Default Wall bulge.

From a condo inspection.
How would you report this. I do not want to add or imply related trade influence.
Full HD photo with 14 mmp.. Snip and zoom will show more of the deficiency or defect. I say defect.
wall-bulge-colin-roch-003.jpg



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/27/11, 9:42 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Wall bulge.

I can't tell a thing from your pic. I use this statement for what I call imperfections, especially in new homes.

"The wall in the *LOCATION(rooms-interior)* is slightly bowed. Achieving absolute perfection while building a home is impossible and slight imperfections are normally only aesthetic issues that may never be noticed by guests. Sometimes, however, a defect crosses the line into a poor workmanship issue and only you, the buyer, can make that determination. We can elaborate, but you should have the builder or seller comment on the reason for the defect and you may wish to have it repaired."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 12/27/11, 9:50 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Wall bulge.

Robert you need to give more information as to what we are looking at please!



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #4  
Old 12/27/11, 9:53 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: Wall bulge.

Are you referring to what appears to be an "uplift" towards the rear of the ledge?

Difficult to respond without actually understanding the issue, so go with what Joe stated above.
Reply With Quote
  #5  
Old 12/27/11, 10:13 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Wall bulge.

Quote:
Originally Posted by jfunderburk View Post
I can't tell a thing from your pic. I use this statement for what I call imperfections, especially in new homes.

"The wall in the *LOCATION(rooms-interior)* is slightly bowed. Achieving absolute perfection while building a home is impossible and slight imperfections are normally only aesthetic issues that may never be noticed by guests. Sometimes, however, a defect crosses the line into a poor workmanship issue and only you, the buyer, can make that determination. We can elaborate, but you should have the builder or seller comment on the reason for the defect and you may wish to have it repaired."
If you said this in Canada you would be the laughing stock of the industry.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #6  
Old 12/27/11, 10:14 AM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Re: Wall bulge.

Are you referring to the bricks all lining up? If that's what they are?



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #7  
Old 12/27/11, 10:51 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: Wall bulge.

OK.
The corners are to be as plumb as the can be.
The structure is 60 feet high.
5 tiers of brick facade.
A brick-shelf starts at every balcony floor.
Angle iron ( brick shelf )tied into the concrete structure using Lag shields and 6-8 inch lag screws.
I built and repair walls like this from 30 feet to 160 feet off the ground.
I started as the setup engineer and worked the brick line also.

Repaired probable defective ones like this. ( Opinion only) on this example.
Might be structural building error. ( opinion only) but they could have stepped the brick pattern out.
Not cobbled. Code violation. I know. I am not going there.
Look for a plum corner and fields ( Always ) with clay brick facade.
Remember the cobbling rule of 1/3 the wall wydth.
This wall is a veneer of 1 brick wydth. 3.5/8 - 3.7/8
I want to stay at arms length to my trade.
Word my report using observation only.

Recommend a architect and engineer.

By pointing to the brick shelf am I committing to my trade experience.
I want to be a witness of observation.
Not to be involved as a witness of building procedure.
Hope that helps.
wall-bulge-2a.jpgwall-bulge-318-zoom.jpgwall-bulge-318-zoomed-.jpg
In photo 2 follow the light yellow lines on the right and left hand side.
It shows obvious signs of movement or improper building practices.
Ether or it can jeopardize public safety.
One method I am unsure of for building on a incline. Cabling runs through the brick holes. It is then anchored into the wall to insure the brick facade will not fall when it becomes deficient over time.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #8  
Old 12/27/11, 10:59 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: Wall bulge.

Sorry for the long post.
Replace photo 2 only. This shows all brick shelf's.

I recommended ( Engineer architect.) and excuse myself of any building knowledge in my report is my point.
If I can install building knowledge , how much?
wall-bulge-z00.jpg



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #9  
Old 12/27/11, 11:08 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: Wall bulge.

Since a brick veneer is not considered structure, I would say you are safe in saying that a failure may occur to the tie back so an evaluation from a engineers view point is required.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #10  
Old 12/27/11, 11:41 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: Wall bulge.

Quote:
Originally Posted by jfunderburk View Post
I can't tell a thing from your pic. I use this statement for what I call imperfections, especially in new homes.

"The wall in the *LOCATION(rooms-interior)* is slightly bowed. Achieving absolute perfection while building a home is impossible and slight imperfections are normally only aesthetic issues that may never be noticed by guests. Sometimes, however, a defect crosses the line into a poor workmanship issue and only you, the buyer, can make that determination. We can elaborate, but you should have the builder or seller comment on the reason for the defect and you may wish to have it repaired."
Thatis ther advice I gave my client Mr. Funderburk.
Thank you Joe.

I feel comfortable now you have addressed my concern in your obvious eloquent well establish narrative.
I do thank you.

I know I have said this before;
I will humbly apologize to " any and all" I have demeaned and or angered upon my arrival to the MB and InterNACHI in general..

I wear these regrets very heavily.
I am now becoming aware of how my words can effect so much and so many.
My InterNACHI members, The report, the client , your business standings. and your personal pride.

I still have and endless amount of education to read and progress to make.
I will do it with reflection now.

Thank you all for your patients.
God bless you all in the new year.
May piece, health, and prosperity be you reward in this up coming New Year..



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you report the absence of house wrap? jfunderburk Exterior Inspections 17 6/17/11 10:04 PM
Bulge at the top of a exterior wall sshockley Structural Inspections 5 1/9/10 10:50 PM
Moisture Management mcyr Exterior Inspections 15 9/8/08 12:11 PM
VIDEO--Bowed Basement Wall, Cracks etc john bubber Structural Inspections 75 7/21/08 5:25 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM


All times are GMT -4. The time now is 4:33 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts