Default Asbestos Cement-Based Siding as Firewall

Hey Folks-

Is asbestos cement-based siding considered a fire-rated material and would suffice as a firewall?

This property had what appeared to be asbestos cement-based siding. They later attached a garage and left the material on the inside wall of the garage toward the house. The interior wall has a couple locations where the firewall is compromised. But if it wasn't compromised and the asbestos cement-based siding was solid all along the interior wall, would you consider it an acceptable firewall separation?

Thanks

Kenny
Attached Thumbnails
asbestos-cement-based-siding-firewall-img_6311.jpg   asbestos-cement-based-siding-firewall-img_6436_r.jpg   asbestos-cement-based-siding-firewall-img_6430.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/18/10, 4:39 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Asbestos Cement-Based Siding as Firewall

I'm not sure if I would be to concerned about the siding. I would however be concerned about the wood storm door, the original wood jamb it is installed on and it appears to me a wood door behind it? Hard to tell in the picture. Also any other penetrations in the parting wall that you mentioned.
Reply With Quote
  #3  
Old 4/18/10, 4:49 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Asbestos Cement-Based Siding as Firewall

Quote:
Originally Posted by krigler View Post
Hey Folks-

Is asbestos cement-based siding considered a fire-rated material and would suffice as a firewall?

This property had what appeared to be asbestos cement-based siding. They later attached a garage and left the material on the inside wall of the garage toward the house. The interior wall has a couple locations where the firewall is compromised. But if it wasn't compromised and the asbestos cement-based siding was solid all along the interior wall, would you consider it an acceptable firewall separation?

Thanks

Kenny
Unless it is "Listed" as an acceptable Fire Wall, then it is not a fire wall.... I would point it out.
The door is not rated so start there....
Reply With Quote
  #4  
Old 4/18/10, 4:56 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Asbestos Cement-Based Siding as Firewall

Quote:
Originally Posted by prussell View Post
I'm not sure if I would be to concerned about the siding. I would however be concerned about the wood storm door, the original wood jamb it is installed on and it appears to me a wood door behind it? Hard to tell in the picture. Also any other penetrations in the parting wall that you mentioned.
Hey Peter-

I agree. But I'm still curious about the details:

1. Would you consider this interior wood door fire-rated? It meets the 1-3/8" but I don't think the glass meets the requirements...but I'd prefer confirmation on that.

2. If the interior door is fire-rated is it okay to have the wood screen door?

3. And I'm still very interested on the acceptability of asbestos cement-based siding as a firewall.

Thanks!

Kenny
Attached Thumbnails
asbestos-cement-based-siding-firewall-img_6379.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #5  
Old 4/18/10, 5:04 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Asbestos Cement-Based Siding as Firewall

There is no U.L. Assembly listing for fire rated separations using that product, so it would now be just considered a non-combustible separation which has no rating.
There is a window breaching the assemble, a wood screen door and frame as others mentioned and part of the gable end louver opening in the attic of the garage. which would be OK only if the garage ceiling has at least a 1/2" drywall and sealed.
Check with the local AHJ to see what is required in your area.
Reply With Quote
  #6  
Old 4/18/10, 5:28 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Asbestos Cement-Based Siding as Firewall

Quote:
Originally Posted by mcyr View Post
There is no U.L. Assembly listing for fire rated separations using that product, so it would now be just considered a non-combustible separation which has no rating.
There is a window breaching the assemble, a wood screen door and frame as others mentioned and part of the gable end louver opening in the attic of the garage. which would be OK only if the garage ceiling has at least a 1/2" drywall and sealed.
Check with the local AHJ to see what is required in your area.
I'm with all of you on the handful of firewall breaches and thanks for confirming those.

But in reference to the siding (and I'm just discussing here, I wouldn't put this in a report), from a practical standpoint the siding is probably a better material to withstand a fire than drywall, yes? But from a technical standpoint since it has no U.L. listing as a fire-rated material it does not meet the requirements...is that fair to say?



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #7  
Old 4/18/10, 5:33 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Asbestos Cement-Based Siding as Firewall

That is correct Kenny, and don't forget, we don't know if it is asbestos siding until tested, But I installed some of the stuff as a kid and I will tell you it was the best siding ever invented and it won't burn. I bet it would compare to the 20 min. that a 1/2" drywall last in a fire.
Reply With Quote
  #8  
Old 4/18/10, 5:53 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Asbestos Cement-Based Siding as Firewall

P.S. They also make a matching siding now for repairs manufactured by GAF;
See here;
http://www.squidoo.com/ResidentialSiding
Reply With Quote
  #9  
Old 4/18/10, 6:41 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Asbestos Cement-Based Siding as Firewall

I agree with Marcel. The siding would probably be OK for a firewall protection but with all of the other penetrations in the wall it"s kinda of a mute point.

As far as the door goes, I would say no way, it should be fire rated with self closing hinges. I would point it out as a safety hazard which I'm sure you did.

Good discussion, thanks!
Reply With Quote
  #10  
Old 4/18/10, 7:34 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Asbestos Cement-Based Siding as Firewall

Quote:
Originally Posted by krigler View Post
I'm with all of you on the handful of firewall breaches and thanks for confirming those.

But in reference to the siding (and I'm just discussing here, I wouldn't put this in a report), from a practical standpoint the siding is probably a better material to withstand a fire than drywall, yes? But from a technical standpoint since it has no U.L. listing as a fire-rated material it does not meet the requirements...is that fair to say?
It may have been better when originally installed....but due to the age alone it my no longer be as resistant as it once was....
Also, I can see broken tiles in the picture.....

My parents house in California built in 1945 or so is still sided and the garage still roofed with the same material.
Reply With Quote
  #11  
Old 4/18/10, 7:41 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Asbestos Cement-Based Siding as Firewall

WHy would you be worried about it being a firewall. The whole house will never meet todays standards. Just write it up as so and move on..




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #12  
Old 4/18/10, 7:52 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: Asbestos Cement-Based Siding as Firewall

Quote:
Originally Posted by sfogarty View Post
WHy would you be worried about it being a firewall. The whole house will never meet todays standards. Just write it up as so and move on..
I think we are all well aware of that Sean, but there is nothing wrong in Kenny asking the question.
Reply With Quote
  #13  
Old 4/18/10, 8:23 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Asbestos Cement-Based Siding as Firewall

Quote:
Originally Posted by sfogarty View Post
WHy would you be worried about it being a firewall. The whole house will never meet todays standards. Just write it up as so and move on..
As Kenney said "the garage was added on later". A fire separation between a house and a garage has been a widely accepted building standard since the 1920's.

I would at least check and see what is necessary to maintain a separation that will comply with, at a minimum, of State or Local requirements.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
Need a home inspection in Minnesota? Check out InterNACHI's listing of Minnesota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 4/19/10, 8:48 AM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: Asbestos Cement-Based Siding as Firewall

Quote:
Originally Posted by prussell View Post
I agree with Marcel. The siding would probably be OK for a firewall protection but with all of the other penetrations in the wall it"s kinda of a mute point.

As far as the door goes, I would say no way, it should be fire rated with self closing hinges. I would point it out as a safety hazard which I'm sure you did.

Good discussion, thanks!
I agree Peter, in this case it was a mute point. But afterward I was thinking about different materials, including the asbestos cement-based siding and their ability to maintain a fire in the garage. When I think firewall I always first assume drywall needed. But what if the interior garage is lined with something like metal siding and there are no other breaches of the firewall...is that okay? I suppose it goes back to Marcel's point on whether or not it has a U.L. listing or not.

Kenny



Rigler Home Inspections
Hays, KS 67601
785-656-0272

Last edited by krigler; 4/19/10 at 8:52 AM..
Reply With Quote
  #15  
Old 4/19/10, 12:06 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Asbestos Cement-Based Siding as Firewall

It would have to meet code as far as a burn rate goes. I think fire rated drywall has a 90 minute burn rate.

Other material can be used, say if it's existing but I think fire rock is the standard we use now.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hard board siding? sfalvey Exterior Inspections 23 11/29/10 2:41 PM
Asbestos.............What is asbestos? mkyriacou Ancillary Inspection Services & Additional Topics 2 9/17/09 5:03 PM
Help! Asbestos Pipe Insulation John Doem General Inspection Discussion 24 6/3/08 9:59 AM
Asbestos jmckenna1 Miscellaneous Discussion for Inspectors 0 1/26/07 11:11 PM


All times are GMT -4. The time now is 4:44 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts