Question Water entry at bottom of vinyl-sided chimneys that jut out

I've recently done a couple of inspections in which there was water entry into the bottom of chimneys that were vinyl-sided and configured as in the pics shown here. The water appears to run down the bottom panel (which was rotting in both cases), and into the basement. This appears to be a systemic design flaw.

My thought is that the water works its way around the edges of the siding in the corners and is caught and drawn in by the "J" channel border that was idiotically installed on the bottom of the course of the siding. With 2 stories of runoff, it certainly appears easy to see how water got in.

My question is how does one fix this with a minimum of surgery?

It seems to me a different configuration that replaces the "J" channels on the bottom and sides would make more sense, but that would involve re-siding the entire chimney, all 2-3 stories of it. It seems that re-configuring the bottom of the siding so water is run out, rather than in would solve most of the problem.

Thoughts?
Attached Thumbnails
water-entry-bottom-vinyl-sided-chimneys-jut-out-century-trail-1.gif   water-entry-bottom-vinyl-sided-chimneys-jut-out-ridgeside-3.gif   water-entry-bottom-vinyl-sided-chimneys-jut-out-ridgeside-2.gif   water-entry-bottom-vinyl-sided-chimneys-jut-out-ridgeside-1.gif   water-entry-bottom-vinyl-sided-chimneys-jut-out-century-trail-3.gif  

Reply With Quote
  #2  
Old 8/9/07, 7:07 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Water entry at bottom of vinyl-sided chimneys that jut out

Flashing...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 8/9/07, 7:27 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water entry at bottom of vinyl-sided chimneys that jut out

Quote:
Originally Posted by fbartlo
I've recently done a couple of inspections in which there was water entry into the bottom of chimneys that were vinyl-sided and configured as in the pics shown here. The water appears to run down the bottom panel (which was rotting in both cases), and into the basement. This appears to be a systemic design flaw.

My thought is that the water works its way around the edges of the siding in the corners and is caught and drawn in by the "J" channel border that was idiotically installed on the bottom of the course of the siding. With 2 stories of runoff, it certainly appears easy to see how water got in.

My question is how does one fix this with a minimum of surgery?

You don't. It requires at least the work you talk about below.

"It seems to me a different configuration that replaces the "J" channels on the bottom and sides would make more sense, but that would involve re-siding the entire chimney, all 2-3 stories of it. It seems that re-configuring the bottom of the siding so water is run out, rather than in would solve most of the problem.

Thoughts?
I have my own report and appendix which took a couple of months to generate. In the appendix, the largest section is about moisture which I start off with this sentence:
"Water is the largest destroyer of value in Canadian buildings"

There are at least 3 wrongs in the pictures shown.
(1) No caulking between the vertical J and the wood cornerboard
(2) Simply a horizontal drip cap/ Z flashing installed over the horizontal bottom trim board. What keeps the water from getting behind the wood at the corners where vertical and horizontal pieces meet?
(3) The middle picture shows a butt joint with caulking. The caulking will dry/shrink leaving a hairline crack which draws water in by capilliary action. This type of joint does not shed water
like shingles & clapboard or a ducks feathers.

A possible #4 is that they probably did not "back prime" or paint all sides of the wood. This unpainted wood becomes a resevoir for water that bypasses the first line of defense. It does not dry out as quickly as it did in the past since our houses are more airtight and don't bleed heat out the walls which usually used to dry this type of moisture intrusion.

Last edited by Brian A. MacNeish; 8/9/07 at 8:19 AM..
Reply With Quote
  #4  
Old 8/9/07, 7:37 AM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Water entry at bottom of vinyl-sided chimneys that jut out

I don't see any Z flashing on the bottom trim, did they use any kind of house wrap?



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #5  
Old 8/9/07, 8:03 AM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water entry at bottom of vinyl-sided chimneys that jut out

Another problem is that there is no drip provided at the bottom of the chimney, so water will run down the face of the chimney and then some will fail to drip from the bottom, collect there, and find its way into the house.
Reply With Quote
  #6  
Old 8/9/07, 11:45 AM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,707
Default Re: Water entry at bottom of vinyl-sided chimneys that jut out

The siding should extend all the way to the bottom, not stop flush on top of the trim, and it also needs a drip edge. Poor installation, but it should be fairly easy to correct without having to replace all of the siding on the chimney.
Reply With Quote
  #7  
Old 8/9/07, 4:23 PM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: Water entry at bottom of vinyl-sided chimneys that jut out

What did they do at the top/cap of the chimney!

Did they run the siding over the old cap?



"I create controversy whether they like it or not"



Reply With Quote
  #8  
Old 8/9/07, 8:01 PM
ckratzer ckratzer is offline
Active Poster
 
Join Date: Mar 2005
Posts: 256
Please Note: ckratzer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Water entry at bottom of vinyl-sided chimneys that jut out

Quote:
Originally Posted by klott
The siding should extend all the way to the bottom, not stop flush on top of the trim, and it also needs a drip edge. Poor installation, but it should be fairly easy to correct without having to replace all of the siding on the chimney.
Good call.
Get rid of the trim at the bottom and extend the siding to the bottom.
Rather than useing "J" ,a "starter strip" would be a way better component in this application .
As already mentioned, the chimney cap should bend over the siding.
This is not a difficult or expensive fix.
Reply With Quote
  #9  
Old 8/9/07, 8:16 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: SE Michigan
Posts: 236
Default Re: Water entry at bottom of vinyl-sided chimneys that jut out

The tops of the chimneys had metal caps that looked fiine, so the leakage appeared to be strictly siding-related, along the vertical J channels and in the bottom J channel. I saw no evidence of any sort of drip cap/Z flashing on the bottom of the siding.

Quote:
The siding should extend all the way to the bottom, not stop flush on top of the trim, and it also needs a drip edge. Poor installation, but it should be fairly easy to correct without having to replace all of the siding on the chimney.
That should solve the problem, Ken.

Also, a configuration that involves 2 Z flashings with a properly overlapped flat metal flashing on a separate board between them, if properly installed, should direct any water out and solve the problem, while maintaining a more consistent appearance.

Even though the siding should be caulked along the vertical "J" channels, it stands to reason that any water that gets in there would mostly be drawn in by capillary action, and would still run down the chimney.

Thanks for your responses, everyone.
Reply With Quote
  #10  
Old 8/11/07, 10:30 AM
Carl A. Brown's Avatar
Carl A. Brown Carl A. Brown is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Kansas City, ks
Posts: 10,763
Default Re: Water entry at bottom of vinyl-sided chimneys that jut out

Did the top of the chimney have a wood trim band around it that the flashing was out and over?

If so the siding stopped below it just like the rest of the trim and with out flashing at that pointe it is now a funnel.



"I create controversy whether they like it or not"



Reply With Quote
  #11  
Old 8/11/07, 3:18 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,608
Default Re: Water entry at bottom of vinyl-sided chimneys that jut out

[quote=ckratzer]Good call.
Get rid of the trim at the bottom and extend the siding to the bottom.
Rather than useing "J" ,a "starter strip" would be a way better component in this application .

quote]Exactly. Pop the bottom row off, install aluminum flashing, eliminate the "J" channel and use a starter strip. There will be nothing to catch the water and it will run off. Flashing just for precaution, wind , ice, etc.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Need Help On Chimney Liners Nick Scibetta Exterior Inspections 13 1/11/06 9:53 PM


All times are GMT -4. The time now is 12:17 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts