What is the proper wall flashing detail for the top edge of cultured stone veneer applied on a gable wall that stops at the eave height. There is a horizontal trim board directly above the stone, and fiber cement siding above that.
Thanks, Matt M. |
|
#2
|
||||
|
||||
|
Quote:
I would want to see a base flashing applied lipping over the stone underneath the trim board, this would realy be a "Z" flashing extending up underneath the trim and siding by 4-6 inches Idealy with a rubberized self adhesive counterflashing applied prior to the trim. Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#3
|
||||
|
||||
|
Kinda like this one except a gable end with stone instead of a window and stucco! Allthough they need to have this with the lick and stick brick and stone. IMO http://www.badstucco.com/repair2.html
It is the same concept! At the sill of the window. Last edited by cbrown1; 3/20/06 at 7:11 PM.. |
|
#4
|
|||
|
|||
|
Please Note:
Matt M is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks for the replys. That is what I thought was needed.
Matt M. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| VIDEO--Bowed Basement Wall, Cracks etc | john bubber | Structural Inspections | 75 | 7/21/08 5:25 PM |
| Chimney flashing photo's needed: brick and stone done correctly | kshepard | Exterior Inspections | 6 | 10/13/07 8:10 AM |
| Newbie here with a slab "standards" question | Robert Young, #3 | Structural Inspections | 17 | 4/10/07 10:48 AM |
| Questionable wall to roof flashing | dbucknavich | Exterior Inspections | 4 | 8/14/06 12:57 PM |
| Step flashing at vertical wall? | jlybolt | Exterior Inspections | 31 | 2/12/06 11:40 AM |