Default Too much roof/attic ventilation?

Ridge vent and roof vents combined with soffit vents. Thoughts & comments appreciated.
Attached Thumbnails
too-much-roof-attic-ventilation-46-oak-dr.-napoleon-099.jpg  
Reply With Quote
Need a home inspection in Oregon? Check out InterNACHI's listing of Oregon certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/4/10, 9:04 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Too much roof/attic ventilation?

I don't think "too much" is a concern.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 6/4/10, 9:26 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Too much roof/attic ventilation?

I agree, I don't think too much is an issue. What may be an issue is that the different types of vents will be working against one another...

Soffit vents are to let air in, ridge vents let it out. If the roof vents let the soffit air out, then all the air from the roof vents to the ridge could stagnate, heat up, and cause the shingles to fail. The ridge vent will only work if there is some other air to replace what is leaving. I'm not saying this is happening, only that it's a possibility. If there are gable vents too, then the fresh air could come from them for the peak.

It's all about the "design" and the building science behind it. If you install two things that are supposed to work together, and then add a third that isn't. That third is just going to get in the way...



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #4  
Old 6/4/10, 9:35 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Too much roof/attic ventilation?

I have read one study (provided at a seminar two years ago) that shows that the additional roof vents can reduce ventilation of the total attic space.

Air moving over the ridge vent draws air from the attic. The added vents a few feet away from the ridge can be providing the replacement air instead of or more than the soffit vent, as originally intended. Or, the air that the added vents are actually drawing is coming in through the ridge. In any event, under these conditions there is insufficient ventilation in the total attic space.

Look, for signs of moisture/damage in the bottom third area.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Last edited by jbushart; 6/4/10 at 9:38 AM..
Reply With Quote
  #5  
Old 6/4/10, 9:38 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Too much roof/attic ventilation?

Did you do a smoke test and determine air flow?

As Mark said, it may not work as intended.
If You want to talk about it, you need to gather the required data.

What does the SOP state? (if I told you, you'd never read it).



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #6  
Old 6/4/10, 9:38 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Too much roof/attic ventilation?

I personally wouldn't reference building science with regard to attic air flow in this case unless I was truly knowledgeable about it. You may open the worm can.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 6/4/10, 9:22 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Too much roof/attic ventilation?

Quote:
Originally Posted by jfunderburk View Post
I personally wouldn't reference building science with regard to attic air flow in this case unless I was truly knowledgeable about it. You may open the worm can.
If you were to contact Dr. Bill Rose (Phd building scientist at U. of Illinois), he would tell you you can draw all the arrows you want on diagrams about "theoretical" or "designed" natural air flow, but ensuring that the air flows that way is not guaranteed. He's been studying roofing, venting, insulation, condensation for years.

To quote him from a 1992 Journal of Light Construction article, The Science of Venting: "In real attics, however, the airflow rarely follows the arrows."
Reply With Quote
  #8  
Old 6/4/10, 10:15 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Too much roof/attic ventilation?

Manufacturer (i.e., AirVent) recommends not mixing static and ridge vents on the same roof as it can shortcut the designed flow from soffit to ridge.

Personally, I think you tend to get flow from windward to leeward, but I have never done my own independent testing, so I go with what the manufacturer states.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #9  
Old 6/4/10, 11:43 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: Too much roof/attic ventilation?

Below copied from: http://www.ventilation-maximum.com/English/faq.html

Question: The building I want to ventilate is 2000 sq. ft. The ventilator, model #301 can ventilate up to 1200 sq. ft., and the model #303 can ventilate up to 800 sq. ft. Can I install one model #301 and one model #303 on the same roof?

Answer: No, you must always use the same model of ventilator, otherwise the stronger ventilator will draw from the weakest, therefore short circuiting the system. This is why we recommend that you block off or remove all other vents on the roof.

Food for thoughts!



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #10  
Old 6/5/10, 5:53 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Too much roof/attic ventilation?

Quote:
Originally Posted by mgratton View Post
Below copied from: http://www.ventilation-maximum.com/English/faq.html

Question: The building I want to ventilate is 2000 sq. ft. The ventilator, model #301 can ventilate up to 1200 sq. ft., and the model #303 can ventilate up to 800 sq. ft. Can I install one model #301 and one model #303 on the same roof?

Answer: No, you must always use the same model of ventilator, otherwise the stronger ventilator will draw from the weakest, therefore short circuiting the system. This is why we recommend that you block off or remove all other vents on the roof.

Food for thoughts!
From the same site:

Question: Would your ventilator not draw the heat out of my house having such a powerful drawing power?
Answer: No, if the house in question is well insulated per standards, has a proper vapour barrier and the soffits are unobstructed and balanced or exceeds the opening of the exhaust vents, this shall never be an issue.

Notice they never mention that the attic should be firstly airsealed to prevent house air containing moisture and heat (that you paid for) from exiting the house to the attic. One of the biggest items the energy audit programs are promoting is airsealing for obvious reasons.......(1) stop warm air from leaving at the ceiling level and (2) prevent house moisture from getting into the attic where it may condense.

They wouldn't want to stop this moisture from getting into the attic.......then they'd have less of a reason to sell their vents......there'd be little or no attic condensation. From the Journal of Light Construction article The Science of Venting by Dr. Bill Rose: "The best protection against condensation and mildew problems in the attic is an airtight ceiling plane- one that allows no air leaks from the attic below."
Reply With Quote
  #11  
Old 6/5/10, 8:52 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: Too much roof/attic ventilation?

Quote:
Originally Posted by Brian A. MacNeish View Post
"The best protection against condensation and mildew problems in the attic is an airtight ceiling plane- one that allows no air leaks from the attic below."
I agree with above statement but that is practicaly impossible to achieve. Newer homes are build better but they still leaks.



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #13  
Old 6/5/10, 10:05 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Too much roof/attic ventilation?

Quote:
Originally Posted by mgratton View Post
I agree with above statement but that is practicaly impossible to achieve. Newer homes are build better but they still leaks.
Yes, it's virtually impossible to achieve a perfect airtight house. The tightest home our company ever tested had .25 ach @ 50 pascals pressure differential......but that is extremely tight. The R2000 requirement in Canada is 1.5 ach or less @ 50 pascals.

When homes are that tight they have air exchangers or HRV's to control the interior RH of the home so any air leaking out is relatively dry and the amount is so little so as not to cause a problem. It was the "wet" houses (wet crawlspaces/basements-in effect a 24/7/365 humidifier; poor or non-existent interior house venting, lots of plants/aquariums; indoor clothes drying/unvented dryers) with lots of air leaks to the attic that brought on the need for so much venting.

Now we know the underlying causes/moisture paths/building science and should be able to provide other options to begin to solve the problem other than only "vent the h ell out of the roof".
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Building Science- research from respected sources Brian A. MacNeish Ancillary Inspection Services & Additional Topics 17 7/12/11 6:31 AM
Way More Intake To Supplement Minimal Exhaust Ventilation? Ed Fako Exterior Inspections 1 12/19/08 6:07 PM
Almost vented directly out? djones6 Inspecting HVAC Systems 15 4/12/07 10:38 AM
Roof/Attic ventilation wwarner Exterior Inspections 5 6/27/06 9:55 AM