 10/2/08 at 1:40 AM..
Reply With Quote
  #2  
Old 4/29/06, 3:07 AM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,090
Default Re: Roof/wall stucco flashing incorrect

It is missing the "kick flashing" otherwise it looks like the same crap I see all the time.
Reply With Quote
  #3  
Old 4/29/06, 7:18 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Roof/wall stucco flashing incorrect

Attachment 3179
click to enlarge

Last edited by dvalley; 10/7/07 at 4:41 PM..
Reply With Quote
  #4  
Old 4/29/06, 8:12 AM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: Roof/wall stucco flashing incorrect

http://www.dryflekt.com

The wall step flashing could very well be there and allright just hidden. But the kick out diverter will be the down fall of the installation. And according to ASTM the stucco should not be within 2 inches of the roof.
Reply With Quote
  #5  
Old 4/29/06, 8:27 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Roof/wall stucco flashing incorrect

Quote:
Originally Posted by cbrown1
That is a very nice product.

I received a couple of samples (1 right hand and 1 left hand) from the company. They are great to keep in the truck for show and tell with the client and even had an occasion to share with the roofer that the seller hired to fix a damaged area.
Reply With Quote
  #6  
Old 4/29/06, 8:35 AM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: Roof/wall stucco flashing incorrect

Bob Givens is a nice guy I met him in OVPK KS. Last fall now if the roofers will just start installing them alot of problems would just vanish!
Reply With Quote
  #7  
Old 4/29/06, 9:05 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Roof/wall stucco flashing incorrect

Hi to all,

there appear to be several issues with that installaion that are incorrect, some have been covered by others.

To add to the list I don't see a pan flashing under the tile (step flashings would not be applicable with a tile roof). Also, what pitch is the roof it seems awfully low for any type of tile or shingle.

I agree solidly with the kickout flashings comments they would save a huge ammount of damage.

Regards

Gerry
Attached Thumbnails
roof-wall-stucco-flashing-incorrect-panflashing.gif  



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #8  
Old 4/29/06, 9:11 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Roof/wall stucco flashing incorrect

10-4 Gerry....missing the pan and kick-out flashing.

I highly doubt there is any flashing on the wall either, it would be visible.

Generally there is a two-three inch reveal at the walls.
Reply With Quote
  #9  
Old 4/29/06, 9:18 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Roof/wall stucco flashing incorrect

Hi Dale,

I agree with you, at best there will just be a straight angled flashing running up the roof/wall intersection, hopefully it was applied prior to the torch-down underlayment.

The whole thing is just a typical crappy install, you see this stuff all the time when the trades are just not working together. The problem is no one gets to set up the flashing systems properly before the stucco is applied.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #10  
Old 4/29/06, 9:34 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Roof/wall stucco flashing incorrect

Gerry,

That is a good picture of the correct installation method. I saved the picture so I don't have to explain or draw examples for clients regarding how the flashing is supposed to be installed.

What gets me is the fact these damn city inspectors could care less about flashing. The IRC really needs to step-up the requirements in more detail.
Reply With Quote
  #11  
Old 4/29/06, 9:37 AM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: Roof/wall stucco flashing incorrect

The different colors does the job !
Reply With Quote
  #12  
Old 4/29/06, 9:44 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Roof/wall stucco flashing incorrect

Quote:
Originally Posted by cbrown1
The different colors does the job !
Thanks guys,

that image is from my "Crayola Series" I needed some flashing details for the online roofing course and nothing out there was really clear enough so I did some myself.

Here's some more

Regards

Gerry
Attached Thumbnails
roof-wall-stucco-flashing-incorrect-basicflashing.gif   roof-wall-stucco-flashing-incorrect-cantstrip.gif  



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #13  
Old 4/29/06, 9:49 AM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: Roof/wall stucco flashing incorrect

Hey Gerry

Can you do one with 2 layers of moisture barrier for a stucco application?
Reply With Quote
  #14  
Old 4/29/06, 10:16 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Roof/wall stucco flashing incorrect

Quote:
Originally Posted by cbrown1
Hey Gerry

Can you do one with 2 layers of moisture barrier for a stucco application?
Carl, I could but I have never seen it done like that

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #15  
Old 4/29/06, 3:28 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Roof/wall stucco flashing incorrect

Thanks guys. It's been a while and I couldn't believe the stucco guys screwed this house up so badly. There was pan flashin but the short lip was smashed down everywhere.

No weep screed and all walls terminated below grade. No caulk at any pentration or termination

Last edited by kshepard; 10/2/08 at 1:40 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Stucco Staining jhagarty Exterior Inspections 23 3/5/11 8:27 AM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 8:10 AM
no flashing; no inspection Leanne Jowers Exterior Inspections 97 5/9/07 12:11 PM
Need to ID type of stucco cdewitt Exterior Inspections 20 12/4/06 10:39 PM
Common Defects List by Age of House trausch Inspection Education & Training 10 6/12/06 4:52 AM


All times are GMT -4. The time now is 7:12 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts