Default Attic Ventilation SOP Requirement

attic-ventilation-standard-practice-requirement-img_0243.jpg attic-ventilation-standard-practice-requirement-img_0020.jpg attic-ventilation-standard-practice-requirement-img_0022.jpg attic-ventilation-standard-practice-requirement-img_0228.jpg attic-ventilation-standard-practice-requirement-img_0230.jpg

According to Res. SOP
2.9. Attic, Ventilation & Insulation
I. The inspector shall inspect
B. the ventilation of the attic spaces
C. mechanical ventilation systems;

II. The inspector is not required to:

F. activate thermostatically operated fans.
Is that confusing to anyone?
Because the SOP requires me to inspect the attic ventilation AND the mechanical ventilation systems, a client might say my inspection includes activating the thermostatically operated fan.

In law, if there is any confusion, the consumer wins.

Last edited by bgromicko; 10/5/09 at 5:10 PM..
Reply With Quote
Find an InterNACHI certified California Home Inspector (and anywhere else in North America)
  #2  
Old 10/5/09, 5:04 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,489
Default Re: Attic Ventilation SOP Requirement

Quote:
Originally Posted by bgromicko View Post
According to Res. SOP
2.9. Attic, Ventilation & Insulation
I. The inspector shall inspect
B. the ventilation of the attic spaces
C. mechanical ventilation systems;

II. The inspector is not required to:

F. activate thermostatically operated fans.
Is that confusing to anyone?
Because the SOP requires me to inspect the attic ventilation AND the mechanical ventilation systems, a client might say my inspection includes activating the thermostatically operated fan.

In law, if there is any confusion, the consumer wins.
How can it be "confusing" when it specifically states that the inspector is not required to activate thermostatically operated fans?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #3  
Old 10/5/09, 5:12 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,143
Default Re: Attic Ventilation SOP Requirement

Quote:
Originally Posted by jbushart View Post
How can it be "confusing" when it specifically states that the inspector is not required to activate thermostatically operated fans?
If a consumer thinks that the mechanical ventilation system in an attic includes a roof fan, then there is confusion. And when there's confusion, the consumer legally is protected (or wins).
Reply With Quote
  #4  
Old 10/5/09, 5:20 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Attic Ventilation SOP Requirement

Quote:
Originally Posted by jbushart View Post
How can it be "confusing" when it specifically states that the inspector is not required to activate thermostatically operated fans?
Ditto.

Just like other exclusions and limitations.
Reply With Quote
  #5  
Old 10/5/09, 6:46 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Attic Ventilation SOP Requirement

II. The inspector is not required to:

F. activate thermostatically operated fans.

Are they talking about a remotely installed thermostat or integrally built-in with the exhaust fan set at a pre-set temperature.

If it is remote, then what is the difference between that and using normal operating controls on a furnace thermostat?

What if I use a simulated heat source (my lighter) to activate the thermostat? Then I did not touch it and know if it worked, right.
Reply With Quote
  #6  
Old 10/5/09, 6:58 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Attic Ventilation SOP Requirement

Hard to activate a thermostat controlled attic fan when the temp is in the 20's. Most of the t-stats don't go much below 60, if that.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #7  
Old 10/5/09, 7:13 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Attic Ventilation SOP Requirement

Blaine, you got to use this one;

Line voltage 0-100


Reply With Quote
  #8  
Old 10/5/09, 7:28 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Attic Ventilation SOP Requirement

Actually, Marcel, I try not to inspect when the temperature is below 60. Just too darn cold for me!



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #9  
Old 10/5/09, 7:35 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Attic Ventilation SOP Requirement

Still looking for one for my area Blaine 0-85.

Poured concrete last Winter at -8 and that was pushing my limit.
My blood stops flowing at below 0
Reply With Quote
  #10  
Old 10/5/09, 8:11 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,393
Default Re: Attic Ventilation SOP Requirement

I think I'd be pretty ticked off at an inspector that started fooling around with the thermostatic controls on the power vent in my attic and have no problem telling a client that is not my job....



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #11  
Old 10/5/09, 8:15 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Attic Ventilation SOP Requirement

Haven't seen one yet so I guess it is not a problem Jim.
Usually, everything is frozen up there anyways.
Reply With Quote
  #12  
Old 10/5/09, 8:21 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,393
Default Re: Attic Ventilation SOP Requirement

yes Marcel it is a regional thing for sure, different parts of the country they are very handy....mine runs a lot in the summer months....it has a thermostat and a humidistat, but you will never hear it come on between September and may....



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #13  
Old 10/5/09, 8:27 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Attic Ventilation SOP Requirement

You know Jim, this makes me think.

Would not having the proper insulation value and the proper 1 sf. of free air ventilation per 300 sf of attic space and a natural balance of eave and soffit vents off-set the cost of the energy usage and maintenance required for those fans to begin with?

Just talking out loud.
Reply With Quote
Find an InterNACHI certified California Home Inspector (and anywhere else in North America)
  #14  
Old 10/5/09, 8:33 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,393
Default Re: Attic Ventilation SOP Requirement

I had that same conversation with my roofer two years ago when this one was installed Marcel...and it sure was borderline on this house, but a number of years back i owned a split level with great temperature differences from level to level...and decided to install a couple of power vents....solved the problem in a heart beat and saved a bundle on heating and cooling...I think it greatly depends on the design of the structure....jmo...



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #15  
Old 10/5/09, 8:41 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Attic Ventilation SOP Requirement

I guess going back to checking an exhaust fan in the Attic, I would personally just note that one was observed and not inspected for whatever design it was intended for. The hell with the fan.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Mold question? ccurrins Interior Inspections 35 1/23/09 12:55 PM
Way More Intake To Supplement Minimal Exhaust Ventilation? Ed Fako Exterior Inspections 1 12/19/08 7:07 PM
Is inadequate roof or attic ventilation a defect? gliebig Exterior Inspections 85 1/16/08 7:56 PM
Attic ventilation requirement rray Inspecting HVAC Systems 42 4/23/06 12:44 PM


All times are GMT -4. The time now is 8:46 PM.