2 part question.
After seeing ghosting in the closet adjacent the bathroom I performed humility evaluation on the gypsum.
Closet averaged 8% to 10% respectively.
Basement and under 500 sq-ft.
Lowest is 30" inches below grade to 0% at the back of the unit.
I did random sampling to form a hypothesis on(organic growth).
Higher levels of humidity in the wall board in a closet adjacent ( connecting too ) and the bathroom.
I covered the lowest and mid sections of the walls inside the closet, bedroom, bathroom.
I separated the unit into 2 parts, front and back half for my hypothesis. .
Back half = bathroom, bedroom.
Front= hall, kitchenette and living room entrance.
Front averaged 5.xxx% relative humidity, the back half averaged 9.xxxx.
#1: Basement apartment.
#2: Wall samples averaged 9%+( bathroom and closet )
#3: 5% in the rest of the unit.
#4: The unit had been vacant for over 1 month.
#5: no visible signs of growth in the living araea.
#6: Signs of living plant and organic growth in-between window openings of the bedroom.
Unit in 5 years old. Windows are hinged mechanical, thermo pain, with exterior screen.
Screened area never cleaned.

What are acceptable levels?
Would a IR camera have been able to complete my hypothesis when investigating form mold?
Thanks...........Robert.
Closet.
PS: I studied the IAC2 course " and think " I remember that relative humidity levels under 17% percent are not conductive to mold growth.
I am going back to complete this cert.

Attachment 45892 Attachment 45893

Other ares---------Attachment 45895Attachment 45894



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816

Last edited by ryoung7; 10/5/11 at 10:36 PM..
Reply With Quote
Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/26/11, 7:03 AM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,185
Default Re: acceptable humidaty levels in gypsum?

Your meter has a +/- 3% accuracy range. Does your fancy meter have a drywall setting?

Last edited by ldapkus1; 6/26/11 at 7:08 AM..
Reply With Quote
  #3  
Old 6/26/11, 8:25 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: acceptable humidaty levels in gypsum?

Quote:
Originally Posted by ldapkus1 View Post
Your meter has a +/- 3% accuracy range. Does your fancy meter have a drywall setting?
Thank you Linas.
The makers is GENERAL.
Yes it can be calibrated. To what extent is more a mathematical equation done after. I will post more.
No it is not fancy. 90 dollars at Home depot.
I am looking now into the settings Linas.
Mr.Adair kindly sent me some information on gypsum product and the article reminded me of settings.
Thanks Mr.Adair.
I have to pay more attention.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #4  
Old 6/26/11, 2:53 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: acceptable humidaty levels in gypsum?

The moisture levels are not that bad, especially if the house is vacant. A 4% difference in moisture levels from one wall to another is suspect. It is common to have higher moisture in closets and bathrooms.
Mold can grow on drywall at 12%.



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #5  
Old 6/26/11, 10:40 PM
Scott Gilligan,  CMI's Avatar
Scott Gilligan, CMI Scott Gilligan,  CMI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,828
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: acceptable humidaty levels in gypsum?

Point of correction:

Humidity is a reference to the amount of water in the air, not how saturated a material is with water. You would be better off referring to your readings as the percentage of moisture content or the saturation percentage. You measure relative humidity with a different kind of instrument all together and your wording could be misleading if someone would ever have to come back and verify your work.
Reply With Quote
  #6  
Old 6/27/11, 6:47 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: acceptable humidaty levels in gypsum?

Quote:
Originally Posted by sgilligan1 View Post
Point of correction:

Humidity is a reference to the amount of water in the air, not how saturated a material is with water. You would be better off referring to your readings as the percentage of moisture content or the saturation percentage. You measure relative humidity with a different kind of instrument all together and your wording could be misleading if someone would ever have to come back and verify your work.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #7  
Old 6/27/11, 8:02 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: acceptable humidaty levels in gypsum?

Quote:
Originally Posted by sgilligan1 View Post
Point of correction:

Relative or Absolute Humidity are references to the amount of water in the air, not how saturated a material is with water. You would be better off referring to your readings as the percentage of moisture content or the saturation percentage. You measure relative humidity with a different kind of instrument all together and your wording could be misleading if someone would ever have to come back and verify your work.
Reply With Quote
  #8  
Old 6/27/11, 8:46 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: acceptable humidaty levels in gypsum?

OK Brian I am waiting for help please or a answer.
Thank you...............................Robert.
I understand your dislike for wording.
I asked you before, help or do not reply.RIGHT.
I will be civil but it works 2 ways Brian. You ether help repair something that is broken " as you state InterNACHI IS ", OR you help HI'S get up off the ground and give the public a better conclusion to the industry.
I am so confused by your attitude of being judging without evidence.?
That's all.
Life is not complex. The industry is fractured in so many ways.
How do you improve it Brian?
A simple human value.
PS:
I should not have replied to Mr.Gillian so quickly. I did look for myself after.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #9  
Old 6/27/11, 11:16 AM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: acceptable humidaty levels in gypsum?

Quote:
Originally Posted by Gilligan View Post
Point of correction:

Humidity is a reference to the amount of water in the air, not how saturated a material is with water. You would be better off referring to your readings as the percentage of moisture content or the saturation percentage. You measure relative humidity with a different kind of instrument all together and your wording could be misleading if someone would ever have to come back and verify your work.
Something you might not be aware of: Young's main language is French so he does get his English words mixed up.



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #10  
Old 6/27/11, 12:26 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: acceptable humidaty levels in gypsum?

Quote:
Originally Posted by ryoung7 View Post
OK Brian I am waiting for help please or a answer.
Thank you...............................Robert.
I understand your dislike for wording.
I asked you before, help or do not reply.RIGHT.
I will be civil but it works 2 ways Brian. You ether help repair something that is broken " as you state InterNACHI IS ", OR you help HI'S get up off the ground and give the public a better conclusion to the industry.
I am so confused by your attitude of being judging without evidence.?
That's all.
Life is not complex. The industry is fractured in so many ways.
How do you improve it Brian?
A simple human value.
PS:
I should not have replied to Mr.Gillian so quickly. I did look for myself after.
Relative humidity or absolute humidity are ways of expressing the amount of water in air!
Reply With Quote
  #11  
Old 6/27/11, 4:29 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: acceptable humidaty levels in gypsum?

So as to express the amount in material would be saturation.
This was in a thread months back.
PS first language is English.
Worked with french, Italian, eastern Slovakian mostly, and Italian.
Thank you Brian.
civility becomes most people.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #12  
Old 6/27/11, 4:57 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: acceptable humidaty levels in gypsum?

Quote:
Originally Posted by jbraun View Post
Something you might not be aware of: Young's main language is French so he does get his English words mixed up.
Wish it was that simple.
As explained several times, dyslexia caused by sever head trauma 40 years ago. 6 nero surgeons and happy to be here alive today. @ years of misunderstanding and a bright athletic possibility gone.

Then working with French Canadians talking a ( bastardized French language ) wife was Parisian, and having to think that way for 35 years compounds the translation in forming a sentence.
Again only when I rush out thought as on the MB..
If you knew the Quebec French language you would understand the translation from French to English.
A simple statement can be compared to asking a question.
Plus the amount of school lost and the doctors unable to see the problem at that time. Early 1970's
Just thought I would explain again.
Henceforth I was on the job trained and learned by example. Watching.
Class B mason, class A Roofer, Class 2 cement finisher and ran most labor and job sites when I worked for large companies and held a specialized license that let me run almost all specialized equipment on a site.
Managed building 3 homes, not mine. I managed as the carpenter and GC.
Mr.Bushart warned me of the complexes while writing reports and seeking information.
I told him it will not wear me down.
Just a recap.
As I explained before, sorry but its the way I see written word Mr.Braun.
My spoken French is just adequate.
Like I said I am not ashamed of myself. No need.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #13  
Old 6/27/11, 9:28 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: acceptable humidaty levels in gypsum?

Long story short, Mold growth starts at about 20% moisture content in materials. If your moisture meter read 17%, you would mention the possibility of mold growth and include a short explanation of the potential health hazards.

"Saturation" is the point at which a material can hold no more moisture and you wouldn't comment on that. It varies with each material and there's no reason to memorize all that.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 6/27/11 at 9:32 PM..
Reply With Quote
Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 6/27/11, 9:49 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: acceptable humidaty levels in gypsum?

Question Kenton.
Mr.Braun mentions 12% percent saturation in gypsum for organisms to grow.
I hesitate using the word living organisem but look for referral when reporting.
Its learning how to save and file that is next.
Opinion please.
http://http://www.massillonohio.com/health/pdfs/mold_health-effects.pdf



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #15  
Old 6/27/11, 10:05 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: acceptable humidaty levels in gypsum?

Bacteria can actually grow on porous materials such as drywall and carpeting as low as 8% moisture content.

The article puts mold in a very basic easy to understand form. I could elaborate on some of the article if you wish such as, there are some medical tests that can detect mold exposure in extreme cases. I have doctors who refer me all the time because they can tell by running tests if it is fungal or not.



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Acceptable Moisture Levels jkeilson General Inspection Discussion 15 11/9/10 9:02 PM
Long Hairline cracks in a gypsum lath ceiling rkie Interior Inspections 5 5/17/08 4:27 PM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 7:47 AM


All times are GMT -4. The time now is 4:40 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts