Default Vertical Cracks in 3Tab Shingles

My neighbor has three areas on his hip roof with 4' long cracks in the shingle running vertically from the ridge to the soffit. I have not looked in the attic, can anyone tell me why shingles would crack this way?
I am guessing snow load with 3 layers of Shingles.



Rick Kie
Reply With Quote
  #2  
Old 5/7/08, 5:36 PM
iniquette's Avatar
iniquette iniquette is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Markesan, WI
Posts: 1,795
Send a message via ICQ to iniquette
Default Re: Vertical Cracks in 3Tab Shingles

Sounds like sheathing may be sagging across the truss span causing the cracking possibly. Need a pic though, just a guess.



Ian Niquette
Square One Home Inspection
Markesan WI 53946
www.squareonehomeinspection.com
Active Rain Network
INACHI Awards Portal
Want To Exchange Links?



What we've got here is......failure......to communicate.....
Reply With Quote
  #3  
Old 5/7/08, 7:38 PM
Rick K. Kie's Avatar
Rick K. Kie Rick K. Kie is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Endwell, NY
Posts: 385
Default Re: Vertical Cracks in 3Tab Shingles

I'll post a pic soon just took it! its a hip roof I dought there are trusses but i will look.



Rick Kie
Reply With Quote
  #4  
Old 5/7/08, 9:11 PM
bjones5's Avatar
bjones5 bjones5 is offline
Active Poster
 
Join Date: Feb 2008
Location: Meaford, ON
Posts: 1,296
Send a message via MSN to bjones5
Default Re: Vertical Cracks in 3Tab Shingles

Quote:
Originally Posted by rkie
My neighbor has three areas on his hip roof with 4' long cracks in the shingle running vertically from the ridge to the soffit. I have not looked in the attic, can anyone tell me why shingles would crack this way?
I am guessing snow load with 3 layers of Shingles.
Not just snow load, although snow doesn't help the problem. You state 3 layers of shingles......only 2 are allowed in most states, provinces. Manufacturee's advise 1 layer only. If you read the fine print on their waranty, the roof has to be "as new" before shingling or the warranty is void. In simple terms, an old roof has to be resheeted.



Brian Jones,
226-662-0152
mcbridesown@hotmail.com

To all newcomers,
"Ceade Mille Failte"
(Gaelic for "A Hundred Thousand Welcomes")
Reply With Quote
  #5  
Old 5/8/08, 8:19 AM
Rick K. Kie's Avatar
Rick K. Kie Rick K. Kie is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Endwell, NY
Posts: 385
Default Re: Vertical Cracks in 3Tab Shingles

I walked the roof last night. there are only two layers of shingles. Lots of spotty moss buildup that could be cleaned off. I just am curious to why they would crack in this direction. There are several sections like this!
They bought the house last year and the inspector said the roof wouldn't need any work for 5 years.
Attached Thumbnails
vertical-cracks-3tab-shingles-neigbors-roof.jpg  



Rick Kie
Reply With Quote
  #6  
Old 5/8/08, 8:53 AM
iniquette's Avatar
iniquette iniquette is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Markesan, WI
Posts: 1,795
Send a message via ICQ to iniquette
Default Re: Vertical Cracks in 3Tab Shingles

After seeing the pic I still say they are saggging between trusses. Where the crack is is probably a truss or rafter. Still, just an opinion right or wrong.



Ian Niquette
Square One Home Inspection
Markesan WI 53946
www.squareonehomeinspection.com
Active Rain Network
INACHI Awards Portal
Want To Exchange Links?



What we've got here is......failure......to communicate.....
Reply With Quote
  #7  
Old 5/8/08, 11:28 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Vertical Cracks in 3Tab Shingles

Quote:
Originally Posted by rkie
They bought the house last year and the inspector said the roof wouldn't need any work for 5 years.
Foolish statement by that inspector.
Reply With Quote
  #8  
Old 5/8/08, 3:50 PM
bjones5's Avatar
bjones5 bjones5 is offline
Active Poster
 
Join Date: Feb 2008
Location: Meaford, ON
Posts: 1,296
Send a message via MSN to bjones5
Default Re: Vertical Cracks in 3Tab Shingles

Quote:
Originally Posted by rkie
I walked the roof last night. there are only two layers of shingles. Lots of spotty moss buildup that could be cleaned off. I just am curious to why they would crack in this direction. There are several sections like this!
They bought the house last year and the inspector said the roof wouldn't need any work for 5 years.
If you can, get into the attic and look at the trusses or rafters, looking for any damage. Also note the absence or presence of H clips in the sheathing if the span between rafters is greater than 16" o/c.
As a sidenote, an astute observation by Mr Maday. I wonder if the inspector even went up on the roof.



Brian Jones,
226-662-0152
mcbridesown@hotmail.com

To all newcomers,
"Ceade Mille Failte"
(Gaelic for "A Hundred Thousand Welcomes")
Reply With Quote
  #9  
Old 5/8/08, 3:52 PM
bjones5's Avatar
bjones5 bjones5 is offline
Active Poster
 
Join Date: Feb 2008
Location: Meaford, ON
Posts: 1,296
Send a message via MSN to bjones5
Default Re: Vertical Cracks in 3Tab Shingles

One other possible reson for the 4' cracking.......the sheathing may not be sitting on the rafter or truss as it should. Again, a trip into the attic may answer a lot of ???



Brian Jones,
226-662-0152
mcbridesown@hotmail.com

To all newcomers,
"Ceade Mille Failte"
(Gaelic for "A Hundred Thousand Welcomes")
Reply With Quote
  #10  
Old 5/8/08, 6:59 PM
Rick K. Kie's Avatar
Rick K. Kie Rick K. Kie is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Endwell, NY
Posts: 385
Default Re: Vertical Cracks in 3Tab Shingles

i guess I will look in the attic and report back, thanks for the suggestions.



Rick Kie
Reply With Quote
  #11  
Old 5/8/08, 7:05 PM
William M. Corbett's Avatar
William M. Corbett William M. Corbett is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Remlap, AL
Posts: 231
Default Re: Vertical Cracks in 3Tab Shingles

Most of the time osb is 4' wide. I am with Ian. Iwould guess the cracks are in line with the seams of osb.



Bill Corbett C.H.I.
Magic City Inspections LLC
InspectingtheUnexpected.com
Reply With Quote
  #12  
Old 5/8/08, 9:00 PM
Russell W. Meyers Russell W. Meyers is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Champaign, IL
Posts: 29
Default Re: Vertical Cracks in 3Tab Shingles

Rick, (Just another thought.)

When you're in the attic, check to see if it is a pre-fab house with a panelized roof system. These sysyems were typically 4' wide and would often sag between the doubled edge joints. If it is this type of system, the doubled edge joint could also be pulling apart during snow loading and causing the shingles to crack. An overall picture showing the relationship of the cracks to one another might be helpful. Definitely some structural movement / deflection taking place to cause this damage. (May be individually reinforced rafters over which the shingles are being stretched and torn when the rest of the roof sags.)



Russ Meyers
NACHI99040101
IL Lic. #450.000314
Reply With Quote
  #13  
Old 6/17/09, 10:26 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Vertical Cracks in 3Tab Shingles

Those splits are over joints in the underlying layer of shingles. It's a type of thermal cracking, meaning it's caused by contraction, sometimes made worse by shingles shrinking over time.

When shingles get cold, they contract and the joints between them get wider, stressing the shingle in the course above which bridges the joint (which has also contracted and is smaller). When the strength of the adhesive strip bond exceeds the tensile strength of the shingle under these circumstances... the upper shingle will split.

The joints align like that because the shingles were installed racked... in other words straight up the roof instead of offset at each subsequent course.
Racking is almost always... but not always... an improper installation.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Vertical lines in asphalt shingles lfoster Exterior Inspections 17 10/26/07 10:00 PM
slab no cracks: Brick veneer cracks gkoehl Structural Inspections 1 4/17/07 4:52 PM
Common Defects List by Age of House trausch Inspection Education & Training 10 6/12/06 4:52 AM
Cracks on shingles syared Exterior Inspections 7 6/8/06 5:54 PM
Asphalt roof shingle cracks. ngifford Exterior Inspections 2 3/25/06 11:47 PM


All times are GMT -4. The time now is 4:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts