Default Valley flashing

Yesterday I was out in a new subdivision under construction and thought that the valley flashing was not wide enough. Of course, rarely is the full flashing visible once the roof covering has been installed, but I was wondering what the minimum width is for that valley flashing. The subdivision in question had four inches on each side of a two-inch upside-down V. Granted, we don't have too much wind-driven rain here in San Diego, but I was wondering what the minimum is in California, and then whether or not it is different from hurricane states like Louisiana and Florida.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #2  
Old 6/30/07, 1:53 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Valley flashing

It depends on several factors - roof pitch, roofing material, etc. - but 4" is generally too narrow, unless the roofing material has been sealed (not nailed) to the flashing.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 6/30/07, 1:57 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Valley flashing

Hey, Jeff.

The ones in the subdivision are going to be our standard Southern California whatever-pitched roof with flat concrete tiles. Is there an absolute minimum expressed by the various codes? I've been looking for something but can find nothing.

I called a CREIA inspector whom I know does draw inspections, and he said 24" flashing is the standard. I never installed 24" flashing when I was working along the Texas Gulf Coast, but that was 20 years ago. We used 18" flashing. He could not cite any code either, though, simply saying that "it's the standard."



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #4  
Old 6/30/07, 3:03 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Valley flashing

National Roofing Contractors Association suggests using the guidelines of the FRSA Roof Tile Institute.

FRSA (Florida based) requires a minimum of 16" wide flashing in the valleys of concrete tile roof systems.

I can send you the PDF if you'd like. . . (2.5mb)



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 6/30/07, 3:05 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Valley flashing

Quote:
Originally Posted by jpope
National Roofing Contractors Association suggests using the guidelines of the FRSA Roof Tile Institute.

FRSA (Florida based) requires a minimum of 16" wide flashing in the valleys of concrete tile roof systems.

I can send you the PDF if you'd like. . . (2.5mb)
Hey, Jeff.

Yes, I'd like to have that in my library. Thanks.

Russel Ray



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #6  
Old 6/30/07, 3:11 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Valley flashing

I just found the one I was looking for, I'll send you both.

ICBO and the Western States Roofing Association (WSRA) call for minimum of 22" wide valley flashing on concrete tile systems (11" from center each way).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 6/30/07, 5:48 PM
Ed Fako's Avatar
Ed Fako Ed Fako is offline
Active Poster
 
Join Date: Feb 2007
Location: NW Chicago Suburbs
Posts: 199
Please Note: Ed Fako is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Valley flashing

It may be useful to others to post the link on this forum please.

Ed
Reply With Quote
  #8  
Old 6/30/07, 6:40 PM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Valley flashing

The IRC also requires waterproofing shingle underlayment in valleys. Check your area's version of the code for the width required.
Reply With Quote
  #9  
Old 6/30/07, 8:38 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,918
Default Re: Valley flashing

Well, the only thing I can contribute here is the fact that most materials available is 36" wide, so the minimum would be 18" for valley flashings.

Before the standard of using this product

http://www.na.graceconstruction.com/...als.html&did=8

We would use the typical aluminum flashings 24" wide and that would also give us 12" in the valleys, and then the double or single coverage which also came in 36" wide rolls.

I am curious on something here;

Has the Code become the Standard or has the Standard become the Code?

As a Builder, it seems that I have never been faced with issues that pertained to a Code minimum.
But as an HI, I sure see a lot of it. ha.ha.

Marcel

</IMG></IMG></IMG>
Reply With Quote
  #10  
Old 6/30/07, 10:18 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Valley flashing

Quote:
Originally Posted by Ed Fako
It may be useful to others to post the link on this forum please.
This forum won't allow me to upload files of that size, so they'll remain on my computer. However, I'd be happy to email you the file so long as your settings will allow you to accept large files such as this.

Send your request to inspectorjeff@sbcglobal.net

Indicate whether you want the WSRA or FRSA version, or both. The actual size is closer to 5mb each, not the 2.5 that I posted earlier.

Otherwise, maybe Russel will post a link to his library once he has included them. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 6/30/07, 10:22 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Valley flashing

Quote:
Originally Posted by mcyr
Has the Code become the Standard or has the Standard become the Code?
Yes. But I think you already knew that



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 7/1/07, 1:44 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Valley flashing

Quote:
Originally Posted by jpope
Otherwise, maybe Russel will post a link to his library once he has included them. . .
It was on my mind.

Here they are:

RTI-ICBO-WSRCA

RTI

Thanks, Jeff. They made very interesting reading.



NACHI 2005 U.S. Member of the Year

Last edited by rray; 7/1/07 at 1:52 AM..
Reply With Quote
  #13  
Old 7/1/07, 2:31 PM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,709
Default Re: Valley flashing

Valley Flashing - Short for streaking thru a low lying area.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Valley dmacy Exterior Inspections 35 3/31/09 9:56 AM
Comp shingles over wood shingles Matthew Hopkins Exterior Inspections 28 10/16/07 12:19 PM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior Inspections 6 10/13/07 9:10 AM
"Synthetic" valley flashing jskrypka Exterior Inspections 3 4/5/07 12:57 AM
NY NACHI Hudson Valley Chapter Meeting pmaietta Miscellaneous Discussion for Inspectors 0 2/27/06 2:42 PM


All times are GMT -4. The time now is 2:46 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts