Default What is an appropriate location for a Carbon Monoxide Detector?

I see them in the same location as the the hallway smoke detectors.
Is this ok? Or is there a different criteria?


David



An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/24/11, 1:21 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: What is an appropriate location for a Carbon Monoxide Detector?

Most AHJ or State laws require one within 15' of all rooms used for sleeping when house uses fossil fuel appliances or when connected to an enclosed garage.

They make smoke/co combo detectors, which is usually in the bedrooms hallway.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #3  
Old 8/24/11, 8:52 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: What is an appropriate location for a Carbon Monoxide Detector?

Quote:
Originally Posted by dnasser View Post
I see them in the same location as the the hallway smoke detectors. Is this ok? Or is there a different criteria?
Per the 2009 IRC, CO alarms must be located outside each separate sleeping area in the immediate vicinity of the bedrooms. The carbon monoxide alarm
can be located near the smoke alarm required in the immediate area of the bedrooms by Section R314.3. At this time, CO detectors are not required to be hard wired or interconnected like smoke alarms. One alarm is insufficient for a home built to the 2009 IRC.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 8/24/11, 10:39 AM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: What is an appropriate location for a Carbon Monoxide Detector?

Quote:
Originally Posted by jfunderburk View Post
Per the 2009 IRC, CO alarms must be located outside each separate sleeping area in the immediate vicinity of the bedrooms. The carbon monoxide alarm
can be located near the smoke alarm required in the immediate area of the bedrooms by Section R314.3. At this time, CO detectors are not required to be hard wired or interconnected like smoke alarms. One alarm is insufficient for a home built to the 2009 IRC.

thanks Joe....



An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
  #5  
Old 8/24/11, 10:53 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,194
Default Re: What is an appropriate location for a Carbon Monoxide Detector?

California Law

Detector Placement

Manufacturer Placement Info
Reply With Quote
  #6  
Old 8/24/11, 11:29 AM
jsecord jsecord is offline
InterNACHI Member
 
Join Date: Dec 2010
Location: Beachwood, N.J.
Posts: 22
Default Re: What is an appropriate location for a Carbon Monoxide Detector?

Joe, just read the quote on your signature area by TR. Right on!!!



New Jersey License 24GI00110700
WWW.jerseyshoreinspections.com
email: jeffrey@jerseyshoreinspections

Complete Radon Testing

Serving all of New Jersey
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Civil suit targets 12 for carbon monoxide deaths jbushart Legislation, Licensing & Legal Issues for Inspectors 5 11/30/11 9:36 PM
Illinois: Carbon Monoxide Alarm Detector Act rcramer Legislation, Licensing & Legal Issues for Inspectors 2 2/9/07 7:52 AM
New Illinois CO detector law ldapkus Legislation, Licensing & Legal Issues for Inspectors 1 10/15/06 12:39 PM
Another reason to recommend CO testers rnewman1 Interior Inspections 2 10/12/06 7:47 AM


All times are GMT -4. The time now is 4:44 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts