Default Advice on bath exhaust vent termination.

I wanted to ask your opinion on the duct termination for my 2 bath exhaust fans.

The question I have is for the termination of one of the fans. It would be easier for me to cut through my cedar siding to do a side wall termination. It would be about 12 -15 feet total vent length. If I did the roof I would need to hire someone to vent through the roof(About 3 feet)

The fan is a Broan Model 683 CFM 80 http://www.broan.com/ImageLibrary/br...s/99043984.pdf

Not sure of the maximum length of vent.

For sidewall application.
Would you slope vent up slightly or run on attic floor?
What type duct would you use? Flex, semi corrigated metal?

Thanks!!



Performing Home Inspections in Cleveland, Strongsville, Brecksville, Broadview Heights, North Royalton, Parma and surrounding areas.
Reply With Quote
Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/1/11, 6:50 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,567
Default Re: Advice on bath exhaust vent termination.

Dave....side wall vent should be fine with that fan and why cut another hole in the roof...15 feet should be no problem with which ever material You choose to work with
just make sure You have a check valve in there for back flow wind and I would say across the floor is fine...



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #3  
Old 12/1/11, 6:51 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by dmacy View Post
I wanted to ask your opinion on the duct termination for my 2 bath exhaust fans.

The question I have is for the termination of one of the fans. It would be easier for me to cut through my cedar siding to do a side wall termination. It would be about 12 -15 feet total vent length. If I did the roof I would need to hire someone to vent through the roof(About 3 feet)

The fan is a Broan Model 683 CFM 80 http://www.broan.com/ImageLibrary/br...s/99043984.pdf

Not sure of the maximum length of vent.

For sidewall application.
Would you slope vent up slightly or run on attic floor?
What type duct would you use? Flex, semi corrigated metal?

Thanks!!
Also, running them out a sidewall with rigid duct buried in insulation to prevent condensation is good.

The distance run would depend on the size of the bathroom and cfm of fan but, like Jim said, it should be okay.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 12/1/11, 6:58 PM
Gary D. Rowden Gary D. Rowden is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Hemet, CA
Posts: 146
Default Re: Advice on bath exhaust vent termination.

Hi David
I would suggest the easiest install
12-15 feet is not too long and I would also use a flex it’s easier to maneuver around. I would also recommend arching the flex piping to prevent water intrusion at termination.
Reply With Quote
  #5  
Old 12/1/11, 7:22 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Advice on bath exhaust vent termination.

Personally I prefer sidewall termination.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #6  
Old 12/1/11, 9:06 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: Advice on bath exhaust vent termination.

Thanks, I appreciate the feedback.



Performing Home Inspections in Cleveland, Strongsville, Brecksville, Broadview Heights, North Royalton, Parma and surrounding areas.
Reply With Quote
  #7  
Old 12/1/11, 10:14 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Advice on bath exhaust vent termination.

I like either way but if the sidewall is what you can do that's what you should do. I like the idea of it being insulated and the sidewall is the easier way of doing that especially if you have blown in. I also prefer the caps with the three louvers. http://www.homedepot.com/h_d1/N-5yc1...atalogId=10053



Nevada Inspector of Structures #1730
Nevada Energy Auditor #30
www.homecsi.com
Reply With Quote
  #8  
Old 12/2/11, 3:10 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: Advice on bath exhaust vent termination.

The vent installation went very well today and thanks to you guys I saved a few hundred dollars.

A roofer wanted a minimum of $350. It cost me around $100.

I attached a few pics of the install. I just want to insulate the exposed pipes in the attic and patch my siding as I had to close to a window.

The hole saw combo worked great and seems to be of good quality.

I am going to post the inferior fan set up that was there before, leaking at connections and molding the wallboard. (I am ashamed to admit I was the dolt that installed the 1st fan about 7 years ago.

Thanks again!!
Attached Thumbnails
advice-bath-exhaust-vent-termination-exhaust-vent-120211-001-small-.jpg.JPG
Views:	88
Size:	44.8 KB
ID:	50271   advice-bath-exhaust-vent-termination-exhaust-vent-120211-003-small-.jpg.JPG
Views:	77
Size:	37.9 KB
ID:	50272   advice-bath-exhaust-vent-termination-exhaust-vent-120211-004-small-.jpg.JPG
Views:	91
Size:	54.4 KB
ID:	50273   advice-bath-exhaust-vent-termination-exhaust-vent-120211-007-small-.jpg.JPG
Views:	76
Size:	55.7 KB
ID:	50274   advice-bath-exhaust-vent-termination-exhaust-vent-120211-010-small-.jpg.JPG
Views:	81
Size:	41.3 KB
ID:	50275  




Performing Home Inspections in Cleveland, Strongsville, Brecksville, Broadview Heights, North Royalton, Parma and surrounding areas.
Reply With Quote
  #9  
Old 12/2/11, 3:26 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Advice on bath exhaust vent termination.

I would vent it into the attic (I know you aren't supposed to) before I would put it out the roof. That would be a leak waiting to happen!



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 12/2/11, 3:33 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by jfunderburk View Post
I would vent it into the attic (I know you aren't supposed to) before I would put it out the roof. That would be a leak waiting to happen!
Not if properly flashed like any other roof penetration, (sewer vent, furnace pipe, etc.).



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #11  
Old 12/2/11, 3:37 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by ccurrins View Post
Not if properly flashed like any other roof penetration, (sewer vent, furnace pipe, etc.).
So properly flashed penetrations never leak? What is the life span of the flashing or the metal or plastic vent?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 12/2/11, 6:11 PM
Gary D. Rowden Gary D. Rowden is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Hemet, CA
Posts: 146
Default Re: Advice on bath exhaust vent termination.

Quote:
Originally Posted by jfunderburk View Post
What is the life span of the flashing or the metal or plastic vent?
Joe
That’s a good question; you would think that metal for the most part would out last the plastic vent cover by far and a few years ago that may have been true, but with the improvements they have made with plastic materials it’s hard to truly say.
I would suspect the life expectancy of the plastic vent cover would be determined on the extreme weather conditions it had to endure, quality of the plastic used and location.

And David
I personally would still arch the last few feet of the flex vent piping above the termination point (vent cover) this will help prevent any possible chance of water running back into flex piping in the event of water intrusion. Just a thought.
Reply With Quote
  #13  
Old 12/2/11, 6:53 PM
Nanci Hagarty Nanci Hagarty is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: West Chester, PA
Posts: 77
Default Re: Advice on bath exhaust vent termination.

Gable ends, sidewalls and eaves are always the preferred method of termination. Only as a last resort do our technicians install venting thru the roof.




Nanci Hagarty
http://www.mrdryervent.com
mrdryervent@comcast.net
Phone : 610-399-3638
Reply With Quote
Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/15/11, 10:49 PM
Paul Walmsley Paul Walmsley is offline
InterNACHI Member
 
Join Date: Dec 2011
Location: Keswick Ontario
Posts: 16
Default Re: Advice on bath exhaust vent termination.

Just an observation but the last few ft. of the pipe should be wrapped with insulation condensation will occur.Warm pipe cold attic air..
Reply With Quote
  #15  
Old 12/16/11, 12:06 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: Advice on bath exhaust vent termination.

http://www.nachi.org/bathroom-ventil...ducts-fans.htm

And the best practice is to slant horizontal runs of duct down toward the exterior outlet to drain any condensation outside, just saying!



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/

Last edited by mgratton; 12/16/11 at 12:09 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sidewall vent termination code update vmitchinson Inspecting HVAC Systems 0 9/16/10 10:14 PM
Is a bath vent fan ok over the stove? rwashington Inspecting HVAC Systems 5 7/23/09 5:08 PM
Question on vent termination gwilcox Inspecting HVAC Systems 4 6/23/09 10:26 PM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 5:22 PM


All times are GMT -4. The time now is 4:43 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts