Does anyone have information regarding how much cellulose fibre is expected to compact over the first year.
I did a one year warranty inspection on a house that was supposed to have 12.2" (R40) insulation in the attic. I measured 8-9". Thanks. |
| Find an InterNACHI certified Minnesota Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Quote:
try this US CIMA info: Installation standards & practices Loose-fill cellulose insulation, like all loose-fill insulation, should be installed in accordance with ASTM Standard C-1015, Standard Practice for Installation of Cellulosic and Mineral Fiber Loose-Fill Thermal Insulation. In wall applications standard practice is to compact loose-fill cellulose to a density that will prevent settling. While this is a matter of some controversy most authorities recommend a density of at least 3.0 pcf for cellulose insulation in walls. Materials with high nominal settled densities (2.0 pcf and higher) should be installed at 3.5 pcf. Research has confirmed that settling is virtually nil with any cellulose insulation at densities of 3.5 pcf, or higher. Compacting cellulose insulation may produce a very slight reduction of R-value. Specifiers do not need to compensate for settling in attics since federal law (the CPSC standard and the FTC R-Value Rule) requires R-value and coverage data to be stated at settled density. Open blow cellulose installations do lose R-value as the material settles, however such installations provide “bonus R-value” until they reach settled density Specifiers, installers, and buyers need to understand that the "minimum thickness" column on cellulose coverage charts represents settled thickness, if the chart has only one thickness column. This is not done to confuse or mislead. It results from the fact that there is no accepted procedure for determining blown thickness that has been proven to correlate with the amount of material, by weight, required to yield the desired R-value. ASTM is working on an appropriate procedure. Some manufacturers provide initial installed thickness recommendations, but this is only a guideline to aid installers. The bag count and weight columns are the "official" coverage statements. http://www.cellulose.org/userdocs/Te...Bulletin01.pdf I'd look on the certificate or ask builder to prove what the bag count was and calculate from that or contact Energy Auditor with IR for more accurate information. hth ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good Last edited by badair; 4/15/09 at 11:05 AM.. |
|
#3
|
||||
|
||||
|
John,
Industry standard in Canada is blown cellulose: 12" blown thickness for R40 (actually works out to R45.6) Settles to 10.5"= R40. 14.7" blown thickness for R50 (actually R55.1) Settles to 13.15" (R50) R Value 3.8 per inch Hope this hepls. Rodney Misener, CMI Trinity Inspection Services Pictou County, Nova Scotia http://www.trinityinspectionservices.com Certified Home Inspector Certified Level 1 Thermographer Certified Energy Advisor WETT Certified Inspector IAC2 Radon/Mold Certified Infrared Certified |
|
#4
|
||||
|
||||
|
You will find some contractors blow the cellulose with too much air. This causes the insulation to "fluff up". It enables the contractor to install less product for 12" depth, but it can settle to 8 - 9" over time, therfore decreasing the R Value obtained. This is an incorrect and sometimes deliberate installation.
Rodney Misener, CMI Trinity Inspection Services Pictou County, Nova Scotia http://www.trinityinspectionservices.com Certified Home Inspector Certified Level 1 Thermographer Certified Energy Advisor WETT Certified Inspector IAC2 Radon/Mold Certified Infrared Certified |
|
#5
|
|||
|
|||
|
Quote:
Thanks Rodney. Is this info documented somewhere? |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Travisty | cbrown1 | Exterior Inspections | 384 | 9/11/08 6:40 PM |
| Options in selecting materials for basement construction | wdevries | Canadian Inspectors | 2 | 8/4/08 2:30 PM |
| UFFI or cellulose? | jkogel | Exterior Inspections | 12 | 7/1/08 1:10 PM |
| If anyone runs into pest problems | tallen | General Inspection Discussion | 13 | 5/8/07 1:22 AM |
| Cellulose Fiber Insulation | jallingham | Interior Inspections | 4 | 3/23/06 2:18 PM |