I have a client that is getting water coming in at the tile floors and wall intersection on the inside of their home when it rains. This is a newly built home (2007-200. This appears to be happening below the windows. There is baseboard tile installed, which is starting to move out away from the wall, but at the top grout line my moisture meter pegs, as I move up the interior wall the moisture meter drops back down. The windows are a Built Best brand, model # BIB-N-003 series ECLD/CSMT/AWN/VT. They are a casement type window. I am trying to help figure out were the water is coming from. Anyone had any experience with figuring something like this out?

The landscaping on the exterior does not seem to be the problem as the sill plate appears to be a good 4-6 inches above the soil and the owners said there is not water ponding at the foundation when it rains.

See pictures of windows
Attached Thumbnails
water-entry-picture-001.jpg   water-entry-picture-002.jpg   water-entry-picture-003.jpg   water-entry-picture-004.jpg   water-entry-picture-005.jpg  

Reply With Quote
  #2  
Old 8/1/08, 1:18 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,513
Default Re: Water entry

I know this is probably not what you want to hear, but it is really not your job to figure out where or why the water is coming in. You are the inspector, find the problem and defer it to a professional. I have to constantly remind myself of where my responsibility ends and others begins. I think most home inspectors are naturally curious and want to know as much as they can and that is what attracted many of us to the profession. The water could be coming in just about anywhere from the sole plate up to the roof and running down inside the wall. This kind of problem requires further investigation, possibly with special training and equipment (Wet wall meters, etc.) The fact that you found it is to your credit, many would not have. If it is only happening under windows, that would be my first "guess" as the culprits. And it would only be a guess and we should refrain from doing too much guessing in our line of work.
Reply With Quote
  #3  
Old 8/1/08, 1:28 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: Water entry

I'm one of the guys Doug refered to.

Improper flashing and alarm sensors drilled though sills are the #1 & #2 culprits for wall moisture intrusion around here.

Another that I see a lot when inspecting casements is the installers and occupants aren't engaging the locking mechanisms properly, usually upper latch, thus allowing moisture entrance without even noticing until it's too late.

Scuppers over windows is just a dumb design even in an arid climate!



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good

Last edited by badair; 8/1/08 at 1:32 PM..
Reply With Quote
  #4  
Old 8/1/08, 1:33 PM
Ronald G. Chorey II's Avatar
Ronald G. Chorey II Ronald G. Chorey II is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Las Cruces, NM
Posts: 124
Send a message via MSN to rchorey
Default Re: Water entry

There was no evidence of water coming down the interior walls below the windows. But there is definitley moisture at the floor, or up from the floor abour 4 inches(above the tile baseboard). I am helping these folks out to help find the problem. They are my client. The builder has been notified but has not been able to figure it out yet.
Reply With Quote
  #5  
Old 8/1/08, 1:38 PM
Carl Brown's Avatar
Carl Brown Carl Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 9,378
Default Re: Water entry

Moisture barrier over the bottom nail fin on the windows instead of under the the nail fin?

Is there backer rod and sealant joints between the windows and stucco?


Do they do stucco in NM like AZ with foam and chicken wire?


Are the windows mounted behind the foam to get the depth for the bullnose corners?



"I create controversy whether they like it or not"



Reply With Quote
  #6  
Old 8/1/08, 1:39 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: Water entry

Simply, professionally remove the affected tile and sheetrock and trace back to source.
This should be done anyway as the affected materials are now candidates for microbial growth and indoor environmental contamination.



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #7  
Old 8/1/08, 1:41 PM
Carl Brown's Avatar
Carl Brown Carl Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 9,378
Default Re: Water entry

If the builder has any other houses under construction look and see how they install the window's and other componet's.



"I create controversy whether they like it or not"



Reply With Quote
  #8  
Old 8/1/08, 1:45 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: Water entry

Quote:
Originally Posted by cbrown1
If the builder has any other houses under construction look and see how they install the window's and other componet's.
Way too logical, Mr. Spock!



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #9  
Old 8/1/08, 2:26 PM
Ronald G. Chorey II's Avatar
Ronald G. Chorey II Ronald G. Chorey II is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Las Cruces, NM
Posts: 124
Send a message via MSN to rchorey
Default Re: Water entry

I have told the owners they need to have the builder remove the tile baseboard and remove some drywall that is behind the tile so that the wall cavity can dryout. Then we may be able to get a borescope in and see were the water is coming in at. At least I hope. Another thing I saw this morning was ants at the one area, they were on the floor. Be intersting to get the tile off and see if there is/are gaps in the exterior sheathing, I can't tell from the outside. There has been weep screed installed at the base of the wall and the city requires styrofoam to be installed on the outside of the slab.

I have no idea if they installed a moisture barrier over the bottom fin. House was completed when I inspected it a couple months ago. Builder has told owners that the windows were properly flashed but I can not tell. Yes they stucco over foam and use chicken wire, that I have seen.

We had had no significant amount of rain from Oct 07 until about the end of June 08. Then last weekend remenants of Dolly hit us and we had about 2-3 inches of rain last weekend.
Reply With Quote
  #10  
Old 8/1/08, 2:35 PM
Carl Brown's Avatar
Carl Brown Carl Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 9,378
Default Re: Water entry

With the depth of the return of the opening it looks like the window's sit half way in the wall.

Not a doubt in my mind it is a moisture barrier problem at the sill of the window.

Does the stucco slope into the windows on the sill or to the outside of the openings?

Dolly was a doosie we got some of her here to!

It is a design flaw. But only when it rains.



"I create controversy whether they like it or not"



Reply With Quote
  #11  
Old 8/1/08, 2:38 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,946
Default Re: Water entry

All good suggestions. Here's another one.

Not rocket science, and I'm not sure I would have done this with a paying customer, but I found a roof leak for a friend of mine by using a hose.

She had a good idea where the leak was coming from, so she sprayed her garden hose on it, with me in the attic. You know where the hose is spraying, and you see it coming in, it makes it a lot easier to locate.

Soak the bottom of the wall with a hose, and see if the floor gets wet. If not, move up a few feet and soak the bottom of the window, etc etc until you get water. Might not tell exactly where it's coming but might get you in the general proximity.
Reply With Quote
  #12  
Old 8/1/08, 6:38 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water entry

In general when seeing this type of problem and roof , or exterior wall ,flashing , etc are all candidates, I am wondering which professional you guys defer too.?
Reply With Quote
  #13  
Old 8/1/08, 7:19 PM
Carl Brown's Avatar
Carl Brown Carl Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 9,378
Default Re: Water entry

http://uk.youtube.com/watch?v=iCHFVTQKqdQ


Sorry Bob!



"I create controversy whether they like it or not"



Reply With Quote
  #14  
Old 8/1/08, 8:00 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water entry

Funny , but not an answer stucco man.
Reply With Quote
  #15  
Old 8/1/08, 8:04 PM
Carl Brown's Avatar
Carl Brown Carl Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 9,378
Default Re: Water entry

With a window leak?

Stucco problem?

Rotted out interior?



"I create controversy whether they like it or not"



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Site grading and drainage wdevries Canadian Inspectors 5 10/6/09 11:23 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM


All times are GMT -4. The time now is 7:34 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts