  #1  
Old 6/26/08, 12:50 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Builder made fire door suggestions...?

I ran into an improvised metal clad door, seperating the garage from the living areas. The owner said, 'it was like that when they bought the house.' This was 25 years ago. Since my home inspections aren't code inspections, is there a safety concern or helpful avice with a door like this? Or leave it alone?

thx,

tom
Attached Thumbnails
builder-made-fire-door-suggestions-p1020677.jpg  
Reply With Quote
  #2  
Old 6/26/08, 12:54 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Builder made fire door suggestions...?

I'd write it as unorthodox fire separation door.
Unable to determine burn thru rating.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #3  
Old 6/26/08, 12:59 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: Builder made fire door suggestions...?

If it is "field engineered" and not officially UL Listed or Rated then it will provide a false sense of security. I'd definitely write that up as being deficient.
Reply With Quote
  #4  
Old 6/26/08, 1:30 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,393
Default Re: Builder made fire door suggestions...?

I've seen that on older homes with wood doors before Tom , but never on the inside..just outside only...would make you at least want to write something about a truly ugly door in Laundry area....jim



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #5  
Old 6/26/08, 3:02 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Builder made fire door suggestions...?

Thx Jim. FYI, this photo was taken from the garage side.

tom
Reply With Quote
  #6  
Old 6/26/08, 3:39 PM
cmcdonald cmcdonald is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Jaffrey, NH
Posts: 80
Please Note: cmcdonald is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Builder made fire door suggestions...?

Tom,
Other than the metal side visible in the picture, were there any other visible materials for the door (wood for example)? If the metal is covering wood it becomes a conductor of heat and may cause combustion to occur in the living area of the home through conduction in the event of a fire in the garage.

What is the door frame made of? Even if the door were a labeled fire rated door, if the door frame is made of non fire resistive material, it has compromised the fire rating of the door assembly and basically nullified any fire resistive protection that the door would have provided.

Finally, any self-closing devices in the door assembly? Without self closing devices the door may be accidentally left open allow fire and the products of combustion (smoke, carbon monoxide, and so on) to migrate into the home unhampered.

IMO, if any of the above were observed I would write it as a safety concern where the door and its associated components may not provide for adequate protection from fire and the products of combustion. I would recommend repair or replacement with an appropriate fire rated door and door assembly.
Reply With Quote
  #7  
Old 6/26/08, 3:41 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Builder made fire door suggestions...?

From my experiece in north california this is common installation thru the 60's. The only requirement was a 26 gauge metal sheet over the entire door. I always recommend upgrade with weatherstripping and self-closing hinges.

Mark Thorman
Mark Thorman Home inspections
www.MauiHomeInspections.com
Reply With Quote
  #8  
Old 6/26/08, 3:43 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Builder made fire door suggestions...?

I commented, that the inspector could not evaluate the effectiveness of the field engineered door, and recommended further evaluation by a qualified contractor. Something like that.

Thanks everyone.... I was concerned I was splitting hairs.

tom
Reply With Quote
  #9  
Old 6/26/08, 3:46 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Builder made fire door suggestions...?

Tom, It might be fine but without NRTL marking or a standard allowing this construction, what good is it. Good call.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #10  
Old 6/26/08, 4:15 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,393
Default Re: Builder made fire door suggestions...?

Quote:
Originally Posted by tdietrich1
Thx Jim. FYI, this photo was taken from the garage side.

tom
well that at least makes a lot more sense....thanks....jim



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #11  
Old 6/26/08, 8:27 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Builder made fire door suggestions...?

1927 building code requires self-closing, metal clad (26 gauge) at garage dooto living space.

Mark Thorman
Mark Thorman Home Inspections
www.mauihomeinspections.com
Reply With Quote
  #12  
Old 6/27/08, 12:07 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Builder made fire door suggestions...?

Quote:
Originally Posted by Mark Thorman
From my experiece in north california this is common installation thru the 60's.
I see these often as well. Generally it's a solid wood door with a sheet metal cover. No problem.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 6/27/08, 10:47 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Builder made fire door suggestions...?

As far as I can determine only the doors that are not solid wood 1 /38 in. min. or metal clad are required to be fire-rated.

Mark Thorman Home Inspections
www.mauihomeinspections.com
Reply With Quote
  #14  
Old 6/27/08, 11:35 PM
pwiseman pwiseman is offline
InterNACHI Member
 
Join Date: May 2007
Location: Washingtonville, NY
Posts: 108
Default Re: Builder made fire door suggestions...?

If the frame is wood how is the door Protecting the rest of the house.? Self closing is a must have. I would recomend a metal frame with a fire rated self closing door. Good call I beleive that this type of door fosters a false feeling of safety.

Patrick



Patrick Wiseman
PJC Home Inspections LLC
Washingtonville, New York
InterNACHI 107051007
http://www.wisemanhomeinspections.com
Performing Home Inspections in Newburgh, Monroe, Middletown, Goshen, New York
Reply With Quote
  #15  
Old 6/28/08, 1:05 AM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Builder made fire door suggestions...?

In 80 years of building codes no mention is made of the requirement for the door jamb other than tight fitting. To recommend beyond that is your choice but it is not the industry standard.


www.mauihomeinspections.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Escape, Fire & Smoke Alarms badair Interior Inspections 14 1/28/08 8:21 AM
Maytag Recalls Dishwashers Due to Fire Hazard pabernathy Electrical Inspections 1 2/2/07 2:13 PM
Heat Recovery Systems Present Potential Fire Hazards Barrie Inspector Canadian Inspectors 1 2/1/07 4:13 AM


All times are GMT -4. The time now is 1:00 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts