Default Weep Holes

Aren't weep holes supposed to be in the bottom course of bricks?
Attached Thumbnails
weep-holes-img_0158.jpg  
Reply With Quote
Need a home inspection in Illinois? Check out InterNACHI's listing of Illinois certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/31/10, 9:00 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Weep Holes

Yes,they are.
I also recommend pest screens.

They should be just above the foundation with some exposed moisture barrier.

Do not see many with key slots now in days where the simply leave out the mortar , but that part is fine.
Reply With Quote
  #3  
Old 3/31/10, 9:53 PM
Larry J. Michael Larry J. Michael is offline
InterNACHI Member
 
Join Date: Nov 2009
Location: Greensboro, N. C.
Posts: 732
Default Re: Weep Holes

Yes, they should.



Greensboro Home Inspection
Providing home inspections in Greensboro, High Point, Burlington and the surrounding areas.
greensboro-home-inspection.html

Raleigh Home Inspection
Home inspections in Raleigh, Durham, Cary, Chapel Hill, Apex and surrounding areas.
Raleigh-home-inspection.html

BassRumors.com
Providing a blog, news, and forum dedicated to bass fishing.
Reply With Quote
  #4  
Old 3/31/10, 10:03 PM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,489
Default Re: Weep Holes

Quote:
Originally Posted by jallingham View Post
Aren't weep holes supposed to be in the bottom course of bricks?
No, not actually........ depending on the type of foundation and floor height they can be several feet above grade... I have seen them correctly installed as high 4 feet or more.

Rule of thumb is that they are just at the foundation sill plate.

Hope this helps.

Jeff
Reply With Quote
  #5  
Old 3/31/10, 10:56 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Weep Holes

Quote:
Originally Posted by jhaynes View Post
No, not actually........ depending on the type of foundation and floor height they can be several feet above grade... I have seen them correctly installed as high 4 feet or more.

Rule of thumb is that they are just at the foundation sill plate.

Hope this helps.

Jeff
Never heard that one .
Do you have any documentation to back that up?

There is a cavity of one inch behind that brick siding and if up higher than the foundation (weeps) the water would build up and cause issues.
Reply With Quote
  #6  
Old 4/1/10, 2:34 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: Weep Holes

Many years ago about 1970 they used hemp instead of weep holes , Of course hemp is hard to see and it looks like the Brickie did a poor job .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #7  
Old 4/1/10, 2:43 PM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,489
Default Re: Weep Holes

Quote:
Originally Posted by belliott View Post
Never heard that one .
Do you have any documentation to back that up?

There is a cavity of one inch behind that brick siding and if up higher than the foundation (weeps) the water would build up and cause issues.
Bob, you did not carefully read my answer or you don't understand the concept of a pier and curtain foundation which we have all over the place here in the south................ if you still disagree please explain for the crowd why a GC would put weep holes below the sill plate on a pier & curtain foundation. The flashing turn down at the sill plate which is often 24 inches to 48 inches above grade depending on the slope of the lot............ I will be glad to send you pictures if need for clarification and even blue prints........ I have built hundreds of homes from Ohio, Va, Ind., Ky and NC.........the location of weep holes in virtually every application is near the foundation sill plate (regardless if its a slab, crawl, or basement) as well as above windows and doors of a brick veneer.


regards

Jeff
Reply With Quote
  #8  
Old 4/1/10, 3:05 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Weep Holes

Jeff is right Bob, that is very common in some geographic areas like here.
It allows steps in the exposed foundations the minimize the concrete exposure and some of the bricks below the weep holes will be slushed in with type S mortar. Flashings are usually right below the sill plates, normally one brick high.
Similar to this detail here.
This detail shows the flashing at sill height which is not a good idea, because there is always the possibility of wicking and voids underneath the flashing that would allow leakage at the box sill level.
The standard here is one course of brick lower to prevent that.



Hope this helps.
Reply With Quote
  #9  
Old 4/1/10, 4:18 PM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,489
Default Re: Weep Holes

Marcel, the only correction that I see needs to be done to the picture is that the flashing should be BEHIND the felt or approved wrap....not infront.

Jeff
Reply With Quote
  #10  
Old 4/1/10, 4:33 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Weep Holes

Good graphic Marcel. That explains it.
Reply With Quote
  #11  
Old 4/1/10, 7:23 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Weep Holes

Quote:
Originally Posted by jhaynes View Post
Bob, you did not carefully read my answer or you don't understand the concept of a pier and curtain foundation which we have all over the place here in the south................ if you still disagree please explain for the crowd why a GC would put weep holes below the sill plate on a pier & curtain foundation. The flashing turn down at the sill plate which is often 24 inches to 48 inches above grade depending on the slope of the lot............ I will be glad to send you pictures if need for clarification and even blue prints........ I have built hundreds of homes from Ohio, Va, Ind., Ky and NC.........the location of weep holes in virtually every application is near the foundation sill plate (regardless if its a slab, crawl, or basement) as well as above windows and doors of a brick veneer.


regards

Jeff
I would like a diagram.
Thanks.
Reply With Quote
  #12  
Old 4/1/10, 7:25 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Weep Holes

Quote:
Originally Posted by mcyr View Post
Jeff is right Bob, that is very common in some geographic areas like here.
It allows steps in the exposed foundations the minimize the concrete exposure and some of the bricks below the weep holes will be slushed in with type S mortar. Flashings are usually right below the sill plates, normally one brick high.
Similar to this detail here.
This detail shows the flashing at sill height which is not a good idea, because there is always the possibility of wicking and voids underneath the flashing that would allow leakage at the box sill level.
The standard here is one course of brick lower to prevent that.



Hope this helps.
Oh there it is.
Thanks Marcel, I will check it out and see what I missed here.
Reply With Quote
  #13  
Old 4/1/10, 7:37 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Weep Holes

It's a good graphic but it's my understanding that most bricks don't do well below grade.
Reply With Quote
Need a home inspection in Illinois? Check out InterNACHI's listing of Illinois certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 4/1/10, 8:13 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Weep Holes

We must have an epidemic here then cause I have never looked at a house built without the brick being below grade.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #15  
Old 4/1/10, 9:28 PM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,489
Default Re: Weep Holes

Quote:
Originally Posted by jallingham View Post
It's a good graphic but it's my understanding that most bricks don't do well below grade.
Not necessarily.....if you manage the moisture you will be fine......however most builders (good builders) will seal it and if necessary do a french drain.
I always seal the foundation from the footer up to grade.

The diagram is good however it is important that the moisture barrier OVERLAPS the flashing where it turns over onto the brick. Some builders will tape the joints however that is not proper.

regards

Jeff
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Construction & No Weep Holes jfunderburk Exterior Inspections 38 5/26/11 11:28 AM
Brick house nbhi Exterior Inspections 28 2/17/08 3:22 PM
Question about weep holes. gromicko Exterior Inspections 10 1/28/08 10:25 AM
Brick-Veneer Inspection Guide jbowman Exterior Inspections 12 1/8/07 9:20 AM


All times are GMT -4. The time now is 4:34 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts