Does anyone have a good picture of mold in an attic caused by a bathroom exhaust fan terminating in the attic. I have a builder that has allowed the exhaust pipe to terminate in the attic at the decking and then encased in sprayon foam insulation.

Thanks
Russ
Reply With Quote
  #2  
Old 12/29/08, 10:40 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,697
Default Re: bathroom exhaust

http://www.midtninspections.com/syst..._IR_Report.pdf



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #3  
Old 12/29/08, 10:42 AM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 1,114
Default Re: bathroom exhaust

Here ya go! Courtesy of Jeff Remas.

http://b4uclose.tripod.com/cockamami...d-to-attic?i=3



--

Erby Crofutt
B4U Close Home Inspections
Georgetown, Kentucky

KY Lic# HI-2041
www.b4uclose.com
http://www.kentuckyradon.com
Kentucky Home Inspections
Kentucky Home Inspectors
NACHI02090301

Read my Active Rain Blog here: Erby, The Central Kentucky Home Inspector

Join Active Rain HERE and I'll get some points for your participation. Please! I did ask nice!
Reply With Quote
  #4  
Old 12/29/08, 10:56 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: bathroom exhaust

Why do you have to prove it to a contractor with a photo?

"IRC 2006 M1501.1 Outdoor discharge. The air removed by every
mechanical exhaust system shall be discharged to the outdoors.
Air shall not be exhausted into an attic, soffit, ridge vent or
crawl space."

And,

"IRC 2006 M1506.2 Recirculation of air. Exhaust air from bathrooms
and toilet rooms shall not be recirculated within a residence or
to another dwelling unit and shall be exhausted directly to the
outdoors. Exhaust air from bathrooms and toilet rooms shall
not discharge into an attic, crawl space or other areas inside the
building."



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 12/29/08 at 12:13 PM..
Reply With Quote
  #5  
Old 12/29/08, 4:51 PM
Russell E. Napper Russell E. Napper is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Bulverde, TX
Posts: 18
Default Re: bathroom exhaust

Thanks for the inputs. Got what I needed. I wrote it up as per IRC ref. but hardheaded builder and plumber.

Thanks again to all and have a Happy New One.

Russ
Reply With Quote
  #6  
Old 12/29/08, 5:05 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: bathroom exhaust

From my inspection agreement:

"INSPECTION DOES NOT INCLUDE – Negotiating issues with the builder/owner/contractor;...."

If you have to do that, you ought to charge for your time.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 12/29/08, 5:37 PM
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 843
Default Re: bathroom exhaust

Some AHJ's do not enforce that part of the C***. But I always write them up.

Reply With Quote
  #8  
Old 12/29/08, 10:13 PM
John E. Gibson, #2 John E. Gibson, #2 is offline
New User
 
Join Date: Nov 2007
Posts: 12
Please Note: John E. Gibson, #2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: bathroom exhaust

Actually the picture from Erby doesn't begin to do a small leak justice. I have seen the entire inside of an attic coated with 1" of frost. Even the nail heads stuck out like spikes coated in ice. Spent hours crawling around with garbage bags and a scrapper removing the ice so that when it melted it would not come through the vapour barrier and drywall. The end vents of the gable were frozen over solid, and that was just from a leaky vent pipe.
Reply With Quote
  #9  
Old 12/30/08, 12:41 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: bathroom exhaust

I let slide going out the soffit or ridge vent. 95% of them around here do that and I've never seen any negative results from it. It's when it goes nowhere and gets covered by insulation that problems happen.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 12/30/08, 9:33 AM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is online now
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,916
Default Re: bathroom exhaust

Quote:
Originally Posted by jfunderburk View Post
I let slide going out the soffit or ridge vent. 95% of them around here do that and I've never seen any negative results from it. It's when it goes nowhere and gets covered by insulation that problems happen.
Agree. Around here the local AHJ's allow it. They require venting to the soffit or at least 18 inches above the insulation. I see a lot of these strapped to the trusses. (BTW, never found first hand damage from it. Ventilation is usually pretty good.) My own house is older and doesn't even have exhaust tubing. BR vents blow directly into the insulation (of course I moved some of it to allow better air flow.) Not very efficient for heat/air loss, but with a 45 year old house, that's to be expected.

I'm more concerned with dryer vents and kitchen vents. I have seen problems caused from both of these.
Reply With Quote
  #11  
Old 12/30/08, 9:47 AM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 1,114
Default Re: bathroom exhaust

Gee Joe, you mean like the one going out the soffit in my picture?



--

Erby Crofutt
B4U Close Home Inspections
Georgetown, Kentucky

KY Lic# HI-2041
www.b4uclose.com
http://www.kentuckyradon.com
Kentucky Home Inspections
Kentucky Home Inspectors
NACHI02090301

Read my Active Rain Blog here: Erby, The Central Kentucky Home Inspector

Join Active Rain HERE and I'll get some points for your participation. Please! I did ask nice!
Reply With Quote
  #12  
Old 12/30/08, 1:54 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: bathroom exhaust

Quote:
Originally Posted by ecrofutt View Post
Gee Joe, you mean like the one going out the soffit in my picture?
I wonder if that soffit is actually ventilated? I bet not. I don't see how that could happen on a newer home with well ventilated soffits.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bathroom Exhaust jschmidt2 Interior 25 12/12/07 3:49 AM
Bathroom exhaust vents jlomonaco Interior 6 3/19/07 11:10 AM
Bathroom exhaust vents pdacey Interior 8 4/2/06 12:16 PM


All times are GMT -4. The time now is 1:03 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts